Set D Questions 31 to 40
- 31
Is it permissible to connect a sewage ejector discharge pipe directly into a horizontal gravity building drain?
Explanation
IPC 712.4.1: The discharge must connect to the gravity drainage system with a wye-type fitting connected to the top of the horizontal pipe.
- 32
Any liquid/waste with a temperature exceeding ____ is prohibited from discharging directly into the sanitary drainage system without passing through a cooling device.
Explanation
IPC 701.7: The temperature of discharge water emptying into the building drainage system shall not exceed 140°F.
- 33
Which substance is strictly prohibited from entering the sanitary drainage system?
Explanation
IPC 701.3: Flammable or explosive liquids/gases, and highly toxic substances are prohibited from being discharged into the public sewer.
- 34
To test a completed drainage and vent system, water must be filled to a height of at least:
Explanation
IPC 312.2: A water test for the drainage and vent system requires applying a minimum 10-foot head of water (except for the uppermost 10 feet).
- 35
During an air test for a drainage and vent system, the pressure must be held at:
Explanation
IPC 312.3: An air test for plastic/cast iron drainage and vent systems must maintain a uniform pressure of 5 psi for at least 15 minutes without a drop in pressure.
- 36
If a horizontal branch connects to a vertical stack at the same level as another horizontal branch (back-to-back), what fitting should ideally be used if they receive discharge from water closets?
Explanation
IPC 706.3: Back-to-back water closets must use a double fitting specifically designed to prevent cross-flow across the stack.
- 37
Is it allowable to reduce the size of a drainage pipe in the direction of flow?
Explanation
IPC 704.2: The size of the drainage piping shall not be reduced in size in the direction of the flow. A 4-inch pipe cannot dump into a 3-inch pipe.
- 38
A 2-inch horizontal drain pipe has a maximum permitted capacity of how many DFUs?
Explanation
IPC Table 710.1(2): At a 1/4 inch per foot slope, a 2-inch horizontal branch/drain has a capacity of 21 DFUs.
- 39
At a 1/8 inch per foot slope, a 4-inch horizontal building drain has a maximum capacity of how many DFUs?
Explanation
IPC Table 710.1(2): A 4-inch horizontal building drain laid at 1/8 inch slope has a capacity of 180 DFUs.
- 40
When a sump pump or ejector is installed in a building, the sump pit must have a cover that is:
Explanation
IPC 712.3.4: Sump pits and sewage ejector tanks shall be provided with a gastight, structurally sound cover.