Topic 09 · Site Hazards & Power Lines
Set A Questions 1 to 10
- 1
What is the minimum clearance from a power line up to 50 kV during crane operation?
Explanation
Ten feet is the baseline clearance for lines up to 50 kV. Above that the clearance increases with voltage.
- 2
How is the required clearance found for a line above 50 kV?
Explanation
Clearance increases with voltage above 50 kV. Where the voltage is unknown, the larger default distance must be assumed.
- 3
What must be assumed about any power line on site?
Explanation
Every line is treated as energised unless the utility confirms it has been, and continues to be, de-energised and visibly grounded at the worksite.
- 4
Does the covering on an overhead power line make it safe?
Explanation
Overhead line covering is weather protection. It is not rated insulation and gives no protection against contact.
- 5
What should a person do if the crane contacts a power line?
Explanation
The ground around the machine may be energised. Nobody approaches or touches the crane until the utility confirms it is safe.
- 6
What should an operator do if the crane contacts a power line?
Explanation
Staying in the cab is safest while the machine may be energised. If fire forces an exit, jump clear without touching machine and ground together, and shuffle away.
- 7
What is step potential?
Explanation
Current spreading through the ground creates a voltage gradient. Taking a normal stride can put a lethal difference across the body.
- 8
How should a person move away from an energised machine?
Explanation
Small shuffling steps keep the feet at nearly the same potential. Striding bridges a voltage difference across the body.
- 9
What is an insulating link on a crane load line?
Explanation
An insulating link is one of several possible measures. It never removes the requirement to maintain clearance.
- 10
What is a proximity alarm on a crane?
Explanation
Alarms can fail or be confused by field conditions. They supplement planning and spotting rather than replacing them.