Topic 11 · Special Piping & Storage
Set C Questions 21 to 30
- 21
What is a Zone Valve Box in a medical gas system?
Explanation
Zone valves must be located immediately outside each critical care area so that non-maintenance staff can easily shut off pure oxygen feeding a fire.
- 22
Is it permissible to install a medical gas pipeline in the same conduit or trench alongside fuel gas or high-voltage electrical lines?
Explanation
Locating pressurized pure oxygen next to potential ignition sources (high voltage) or fuels (oil/natural gas) is an extreme explosion hazard and is strictly prohibited.
- 23
If medical gas pipe must pass through a masonry wall, what must be done?
Explanation
Just like standard water piping, MedGas copper must be sleeved through all block, brick, or concrete walls to prevent physical scoring and chemical attack.
- 24
After the installer performs their pressure testing, who performs the final verification testing before the medical gas system can be used on patients?
Explanation
NFPA 99 requires a strict separation of duties. A third-party credentialed verifier (ASSE 6030) must perform a massive suite of tests (purity, particulate, cross-connection) before approving the system.
- 25
During the final particulate test for a medical gas system, what is the verifier looking for?
Explanation
The verifier discharges gas through a fine filter at every single outlet. Any dark specks (copper oxide from failed nitrogen purging) or dirt fails the test immediately.
- 26
At what point is the nitrogen purge gas introduced into the piping during the brazing process?
Explanation
Piping must be continuously purged with oil-free nitrogen prior to striking the torch, during the entire heating process, and while the copper cools down to prevent oxidation.
- 27
What is a WAGD system?
Explanation
WAGD systems evacuate trace anesthetic gases (like Nitrous Oxide or Isoflurane) exhaled by surgical patients so the surgeons and nurses do not breathe them.
- 28
Can you use threaded pipe nipples in a medical gas distribution system?
Explanation
While the main runs must be brazed copper, threaded brass/copper fittings are allowed for connecting specific valves or alarms, requiring careful application of oxygen-safe PTFE (Teflon) tape.
- 29
If PTFE (Teflon) tape is used on a threaded medical gas joint, how must it be applied?
Explanation
Tape must be kept off the very leading edge of the male thread. If a fragment of tape enters the pipeline, it could physically block a patient's breathing regulator or respirator.
- 30
Is it acceptable to braze medical gas piping while standing on a ladder and not purging because the nitrogen bottle is empty?
Explanation
Failing to purge creates flaky copper oxide soot inside the pipe. That soot will violently clog patient ventilators. It is never acceptable to braze without a purge.