Topic 01 · Scope & Administration
Set D Questions 31 to 40
- 31
When a pipe sleeve is utilized in a fire-resistance-rated assembly (fire wall), the annular space must be:
Explanation
IPC 312.7 / IBC 714: Penetrations in fire-rated assemblies must use an approved intumescent or fire-blocking system that matches the fire-resistance rating of the wall.
- 32
If copper tubing is laid in a trench and covered with cinders or ashes (which contain sulfur/acids), what will likely happen?
Explanation
IPC 305.1: Copper is highly susceptible to corrosion from acidic materials like ashes, cinders, and certain soils; it must be protected or bedded in clean sand/earth.
- 33
Shield plates (nail plates / strike plates) are required when piping passes through a bored hole or notch in a stud, and the edge of the pipe is located within ____ of the face of the framing member.
Explanation
IPC 305.6: Steel shield plates are required if the pipe is closer than 1-1/4 inches from the stud face or if installed in a notch, to prevent drywall screws or nails from puncturing the pipe.
- 34
How thick must a protective shield plate (nail plate) be according to minimum code standards?
Explanation
IPC 305.6: The protective steel shield plate must be a minimum of 16 gage (0.0578 in. or approx 1.5mm) thick to effectively stop a nail or screw.
- 35
A shield plate (nail plate) protecting a pipe must extend at least ____ beyond the edges of the bored hole/notch.
Explanation
IPC 305.6: The steel shield must project at least 2 inches above the top plate and below the bottom plate, or extend 2 inches beyond the edge of the framing hole.
- 36
Piping laid horizontally in a trench without proper continuous bedding may suffer from which failure?
Explanation
IPC 306.2: Piping must have continuous support. Point-loading the pipe on a few rocks without bedding causes sagging, cracking, or breaking under earth loads.
- 37
What is the required thickness of the PVC or PE tape used to wrap a steel/iron gas pipe or copper water pipe for corrosion protection underground or in concrete?
Explanation
IPC 305.1 (and standard practices): Specifically manufactured 10-mil or heavier plastic pipe wrap tape (corrosion tape) is required to shield against aggressive soils or concrete.
- 38
What device is designed to secure a pipe and allow for its expansion while preventing side-to-side swinging?
Explanation
IPC 308.2: Hangers must permit expansion/contraction. Roller hangers or smooth clevis hangers allow linear movement of hot piping without tearing loose from the structure.
- 39
A newly installed underground PVC sewer line rests on a firm trench bottom. In freezing climates, the pipe must be buried:
Explanation
IPC 305.4.1: Building sewers and water supply pipes installed outside must be a minimum of 12 inches deep and, where subject to frost, at least 6 inches below the local frost depth.
- 40
Piping must NOT be supported directly by:
Explanation
Piping cannot be used to support other piping. Every run must be independently supported by the building structure.