Topic 09 · Traps & Interceptors
Set E Questions 41 to 50
- 41
What happens if grease interceptor flow control is removed?
Explanation
Without flow control, high velocity wastewater sweeps right through the chamber, carrying grease with it into the sewer.
- 42
Which space requires gravity or hydromechanical grease interceptor?
Explanation
IPC 1003.3.1: Commercial food preparation areas require grease interceptors to collect FOG (fats, oils, grease).
- 43
Slaughterhouse interceptor must separate:
Explanation
IPC 1003.8: Specific separators for slaughtering rooms are designed to catch organic solid waste generated by processing.
- 44
Acid Neutralizing basin must contain:
Explanation
Wastes containing acid must pass through an approved neutralizing medium before discharging into the sanitary sewer.
- 45
Trap constructed of what is prohibited?
Explanation
Fixtures and traps made of sheet metal corrode, lack smooth interiors, and develop biofilms, making them unapproved.
- 46
Standpipe height above trap weir must be:
Explanation
IPC 802.4: Standpipes shall extend a minimum of 18 inches and a maximum of 42 inches above the trap weir.
- 47
Horizontal distance from standpipe trap to vent?
Explanation
A standpipe trap is bound by the same rule as any other fixture trap based on its size (Table 909.1).
- 48
Can an entire branch use single trap?
Explanation
IPC 1002.1: Each fixture must be separately trapped to isolate its specific waste line odors from the room.
- 49
Slip joint connectors must be:
Explanation
IPC 405.8: Slip joints shall be accessible (requiring at least a 12x12 access panel if concealed).
- 50
Minimum liquid seal depth?
Explanation
IPC 1002.4: Standard minimum liquid trap seal for virtually all plumbing traps (unless specified deep seal) is 2 inches.