Set B Questions 11 to 20
- 11
Storm drain trap size:
Explanation
IPC 1103.2: Storm drain traps shall be of the same size as the piping they serve.
- 12
Multiple roof drains need:
Explanation
IPC 1103.1 Exception: Where a branch storm drain serves multiple roof drains, a single trap can be installed on the main branch before it connects to the combined sewer.
- 13
Storm drain trap cleanout location:
Explanation
IPC 1103.3: An accessible cleanout shall be located on the downstream side of the trap or the trap shall be provided with a cleanout on the building side.
- 14
Three-inch drain minimum slope:
Explanation
IPC Table 1106.3 / general drainage principles dictate the minimum slope based on pipe size, similar to sanitary: 3-6 inches generally require 1/8 inch per foot.
- 15
Wall projection runoff calculation:
Explanation
IPC 1106.4: Where a vertical wall projects above a roof so as to contribute runoff onto the roof, an allowance must be made (often 50% of adjacent wall area added to roof area).
- 16
Siphonic drain system operates:
Explanation
IPC 1107.1: Siphonic roof drains prevent air from entering the pipes, allowing them to flow completely full at high velocity (siphonic action).
- 17
Siphonic drain horizontal piping:
Explanation
Since siphonic systems operate under negative pressure/siphonage, horizontal pipe runs do not require gravity slope and are typically installed flat.
- 18
Subsoil drain minimum diameter:
Explanation
IPC 1111.1: Subsoil drains shall not be less than 4 inches in diameter.
- 19
Subsoil drain protection:
Explanation
IPC 1111.1: Subsoil drains must be covered with a minimum of 2 inches of washed gravel or crushed stone to act as a filter medium.
- 20
No-gravity subsoil drainage:
Explanation
IPC 1111.1: When gravity drainage is impossible, a sump and pump (sump pump) must be utilized to lift the groundwater to discharge.