Topic 09 · Traps & Interceptors
Set A Questions 1 to 10
- 1
How many traps are normally required for a single plumbing fixture?
Explanation
IPC 1002.1: Each plumbing fixture shall be separately trapped by a liquid-seal trap, except as otherwise permitted by this code.
- 2
What is the required minimum depth of a standard liquid trap seal?
Explanation
IPC 1002.4: Each fixture trap shall have a liquid seal of not less than 2 inches.
- 3
What is the MAXIMUM depth of a standard liquid trap seal, unless specifically designed as a deep-seal trap?
Explanation
IPC 1002.4: The standard trap seal shall have a liquid seal of not less than 2 inches and not more than 4 inches.
- 4
What is the maximum permitted depth for a deep-seal trap?
Explanation
Most plumbing codes define a deep seal trap as having a seal exceeding 4 inches but generally not more than 6 inches in common application to avoid excessive fouling.
- 5
Are double-trapped fixtures permitted?
Explanation
IPC 1002.1: Exception 2 or general rules dictate that fixtures shall not be double trapped. Double trapping creates an air lock that restricts drainage.
- 6
What is the maximum allowed vertical distance from the fixture outlet to the trap weir?
Explanation
IPC 1002.1: The vertical distance from the fixture outlet to the trap weir shall not exceed 24 inches.
- 7
What is the maximum permitted horizontal distance from the fixture outlet to the trap?
Explanation
IPC 1002.1: The horizontal distance from the fixture outlet to the trap shall not exceed 30 inches measured from the centerline of the fixture outlet to the centerline of the inlet of the trap.
- 8
Which trap type is prohibited by the IPC?
Explanation
IPC 1002.3: S-traps, bell traps, crown-vented traps, and traps that depend on moving parts to maintain the seal are prohibited.
- 9
Are drum traps permitted?
Explanation
IPC 1002.3: Drum traps are prohibited EXCEPT where specifically approved as an interceptor (like a hair/solids interceptor).
- 10
What device prevents trap seal evaporation?
Explanation
IPC 1002.4.1: Trap seals of emergency floor drains and other subject to evaporation shall be protected by a trap seal primer valve, barrier-type device, or other approved method.