Topic 11 · Special Piping & Storage
Set D Questions 31 to 40
- 31
Medical gas terminal units (the outlets on the wall where nurses plug in hoses) must be:
Explanation
NFPA 99 requires gas-specific indexing (like DISS or Pin-Index Safety Systems). It is physically impossible to plug an oxygen flowmeter into a medical air wall outlet.
- 32
What is the standard operating pressure for a hospital Oxygen distribution pipeline?
Explanation
Most standard medical gases (Oxygen, Medical Air, Nitrous Oxide) are regulated at the manifold to operate structurally at 50-55 psi throughout the hospital.
- 33
What is the standard operating pressure for an Instrument Air or Nitrogen distribution pipeline used for driving surgical power tools (like bone saws)?
Explanation
Gases used for "power" rather than "breathing" operate at significantly higher pressures, typically around 160-185 psi, to drive pneumatic surgical equipment.
- 34
What type of valve must be used for isolation and zone valves in medical gas systems?
Explanation
Quarter-turn ball valves are exclusively required because they provide immediate visual verification of their state (open/shut) and provide full, unrestricted flow.
- 35
How MUST underground medical gas piping be protected?
Explanation
Underground med gas runs are highly vulnerable. NFPA 99 generally demands they be run inside a continuous protective sleeve/conduit that is vented to the atmosphere.
- 36
Can you use push-fit or standard compression fittings to assemble medical gas distribution lines concealed in walls?
Explanation
Standard plumbing push-fits and compression fittings leak over time and are strictly prohibited in concealed gas pipelines to prevent catastrophic, highly-pressurized oxygen leaks inside walls.
- 37
When installing medical gas piping, the hanger spacing is mostly equivalent to standard plumbing, but what must be added in seismic zones?
Explanation
Hospitals are critical infrastructure. Special rigid seismic restraints are engineered and installed on MedGas pipes so they survive earthquakes and remain operational.
- 38
A medical gas manifold system requires two banks of cylinders. Why?
Explanation
Bulk manifolds use an alternating supply system to ensure absolute, uninterrupted continuous flow of gas delivery 24/7/365 to patients.
- 39
If you accidentally contaminate a section of medical gas copper tubing by dropping it in mud and oil, can it be used?
Explanation
Once factory cleanliness is compromised, field cleaning (like wiping with a rag) is heavily disallowed. Oil + Pressurized Oxygen = Explosion.
- 40
What is the required test pressure for the "Standing Pressure Test" consisting of a 24-hour hold without dropping?
Explanation
NFPA 99: The 24-hour standing pressure test (often witnessed by the Verifier) requires the system to hold a pressure 20% above its standard operating pressure (e.g., 60 psi for a 50 psi system) for a full 24 hours with zero leaks.