Set D Questions 31 to 40
- 31
PEX tubing for roof conductor:
Explanation
IPC Table 1102.4: Approved materials for interior conductors include Cast Iron, Galvanized Steel, Copper, PVC, ABS, etc., but PEX is for water distribution.
- 32
Independent storm sewer trap:
Explanation
IPC 1103.1: Storm drains shall not be trapped when they connect to a storm sewer (dedicated), as traps impede flow and are unnecessary without sanitary gases present.
- 33
Offset horizontal section sized:
Explanation
IPC Table 1106.3: A horizontal section of a storm drainage system must be sized according to the horizontal building storm drain tables based on its slope.
- 34
Area drain grating must support:
Explanation
Area drains installed in accessible locations must feature gratings strong enough to resist the loads expected in that area.
- 35
Roof downspout discharge must not:
Explanation
IPC 1101.2: Storm water shall not discharge across public sidewalks or right-of-ways in a manner that creates a nuisance or hazard.
- 36
Exterior above-ground PVC leader:
Explanation
While PVC is commonly allowed for leaders, standard PVC degrades under UV light over time and must be protected (e.g., latex paint) if used in permanent exterior above-ground applications.
- 37
Storm drainage water test:
Explanation
IPC 312: Both sanitary and storm gravity drainage piping are typically tested under a 10-foot head of water.
- 38
Combined sewer sizing:
Explanation
IPC 1104.2 / Appendix: When sizing a combined system, sanitary DFUs are converted into an equivalent square footage of roof area to find the aggregate load for building drain sizing.
- 39
Sump pit location must be:
Explanation
IPC 1113.1: The sump pit and pump must be accessible for maintenance, inspection, and replacement.
- 40
A "scupper" is:
Explanation
IPC Definitions: A scupper is an opening built through a wall or parapet to allow storm water to overflow and exit the roof into a downspout or to the ground.