Set A Questions 1 to 10
- 1
According to IPC Chapter 5, what is the maximum permitted pressure setting for a water heater pressure relief valve?
Explanation
IPC 504.4.1: The pressure setting of relief valves shall not exceed 150 psi or the maximum pressure rating of the water heater.
- 2
The temperature relief valve on a water heater shall be set to open at a maximum temperature of:
Explanation
IPC 504.4.1: Temperature relief valves shall be set to open at a maximum temperature of 210°F.
- 3
Maximum domestic water temperature for space-heating systems:
Explanation
IPC 501.2: Water heaters utilized for both space heating and domestic water heating shall be equipped with a mixing valve limiting the domestic water temperature to a maximum of 140°F.
- 4
Water heater must be permanently marked with:
Explanation
IPC 504.5: Water heaters and storage tanks shall be clearly and indelibly stamped or marked with the maximum working pressure.
- 5
The temperature sensor of a T&P relief valve must be located in:
Explanation
IPC 504.4.1: The temperature relief valve must be installed such that its temperature-sensing element is within the top 6 inches of the tank (where water is hottest).
- 6
A bottom-fed water heater installation requires:
Explanation
IPC 504.2: Bottom fed water heaters and those located above the fixtures they serve require a vacuum relief valve to prevent tank collapse during an empty-out.
- 7
T&P relief discharge pipe cannot connect directly to:
Explanation
IPC 504.6: T&P relief valve discharge pipes must not be directly connected to the sanitary drainage system to prevent sewer gas entry and contamination.
- 8
T&P relief discharge pipe may be threaded at the end?
Explanation
IPC 504.6: Discharge pipes shall not be threaded or equipped with a threaded fitting at the end, preventing it from being accidentally capped or closed.
- 9
T&P discharge pipe minimum size requirement:
Explanation
IPC 504.6: The discharge piping shall not be smaller than the diameter of the outlet of the valve served (usually 3/4 inch minimum).
- 10
Valves are permitted in T&P relief discharge pipes?
Explanation
IPC 504.6: Valves shall not be installed in the relief valve discharge pipe to ensure an unobstructed path for emergency pressure relief.