Set E Questions 41 to 50
- 41
Scupper secondary drainage sizing:
Explanation
IPC 1108.3: Scuppers acting as the secondary (emergency) drainage system shall be sized to prevent the depth of ponding water from exceeding the roof's design limits under 100-year rainfall.
- 42
Secondary drain inlet elevation:
Explanation
IPC 1108.1: Secondary drains exist to handle overflow; thus, they are elevated somewhat above the primary drains so they only activate when the primary system is clogged or overwhelmed.
- 43
Subsoil drain trap requirement:
Explanation
IPC 1111.1: If the subsoil drain connects to a combined sewer (storm and sanitary), it must be trapped and provided with a backwater valve to prevent sanitary wastewater/gas from backing up around the foundation.
- 44
Gutter slope adjustment improves:
Explanation
Table 1106.6 indicates that as the slope of the gutter increases, its capacity (the square footage it can drain) increases.
- 45
Storm trap vent protection:
Explanation
If a trap is required to prevent sanitary gases from escaping a combined sewer, the integrity of that trap seal must be protected from siphonage via proper venting.
- 46
Four-inch conductor capacity depends on:
Explanation
IPC Table 1106.2: Conductor and leader sizing tables are based entirely on pipe diameter and rainfall rate; vertical drop length is essentially irrelevant to capacity in standard gravity flow.
- 47
Backwater valves required when:
Explanation
IPC 1101.9: Where subject to backflow from the public sewer (e.g., basement storm drains below street level), storm drains must be fitted with backwater valves.
- 48
Roof drain into sanitary vent:
Explanation
IPC 1101.2/901.1: Storm water cannot enter the sanitary system, and vent pipes cannot be repurposed as storm conductors.
- 49
Sump pit must be located below the:
Explanation
Subsoil drains pull groundwater away; they must gravity-flow into a sump pit located beneath the slab/footer grade, which is naturally below the groundwater table being managed.
- 50
Underground storm sewer material:
Explanation
IPC 1102.2: Building storm sewers must be constructed from materials meeting the exact same stringent ASTM standards as building sanitary sewers.