Set E Questions 41 to 50
- 41
Which fitting is prohibited on T&P discharge piping:
Explanation
IPC 504.6: The discharge pipe shall not be equipped with a tee fitting to prevent multiple discharge sources.
- 42
An outdoor T&P relief discharge pipe must have:
Explanation
IPC 504.6: T&P discharge pipes terminating outdoors must be protected from freezing to prevent blockage and valve failure.
- 43
Tankless water heaters generally require which relief valve:
Explanation
Tankless water heaters have no storage tank capacity, thus typically require only a pressure relief valve, though manufacturer instructions always take precedence.
- 44
At the bottom of every water heater must be installed:
Explanation
IPC 503.2: A drain valve must be installed at the lowest point of every water heater for servicing and flushing.
- 45
Solar thermal systems require backflow protection:
Explanation
IPC 608.17.1 / 608.17.2: Specialized protection like DCVA (Double Check Valve Assembly) or RPZ (Reduced Pressure Zone) is required depending on heat transfer fluid toxicity.
- 46
The T&P valve temperature probe must be inserted into:
Explanation
IPC 504.4.1: The sensing element must be in the top 6 inches where tank water is hottest to detect dangerous temperature rise.
- 47
Hot water distribution piping must be rated for:
Explanation
IPC 605.4: Hot water distribution pipe and tubing must have a minimum pressure rating of 100 psi at 180°F sustained operation.
- 48
The size of an expansion tank is determined by:
Explanation
Expansion tank sizing requires calculating the system volume, incoming water pressure, and the amount of thermal expansion expected.
- 49
A water heater pan drain line should NOT be hard-piped to:
Explanation
While a T&P valve can discharge into a pan, the pan drain piping must be separate and independent. The pan drain cannot be hard-connected directly to the T&P discharge pipe.
- 50
The cold water shutoff valve for a heater must be a:
Explanation
IPC 503.1: Shutoff valves for water heaters must be of the full-open type (like a ball valve or gate valve) to completely isolate the heater.