Set C Questions 21 to 30
- 21
Sump pump discharge capacity:
Explanation
IPC 1113.1.2: A sump pump handling subsoil drainage and/or clear water must have a pumping capability of not less than 15 gallons per minute.
- 22
Sump pump discharge pipe:
Explanation
IPC 1113.1.2: The discharge pipe size shall not be less than 1-1/4 inches in diameter.
- 23
A "leader" is defined as:
Explanation
IPC Definitions: A "Leader" is an exterior drainage pipe for conveying storm water. A "Conductor" is an interior drainage pipe conveying storm water.
- 24
A "conductor" is defined as:
Explanation
IPC Definitions: Conductor refers specifically to the interior piping descending from the roof.
- 25
Building storm drain carries:
Explanation
IPC Definitions: The building storm drain is the lowest piping (usually horizontal in the building foundation) that receives the conductors and conveys water out to the storm sewer.
- 26
Storm drain cleanouts required:
Explanation
IPC Chapter 11/708: Cleanouts are required for horizontal storm drains under similar spacing rules as sanitary drainage (typically every 100 feet).
- 27
Semicircular gutter sizing based on:
Explanation
IPC Table 1106.6: the capacity of a gutter is determined by its dimensions, the rainfall rate, and the slope (e.g., 1/16, 1/8, 1/4 inch per foot) it is set to.
- 28
Rainfall sizing factor:
Explanation
IPC 1106: Designers must consult Table 1106.2 referencing 4.0 inches/hr rainfall and find the pipe diameter capable of handling 10,000 square feet.
- 29
Standard roof drain flow:
Explanation
Standard gravity roof drains must be sized to handle the calculated rainfall without bottlenecking, hence why strainers have 1.5x the cross-sectional area of the pipe.
- 30
Controlled flow roof drainage:
Explanation
IPC 1110.1: Controlled flow systems purposely pond water; thus, the building must be structurally evaluated to hold that massive hydro-static weight safely.