Topic 05 · Water Supply & Distribution
Set D Questions 31 to 40
- 31
Dielectric fittings required when:
Explanation
IPC 605.23: Dielectric fittings or unions are required to prevent galvanic corrosion when joining dissimilar metals, such as copper tubing and galvanized iron pipe.
- 32
Tub/shower cold water minimum:
Explanation
IPC Table 604.5: The minimum pipe size serving a bathtub or a shower is 1/2 inch.
- 33
Hot water circulation is required when the distance from the source exceeds:
Explanation
IPC 607.2: If the distance from the hot water source to a fixture exceeds 50 feet in developed length, a temperature maintenance system is required.
- 34
Hot water insulation thickness:
Explanation
IPC 607.5/IECC: Typically, hot water recirculation piping requires at least 1-inch thick insulation depending on the exact energy code applied.
- 35
Saddle valves are:
Explanation
IPC 605.9: Saddle valves and saddle fittings are prohibited because they puncture the pipe and frequently leak.
- 36
Hose bibbs in freezing areas must be:
Explanation
IPC 608.16.2 / 305.4: To prevent freezing and cross connection, wall hydrants must be frost-proof models with integral backflow protection.
- 37
The minimum test pressure for water distribution systems is:
Explanation
IPC 312.5: Water supply system tests must not be less than the working pressure of the system (or a 50 psi air test).
- 38
The minimum air test pressure for water systems is:
Explanation
IPC 312.5: The air test for water supply distribution systems must be maintained at not less than 50 psi.
- 39
The water supply fixture unit value for a private kitchen sink is:
Explanation
IPC Table 604.3: A private kitchen sink is assigned a water supply fixture unit (WSFU) value of 1.4.
- 40
Cross-connections in potable water systems are prevented by:
Explanation
IPC 608.1: The potable water supply shall be protected against cross-connection by backflow preventers or air gaps.