Topic 01 · Scope & Administration
Set C Questions 21 to 30
- 21
What device is used to firmly support vertical piping runs extending through floor penetrations?
Explanation
A riser clamp or friction clamp is bolted tightly around the pipe and rests on the floor structure to transfer the pipe's vertical load to the building.
- 22
What is the required backfill material for underground pipe bedding?
Explanation
IPC 306.2/306.3: Pipe must rest on a firm bed. Backfill must be free of rocks, broken concrete, and frozen chunks to prevent crushing the pipe during compaction or settlement.
- 23
When backfilling over an underground plastic pipe, the initial layer of backfill material placed over the pipe must be carefully compacted until it is at least ____ above the pipe before machinery is used.
Explanation
IPC 306.3: Backfill must be placed in thin layers and tamped carefully until 12 inches of cover is over the pipe to protect it from heavy equipment.
- 24
If a trench is over-excavated (dug too deep) during pipe installation, what must be done before laying the pipe?
Explanation
IPC 306.2.1: Where trenches are excavated below the installation depth, the trench must be backfilled to the proper grade with compacted approved material to prevent pipe sagging.
- 25
A horizontal copper pipe passes through a hole bored in a wooden stud. Does the hole itself count as an approved support?
Explanation
IPC 308.1: Holes in framing members act as adequate supports provided the spacing requirements are met and the pipe isn't damaged by the wood (e.g. sharp edges rubbing during expansion).
- 26
To prevent damage from freezing, water piping located in exterior walls must be:
Explanation
IPC 305.4: Water piping installed in exterior walls, unheated crawl spaces, or attics must be protected against freezing, typically by placing them inside the thermal envelope (warm side of insulation).
- 27
A water pipe installed parallel to a building footing must not be installed deeper than:
Explanation
IPC 304.4: Excavations parallel to building footings cannot extend beneath a 45-degree bearing plane originating from the bottom edge of the footing, to avoid undermining the foundation.
- 28
When piping passes through a foundation wall, what accommodation is typically required around the pipe?
Explanation
IPC 305.5: Pipes passing through foundation walls require a relieving arch or a sleeve that is not less than 2 pipe sizes greater than the pipe passing through to protect against structural settlement.
- 29
Piping installed underground beneath a concrete slab requires a minimum trench depth to protect the pipe, but what must surround the pipe in the trench?
Explanation
IPC 306: The pipe must be fully supported continuously for its entire length by firm, compacted earth or approved bedding material.
- 30
Any piping passing through a concrete/masonry wall or floor must be protected from corrosion by using:
Explanation
IPC 305.1: Piping passing through concrete/masonry requires sleeves or corrosion-resistant wrapping (e.g. 10-mil plastic tape or proper sleeving) to prevent abrasion and chemical corrosion from the concrete.