Set B Questions 11 to 20
- 11
Cleanouts shall be installed at intervals NOT exceeding ____ feet in horizontal drainage lines.
Explanation
IPC 708.1.1: Horizontal drainage pipes shall be provided with a cleanout at intervals of not more than 100 feet.
- 12
Cleanouts must be installed at each change of direction of a horizontal drainage pipe that is greater than:
Explanation
IPC 708.1.3: Cleanouts are required at each change of direction greater than 45 degrees in horizontal building drainage and building sewers.
- 13
If multiple changes of direction occur within a run of ____ feet, only one cleanout is required for the entire distance.
Explanation
IPC 708.1.3 Exception: Where more than one change of direction occurs in a run of piping, only one cleanout is required for every 40 feet of developed length.
- 14
What is the required minimum clearance (working space) in front of a cleanout for a pipe that is 6 inches or larger in diameter?
Explanation
IPC 708.1.8: Cleanouts on 6-inch and larger pipes shall be provided with a clearance of not less than 36 inches for rodding.
- 15
What is the required minimum clearance in front of a cleanout on a pipe that is smaller than 6 inches in diameter?
Explanation
IPC 708.1.8: Cleanouts on pipes less than 6 inches in size shall be provided with a clearance of not less than 18 inches.
- 16
Cleanout sizes must match the size of the pipe served, up to a maximum cleanout size of:
Explanation
IPC 708.1.7: Cleanouts shall be the same nominal size as the pipe they serve, up to 4 inches. For pipes larger than 4 inches, a 4-inch cleanout is acceptable.
- 17
Building sewers shall be provided with a cleanout where they connect to a building drain, located within ____ of the building wall.
Explanation
IPC 708.1.2: A cleanout is required on the building sewer within 10 feet of the junction with the building drain.
- 18
If an off-set is installed in a soil stack, and it is made at an angle of 45 degrees or less to the vertical, how is the stack sized?
Explanation
IPC 711.2: An offset in a vertical stack with a change of direction 45 degrees or less from vertical is sized as a straight vertical stack.
- 19
An offset in a soil stack made at an angle greater than 45 degrees to the vertical must be sized based on:
Explanation
IPC 711.3: For offsets greater than 45 degrees, the horizontal section must be sized as a building drain. It represents a horizontal run.
- 20
What is the minimum pipe size for any building drain serving a water closet?
Explanation
IPC Table 710.1: A building drain or branch receiving the discharge of a water closet must be a minimum of 3 inches in diameter.