Topic 09 · Traps & Interceptors
Set C Questions 21 to 30
- 21
Minimum depth of liquid in oil separator?
Explanation
IPC 1003.4.2.2: Oil separators shall have a depth of not less than 2 feet below the invert of the discharge drain.
- 22
Oil separator outlet water seal depth?
Explanation
IPC 1003.4.2.2: The outlet opening of an oil separator shall have not less than an 18-inch water seal.
- 23
Sand interceptor must have access for:
Explanation
IPC 1003.5: Sand and similar interceptors for heavy solids must have ready access for cleaning/removal of collected material.
- 24
Installation with heavy lint must discharge through:
Explanation
IPC 1003.6: Commercial laundries shall be equipped with an interceptor with a wire basket or similar device to catch lint, string, buttons, etc. (lint interceptor).
- 25
Maximum openings in lint basket?
Explanation
IPC 1003.6: Interceptors are usually equipped with a basket having openings not larger than 1/2 inch.
- 26
Specialized interceptor for bottling/slaughterhouse?
Explanation
IPC 1003.7 / 1003.8: Specialized industries like slaughtering rooms and bottling establishments require catch basins or specific sediment separators to prevent distinct types of waste (feathers, glass, bone) from clogging the sewer.
- 27
Building traps before public sewer permitted?
Explanation
IPC 1002.6: Building (house) traps are prohibited except where local conditions necessitate such traps and approved by the code official.
- 28
What required with building trap?
Explanation
IPC 1002.6: Where a building trap is installed, it must be provided with a relief vent or fresh air inlet on the inlet side of the trap.
- 29
Trap weir is:
Explanation
The weir of the trap is the level at which water begins to spill over into the drain pipe. It defines the top of the trap seal.
- 30
Trap dip is:
Explanation
The dip of the trap is the lowest portion of the inside top surface of the trap, determining the bottom of the trap seal.