Topic 05 · Water Supply & Distribution
Set B Questions 11 to 20
- 11
Air gap for 1" outlet unaffected:
Explanation
IPC 608.16.1: The minimum air gap is two times the diameter of the effective opening. 1 inch x 2 = 2 inches.
- 12
High-hazard backflow preventer:
Explanation
IPC 608.17.2: For a boiler system containing chemicals (high hazard), an RPZ backflow preventer is required.
- 13
AVB continuous pressure limit:
Explanation
IPC/ASSE 1001: Atmospheric vacuum breakers are not designed for continuous pressure and must not be pressurized for more than 12 consecutive hours.
- 14
AVB discharge valve permitted:
Explanation
IPC 608.17.4: No valve is permitted on the discharge side of an AVB. If a valve is closed, it subjects the device to continuous pressure.
- 15
Interior meter downstream valve:
Explanation
IPC 606.1: A full-open valve shall be installed on the water service pipe immediately downstream of the water meter.
- 16
Full-open valve at riser base is required for buildings with more than:
Explanation
IPC 606.1: A full-open valve is required at the base of every water riser pipe in occupancies other than multiple-family residential occupancies that are two stories or less.
- 17
Dwelling unit water supply requires:
Explanation
IPC 606.1: A shutoff valve shall be provided on the water supply pipe to each dwelling unit.
- 18
Parallel water manifold installation:
Explanation
IPC 604.10: Manifolds for parallel water distribution systems must be accessible.
- 19
PVC interior hot/cold water:
Explanation
IPC Table 605.4: PVC is permitted for water service exterior to the building, but is NOT approved for interior hot or cold water distribution piping. CPVC, PEX, and Copper are approved.
- 20
Plastic pipe for hot/cold water:
Explanation
IPC Table 605.4: CPVC (Chlorinated Polyvinyl Chloride) is widely approved for water distribution inside the building.