Set A Questions 1 to 10
- 1
Can storm water discharge into sanitary-only sewers?
Explanation
IPC 1101.2: Storm water shall not be drained into sewers intended for sanitary drainage only.
- 2
Subsoil drains must be placed:
Explanation
Subsoil drains (often French drains) surround basements/crawl spaces to manage groundwater per general drainage principles.
- 3
Storm drain connected to combined sewer requires:
Explanation
IPC 1103.1: Leaders/storm drains connected to a combined sewer shall be trapped to prevent sewer gas from escaping via the roof drains.
- 4
Roof drain strainer must extend above roof:
Explanation
IPC 1105.1: Strainers shall extend not less than 4 inches above the surface of the roof.
- 5
Strainer inlet area must be at least:
Explanation
IPC 1105.1: Strainers shall have an available inlet area of not less than one and one-half (1.5) times the area of the conductor or leader to which the drain is connected.
- 6
Flat deck strainer inlet area must be at least:
Explanation
IPC 1105.2: Flat deck drain strainers used on sun decks/parking decks shall have an available inlet area of not less than two times the area of the conductor/leader.
- 7
Storm drain sizing is based on:
Explanation
IPC 1106.1: Sizing is based on the 100-year, 1-hour rainfall rate indicated for the specific geographic location and the roof area.
- 8
Secondary roof drains required when:
Explanation
IPC 1108.1: Secondary drainage or scuppers are required where the roof design allows water to pond if the primary drainage system fails.
- 9
Secondary roof drain system must:
Explanation
IPC 1108.3: Secondary roof drain systems must have the end point of discharge separate from the primary system (to ensure overflow serves as a visible warning and works if the primary main is clogged).
- 10
Secondary roof drain must discharge to:
Explanation
IPC 1108.3: Discharge must be in a location where its operation will be observed by occupants or maintenance personnel, indicating a primary drain blockage.