Topic 05 · Water Supply & Distribution
Set A Questions 1 to 10
- 1
What is the absolute minimum size required for a water service pipe entering a building?
Explanation
IPC 603.1: The water service pipe shall be sized to supply water to the structure, but shall not be less than 3/4 inch in diameter.
- 2
Water service/sewer separation distance:
Explanation
IPC 603.2: The water service and the building sewer shall be separated by not less than 5 feet of undisturbed or compacted earth.
- 3
When a water service pipe is placed in the same trench as the building sewer, the bottom of the water service pipe must be at least ____ above the top of the highest point of the sewer.
Explanation
IPC 603.2: If installed in the same trench, the bottom of the water service must be located a minimum of 12 inches above the top of the sewer.
- 4
What is the required minimum pressure at the fixture outlet for a standard plumbing fixture (other than a flushometer)?
Explanation
IPC 604.3: The water distribution system shall ensure a minimum pressure of 8 psi at the fixture outlet for most fixtures.
- 5
What is the minimum pressure required at the fixture outlet for a flushometer valve water closet?
Explanation
IPC Table 604.3: A standard flushometer valve requires a minimum of 15 psi, though some commercial styles require 25 psi. 15 is the code minimum for a standard blowout or siphonic.
- 6
Maximum static water pressure:
Explanation
IPC 604.8: Where static water pressure exceeds 80 psi, an approved pressure-reducing valve (PRV) shall be installed.
- 7
Strainer required pre-PRV check:
Explanation
IPC 604.8: The PRV shall be preceded by an approved strainer. A strainer made part of the PRV is acceptable.
- 8
Water hammer arrestor installed on:
Explanation
IPC 604.9: A water hammer arrestor shall be installed where quick-closing valves (like dishwasher, washing machine, or flushometer valves) are utilized.
- 9
Air gap for 1/2" opening:
Explanation
IPC 608.16.1: The minimum required air gap shall be twice the effective opening (2 x 0.5 = 1 inch), but never less than 1 inch.
- 10
Air gap near wall requirement:
Explanation
IPC 608.16.1: When located near a wall (within 3 times the diameter of the opening), the air gap must be increased (typically to 3x the diameter).