Set D Questions 31 to 40
- 31
When a backflow preventer creates a closed system, it requires:
Explanation
IPC 607.3: When a closed system is created by a backflow preventer, a thermal expansion tank or other device must be installed to handle thermal expansion.
- 32
PEX tubing near gas heater flue vent shall be:
Explanation
Manufacturer instructions and many codes require PEX to stay at least 18 inches away from the flue/vent on gas water heaters to prevent melting.
- 33
A water heater must be installed so it can be serviced:
Explanation
IPC 501.4 and IMC 306: Appliances must be installed to allow for observation, servicing, and replacement without tearing into the building structure.
- 34
Plastic water heater pan must meet IPC requirements for:
Explanation
IPC 504.7: Plastic pans must have minimum thickness (0.036 inch) and be capable of holding the required depth of water (1.5 inches).
- 35
An acceptable alternative to a drain pan under a heater might be:
Explanation
IPC 504.7: While pan drainage is standard, approved leak detection shutoff devices that stop the water supply on a leak are recognized alternatives for leak protection.
- 36
A drain pan must be sized larger than the tank by:
Explanation
IPC 504.7: Pans must be sized large enough to catch all water, typically at least 2 inches larger in diameter/width than the appliance.
- 37
T&P discharge to a floor drain requires:
Explanation
IPC 504.6: The discharge piping must discharge through an air gap into the same room as the water heater, not hard-piped to the drain.
- 38
An attic heater pan drain should discharge to a location where:
Explanation
IPC 504.7.1: Pan drains must discharge to a location where occupants will easily notice water leaking (like an visible exterior location), not hidden from view.
- 39
The primary function of a T&P relief valve is:
Explanation
The T&P valve is strictly a safety relief device for emergencies, not for operational temperature regulation or flow control.
- 40
A T&P discharge pipe with horizontal runs must:
Explanation
IPC 504.6: T&P discharge pipe shall drain by gravity and must not be trapped, allowing water to completely drain out.