Topic 08 · Vents & Venting Systems
Set E Questions 41 to 50
- 41
'Relief vent' is:
Explanation
IPC Definitions: A relief vent is an auxiliary vent that permits additional circulation of air to prevent massive pressure transients from affecting trap seals.
- 42
Vent stack sizing depends on:
Explanation
IPC Table 906.1: Vent stack sizes are determined by the size of the soil/waste stack, the total DFUs connected, and the developed length of the vent pipe.
- 43
Vent terminal location under soffit?
Explanation
IPC 903.5: Vent terminals must remain 10 feet away from any air intake opening, which includes soffit vents that pull air into the structure.
- 44
'Yoke vent' is:
Explanation
IPC Definitions/914.1: Yoke vents connect upward from the drainage stack to the vent stack to relieve pressure changes in multi-story applications.
- 45
For 4" stack with 500 DFUs, vent sizing from:
Explanation
IPC Table 906.1 specifies the size and developed length of vent stacks based on the size of the soil stack and total DFUs.
- 46
Back-to-back fixture common vent called:
Explanation
IPC 908.1: An individual vent is permitted to vent two traps as a common vent when connected at the same level.
- 47
Vent stack size not less than:
Explanation
IPC 906.2/906.1: Normally vent sizes are not less than one-half the required diameter of the drain pipe served, or 1-1/4 inches minimum.
- 48
Sump tank vent sizing based on:
Explanation
IPC Table 916.5.1: Sump vent sizing is derived from the discharge capacity of the pump (in gpm) and the developed length of the vent piping.
- 49
Waste stack (clear water) without individual vents?
Explanation
IPC 910.1: A waste stack vent installation allows fixtures on multiple floors to drain into an oversized stack that handles both air and waste without individual horizontal back vents (water closets prohibited).
- 50
Roof penetration vent sizing frost climate?
Explanation
IPC 903.2: Vent pipe sizing penetrating the roof in freezing climates must be a minimum of 3 inches to avoid frost closure.