Topic 05 · Water Supply & Distribution
Set C Questions 21 to 30
- 21
PEX-A tubing fittings typically use:
Explanation
IPC 605.17.2: PEX does not use solvent cement; it connects using mechanical fittings such as crimp rings or expansion fittings.
- 22
Hot water piping pressure rating:
Explanation
IPC 605.4: Water distribution pipe must have a minimum pressure rating of 100 psi at 180°F.
- 23
Solder/flux lead content maximum:
Explanation
IPC 605.14.3: Solder and fluxes used to connect copper water piping must be lead-free, containing a maximum of 0.2 percent lead.
- 24
Pipe/fitting lead content limit:
Explanation
IPC 605.2.1 / Safe Drinking Water Act: The wetted surface area of potable water components must not exceed 0.25 percent lead.
- 25
Purple primer is required for joints on:
Explanation
IPC typically requires a purple primer for PVC joints to visually indicate that primer has been applied prior to solvent cementing.
- 26
Irrigation system backflow protection:
Explanation
IPC 608.17.5: Connections to lawn irrigation systems shall be protected against backflow by an atmospheric vacuum breaker, pressure vacuum breaker assembly, or reduced pressure principle backflow preventer.
- 27
AVB elevation for irrigation:
Explanation
IPC 608.17.4: Atmospheric vacuum breakers must be installed a minimum of 6 inches above the highest piping or outlet.
- 28
PVB elevation for irrigation:
Explanation
IPC 608.17.5: A pressure vacuum breaker assembly must be installed a minimum of 12 inches above the highest piping or outlet downstream.
- 29
RPZ elevation requirement:
Explanation
IPC 608.18.2: RPZ assemblies require that the relief valve discharge port be a minimum of 12 inches above the floor or finished grade.
- 30
Cooling tower makeup protection:
Explanation
Cooling towers contain chemicals and biological hazards, making them a high hazard requiring an RPZ or a full air gap on the supply.