Topic 08 · Vents & Venting Systems
Set B Questions 11 to 20
- 11
To allow moisture to drain back to the sanitary system, all vent and branch vent pipes must be:
Explanation
IPC 905.2: All vent and branch vent pipes shall be so graded and connected as to drain back to the drainage pipe by gravity.
- 12
Vent rise before horizontal offsetting?
Explanation
IPC 905.4: A dry vent shall rise vertically to a minimum of 6 inches above the flood level rim of the highest trap or fixture being vented before turning horizontally.
- 13
Can you connect a dry vent to a horizontal drain line?
Explanation
IPC 905.3: Where a dry vent connects to a horizontal drain, the vent shall connect above the centerline of the horizontal drain pipe.
- 14
According to the IPC trap-to-vent distance table, what is the maximum permitted distance from a trap to its vent for a 1-1/2 inch fixture drain?
Explanation
IPC Table 909.1: The maximum distance of a 1-1/2 inch fixture drain from its trap weir to the vent is 6 feet.
- 15
What is the maximum distance from a trap to its vent for a 2-inch fixture drain?
Explanation
IPC Table 909.1: For a 2-inch fixture drain, the maximum distance to the vent is 8 feet.
- 16
What is the maximum distance from a trap to its vent for a 3-inch fixture drain?
Explanation
IPC Table 909.1: A 3-inch fixture drain can run up to 12 feet before requiring a vent connection.
- 17
What is the maximum distance from a trap to its vent for a 4-inch fixture drain?
Explanation
IPC Table 909.1: A 4-inch fixture drain (like a building drain serving a large water closet run) can extend up to 16 feet from the vent connection.
- 18
What is 'crown vent'?
Explanation
IPC 909.2: A vent shall not be installed within two pipe diameters of the trap weir. This setup is historically called a "crown vent" and is prohibited to prevent stoppage of the vent connection.
- 19
Minimum individual vent size?
Explanation
IPC 906.2: The minimum required diameter of individual vents, branch vents, or circuit vents is 1-1/4 inches (or roughly one-half the required drain size, whichever is greater).
- 20
Individual vent diameter calculated as:
Explanation
IPC 906.2: Vents shall not be less than one-half the required diameter of the drain served and not less than 1-1/4 inches.