Set C Questions 21 to 30
- 21
How many water closets are allowed on a single 3-inch horizontal branch drain?
Explanation
IPC Table 710.1 (Note a): A maximum of two water closets are permitted to discharge into a single 3-inch horizontal branch.
- 22
How many water closets are allowed on a 3-inch building drain (horizontal)?
Explanation
IPC Table 710.1 (Note a): No more than two water closets shall discharge into a 3-inch horizontal building drain or branch.
- 23
How many water closets can discharge into a 3-inch vertical soil stack?
Explanation
IPC Table 710.1 (Note a): Not more than six water closets shall discharge into a single 3-inch stack.
- 24
Underground building drainage and vent pipe installed below ground must typically be at least what schedule if using PVC?
Explanation
IPC Table 702.2: PVC plastic pipe used for underground building drainage must meet ASTM D 2665 (Schedule 40) or equivalent solid wall/cellular core standards.
- 25
Can cellular core PVC (ASTM F 891) be used for building drainage piping?
Explanation
IPC Table 702.1 / 702.2: Coextruded PVC (cellular core) conforming to ASTM F 891 is approved for both above and below ground sanitary drainage.
- 26
What joint type must be used to connect cast-iron hubless soil pipe?
Explanation
IPC 705.4.3: Hubless cast-iron pipe joints are made with an approved elastomeric sealing sleeve and stainless steel shield and clamp assembly.
- 27
If a sewage ejector pump needs to discharge the effluent of a water closet, the minimum discharge pipe size from the pump is:
Explanation
IPC 712.4.2: Discharge piping from sewage ejectors handling water closets must be a minimum of 2 inches in diameter.
- 28
Sewage pumps and ejectors that handle solids must be capable of passing spherical solids of what minimum size?
Explanation
IPC 712.4.1: Sewage ejectors (when handling water closets) must pass a spherical solid of not less than 1-1/2 inches, unless it is a grinder pump.
- 29
For a grinder pump serving a water closet, the minimum discharge pipe size is allowed to be reduced to:
Explanation
IPC 712.4.2: Discharge piping from a grinder pump can be a minimum of 1-1/4 inches, whereas a standard sewage ejector requires 2 inches.
- 30
When installing a sewage ejector, the discharge pipe must include a check valve. Where must the shutoff valve be located in relation to the check valve?
Explanation
IPC 712.3.2: A full-open valve must be installed on the discharge side of the check valve (downstream) to allow servicing of the check valve.