Topic 09 · Traps & Interceptors
Set B Questions 11 to 20
- 11
A trap primer valve must connect to the trap at a point above the:
Explanation
Trap primers supply water directly into the trap body above the dip to replenish the water forming the seal.
- 12
Can three sink compartments connect to a single trap?
Explanation
IPC 1002.1 Exception 1: A single trap is permitted to serve two or three sink compartments located in the same room where the furthest sink's center is no more than 30 inches apart.
- 13
Where must trap cleanout be located?
Explanation
IPC 1002.2: Fixture traps shall be self-cleaning. Traps without an integral cleanout plug must use a slip joint or union type connection for removal/cleaning.
- 14
Is slip joint permitted on trap discharge side?
Explanation
IPC 1002.2/405.8: A maximum of ONE slip joint is permitted on the trap outlet side (typically joining the trap arm to the drainage system).
- 15
Must interceptors be vented to prevent air binding?
Explanation
IPC 1003.1: Interceptors and separators shall be so designed that they will not become air bound if tight covers are used, thus requiring venting.
- 16
Grease interceptors are NOT required where?
Explanation
IPC 1003.3.1: Grease interceptors shall be required to receive the drainage from fixtures... EXCEPT for individual dwelling units or any private living quarters.
- 17
Device required upstream of grease interceptor?
Explanation
While often built in, a solids interceptor separates solid waste before the grease interceptor to prevent it from displacing volume in the grease capture chamber.
- 18
Can food waste grinder discharge into grease interceptor?
Explanation
IPC 1003.3.2: Food waste grinders shall not discharge to the building drainage system through a grease interceptor unless approved in combination with a solids interceptor.
- 19
Flow control device restricts wastewater to:
Explanation
The flow control restricts water velocity so the wastewater does not pass through the interceptor faster than the time needed for grease separation.
- 20
When is oil separator required?
Explanation
IPC 1003.4: At repair garages, car washing facilities, and engine washing facilities, drainage passing through the floor shall discharge through an oil separator.