Topic 13 · Subsurface Irrigation
Set C Questions 21 to 30
- 21
What is required for the trench bottom before placing subsurface gray water irrigation pipes?
Explanation
IPC 1402.5.1: The absorption trench bottom shall be level and scarified to minimize smearing and compaction of the soil pores.
- 22
Irrigation systems connected to a potable water supply using quick-closing valves may require the installation of what device?
Explanation
IPC 604.9: Water-hammer arrestors must be installed where quick-closing valves (such as solenoid irrigation valves) cause high-pressure shocks in the potable piping.
- 23
A diverter valve on a gray water irrigation system allows the homeowner to do what?
Explanation
IPC Chapter 14: All gray water systems must include a diverter valve allowing safe bypass to the primary building sewer.
- 24
Are backwater valves required on a gravity gray water subsurface irrigation system?
Explanation
IPC 1402.1: Where required by gravity and elevation, backwater valves prevent the irrigation field from backing up into the house.
- 25
Because nonpotable water can cause biological sliming, subsurface drip irrigation systems must be equipped with:
Explanation
IPC 1402.8.2: Subsurface drip systems must have accessible flush valves to clean out the biological sliming inherent in gray water.
- 26
When an irrigation water service pipe is installed in the same trench as a building sewer, what is the required vertical separation if the water line is not placed on a solid shelf?
Explanation
IPC 603.2: If laid in the same trench and not on a solid shelf, the bottom of the water service pipe must be a minimum of 12 inches above the top of the sewer.
- 27
Which of the following is absolutely prohibited regarding the disposal of untreated gray water?
Explanation
IPC Chapter 14: Untreated gray water must remain completely below the surface. Spraying it exposes the public to pathogens.
- 28
The tank holding gray water before it is pumped to the irrigation field must be constructed of materials that are:
Explanation
IPC 1301.9: Nonpotable storage tanks must be solidly constructed, completely water-tight, and resistant to environmental degradation and corrosion.
- 29
How is a cross-connection visually prevented before burying a newly installed nonpotable subsurface irrigation plumbing system?
Explanation
IPC 1301.5: The code requires an inspection of the piping before backfilling to ensure nonpotable pipes have not been cross-connected to the potable supply.
- 30
If a pump is used to supply nonpotable water to the irrigation field, it must be appropriately sized and:
Explanation
Pumps capable of over-pressurizing irrigation plastic piping must have pressure relief protection to prevent bursting the lines underground.