Fixtures, Faucets & Clearances

Chapter 4 of the 2024 International Plumbing Code (IPC) establishes the foundational rules for plumbing fixtures, faucets, and fixture fittings. Its primary purpose is to ensure that buildings have the minimum required sanitary facilities based on their occupancy type, and to mandate that all fixtures are manufactured from safe, durable materials and installed in a way that prevents contamination, scalding, and backflow while promoting accessibility and water conservation.

  • Occupancy Determines Fixtures: The absolute minimum number of plumbing fixtures a building needs is strictly dictated by Table 403.1 based on its use classification and occupant load.
  • Separation of Sexes: Separate facilities for males and females are generally required, with specific exceptions for small occupancy loads, dwelling units, and single-user accessible toilet rooms.
  • Clearance is King: Specific measurements (like 15 inches from center to wall, and 21 inches of front clearance) are strictly enforced for toilets, bidets, and urinals to ensure usable space.
  • Temperature Control: To prevent scalding, maximum water temperatures are heavily regulated (e.g., 120°F for showers, bathtubs, and public handwashing; 110°F for bidets).
  • Backflow Prevention: Every water supply line to a fixture must be protected against backflow via air gaps, air breaks, or approved backflow preventers.
  • Public Access Restrictions: Public restrooms cannot be routed through kitchens or storage rooms, and doors cannot open directly into commercial food prep areas.
  • Water Closet: The technical plumbing code term for a toilet.
  • Lavatory: A sink that is specifically designed and used for washing hands and face, typically located in a bathroom.
  • Urinal: A plumbing fixture designed primarily for receiving and disposing of urine, typically used by males.
  • Bidet: A fixture used for washing the lower body, often installed next to a toilet.
  • Flushometer Valve: A specialized valve attached directly to a pressurized water supply that flushes a toilet or urinal without using a storage tank.
  • Air Gap: A physical, unobstructed vertical space between the water supply outlet and the flood rim of a receiving vessel, used to absolutely prevent backflow.
  • Slip Joint: A plumbing connection made using a compression nut and a specialized gasket or washer, commonly found on traps under sinks.
  • Cultured Marble: A manufactured synthetic material used for vanity tops and sinks that mimics the look of natural stone.
  • Volute: The inner casing of a centrifugal pump, such as those used in whirlpool bathtubs, which must be able to drain completely.

Exam Prep & Tips

  • Clearances are guaranteed questions: Always remember 15 inches from the center of a toilet/urinal to a wall, and 21 inches of clearance directly in front.
  • Occupancy exceptions: Memorize the thresholds where separate male/female restrooms are not required: occupant loads of 15 or fewer (general/tenant), 25 or fewer (business), and 100 or fewer (mercantile).
  • Fractions in Calculations: When calculating fixture counts based on occupant loads, always round up to the next whole number for each occupancy classification before summing them up.
  • Showers: Know that shower pan liners must slope at exactly 2% (1/4 inch per foot) toward the drain, and the walls must be waterproofed up to 70 inches above the drain.

Prohibited Practices

  • Concealed Traps: Water closets with concealed trap seals are explicitly prohibited.
  • Unventilated Toilets: Water closets with unventilated spaces are prohibited.
  • Siphonage Toilets: Any toilet that allows bowl contents to siphon back into the tank is strictly prohibited.
  • Trough Urinals: Trough-style urinals are completely prohibited.
  • Food Prep Areas: Restrooms shall not open directly into a room used for public food preparation.
  • Restroom Routes: Public restrooms cannot be accessed by walking through kitchens, storage rooms, or closets.
  • Drinking Fountains: You shall not install a drinking fountain, water cooler, or dispenser inside a public restroom.
  • Locking Egress Doors: Multi-occupant restroom egress doors cannot be lockable from the inside (unless explicitly for authorized personnel only and capable of being unlocked from the outside).
  • Mental Health Centers: Exposed pipes, traps, and standard fixture mounting are prohibited; everything must be concealed and fixtures bolted through walls.
  • Shared Flush Valves: A single flushing device (flushometer) shall not serve more than one fixture.

Most Tested Numbers

Clearances & Distances:

  • 15 inches: Minimum distance from center of toilet, urinal, or bidet to side wall/partition.
  • 30 inches: Minimum distance center-to-center between adjacent toilets/urinals.
  • 21 inches: Minimum clearance space in front of a toilet, urinal, or bidet.
  • 30 inches (width) x 60 inches (depth): Minimum compartment size for a floor-mounted toilet.
  • 30 inches (width) x 56 inches (depth): Minimum compartment size for a wall-hung toilet.
  • 12 inches: Maximum starting height for a urinal privacy partition from the floor.
  • 60 inches: Minimum height a urinal partition must reach above the floor.
  • 18 inches: Minimum distance a urinal partition must stick out from the wall.
  • 500 feet: Maximum travel distance to a required public/employee restroom (or drinking fountain) in standard buildings.
  • 300 feet: Maximum travel distance to central restrooms (or service sinks) in mall buildings.
  • 1 story: Maximum vertical travel (up or down) to reach a required public/employee restroom.

Temperatures (Maximums):

  • 110°F (43°C): Maximum water temperature for bidets.
  • 120°F (49°C): Maximum water temperature for individual showers, tub-showers, public lavatories (hand washing), shampoo sinks, footbaths, and pedicure baths.

Pipe Sizes & Weights:

  • 1-1/4 inches: Minimum waste outlet size for a lavatory (bathroom sink).
  • 1-1/2 inches: Minimum waste outlet size for bathtubs, food waste disposers (domestic and commercial), laundry trays, showers, and kitchen sinks.
  • 2 inches: Minimum size for an automatic clothes washer standpipe trap and floor drain outlets.
  • 3 inches: Minimum size for the branch/stack serving a washer standpipe, and floor drains in public laundries.
  • 4-inch by 3-inch: Acceptable dimensions for a closet bend (toilet drain fitting).
  • 12 ounces per square foot: Minimum weight for sheet copper used in general applications and shower pans.
  • 10 ounces per square foot: Minimum weight for sheet copper used as a flush tank lining.
  • 4 pounds per square foot: Minimum weight for sheet lead used for pans.

Shower Measurements:

  • 900 square inches: Minimum interior cross-sectional area of a shower compartment.
  • 30 inches: Minimum interior dimension of a shower compartment (can be 25" if total area is over 1300 sq inches).
  • 70 inches: Minimum height above the drain for waterproof wall materials in a shower or tub-shower.
  • 22 inches: Minimum clear width for a shower access/egress opening.
  • 2 inches: Minimum height a shower pan liner must turn up the wall above the finished threshold.
  • 1 inch: Distance above the threshold where you are finally allowed to nail/puncture a shower liner.

Other Measurements:

  • 20 inches: Amount of rim space on a group wash fixture that counts as "one" lavatory.
  • 1 inch: Minimum distance a fill valve backflow preventer must be installed above the flush tank overflow pipe.
  • 15 occupants: The magic number. If a business/mercantile space has 15 or fewer occupants, separate male/female restrooms are not required, drinking fountains are not required, and service sinks are not required.
  • 100 occupants: Threshold where mercantile spaces don't need separate sex restrooms.
  • 25 occupants: Threshold where business spaces don't need separate sex restrooms.

Section 401 - General

  • 401.1 Scope: This chapter outlines the rules for what fixtures are made of, how they are designed, how they are installed, and the absolute minimum number of fixtures you must put in a building based on what the building is used for.
  • 401.2 Prohibited fixtures and connections: You cannot install toilets with hidden traps or unventilated spaces. If a toilet doesn't thoroughly wash its walls when flushed, it's out. Toilets that can suck waste back into the tank (siphonage) are strictly illegal. Also, trough-style urinals are totally banned.
  • 401.3 Water conservation: All fixtures must comply with the maximum flow rates and flush volumes set elsewhere in the code (Section 604.4) to save water.

Section 402 - Fixture Materials

  • 402.1 Quality of fixtures: Plumbing fixtures have to be made of approved, smooth, waterproof materials without defects or hidden areas where gunk can build up. If it's porcelain enameled, it must be acid-resistant.
  • 402.2 Materials for specialty fixtures: If the code doesn't specifically mention a material for a unique fixture, you must use stainless steel, soapstone, chemical stoneware, plastic, or line it with heavy-duty metals like lead, copper alloys, or corrosion-resistant steel.
  • 402.3 Sheet copper: General application sheet copper must weigh at least 12 ounces per square foot.
  • 402.4 Sheet lead: Sheet lead used for pans (like shower bases) must weigh at least 4 pounds per square foot and be coated with asphalt paint to protect it.

Section 403 - Minimum Plumbing Facilities

  • 403.1 Minimum number of fixtures: You have to look at Table 403.1 to figure out exactly how many toilets, sinks, and fountains a building needs. The Building Code tells you how many people are in the building.
  • 403.1.1 Fixture calculations: To figure out how many fixtures men and women get, chop the total building population in half. Apply the ratios from the table. If you end up with a fraction (like 2.3 toilets), always round up to the next whole number (3 toilets). If a building has mixed uses, calculate the fractions for each use, add those fractions together first, and then round up. Exceptions: You don't have to divide 50/50 if you have approved statistical proof the demographic is different. Gender-neutral multi-user restrooms calculate at 100% of the total load.
  • 403.1.2 Fixtures in single-user toilet facilities and bathing rooms: Single-user, family, or assisted-use bathrooms count toward your total required fixtures. You deduct them from the male/female requirements equally, but they must be labeled for use by all sexes.
  • 403.1.3 Lavatory distribution: If you have multiple restrooms, the hand sinks must be distributed proportionally to the number of toilets for each sex.
  • 403.2 Separate facilities: Generally, men and women must have separate restrooms. Exceptions: You don't need separate restrooms in homes/apartments, places with 15 or fewer total people, stores (mercantile) with 100 or fewer people, offices (business) with 25 or fewer people, or if you use compliant single-user gender-neutral restrooms.
  • 403.3 Employee and public toilet facilities: The public and the employees both need restrooms. You can combine them or keep them separate. Exceptions: Unattended parking garages and quick-transaction spots (like tiny drive-thrus under 300 sq ft) don't need public restrooms.
  • 403.3.1 Access: The path to the public restroom cannot go through a kitchen, storage room, or closet. It must be accessible whenever the building is occupied.
  • 403.3.2 Prohibited location: Restroom doors absolutely cannot open directly into a room where food is being prepared for the public.
  • 403.3.3 Location in occupancies other than malls: You can't make people walk more than 500 feet, or go up/down more than one story, to reach a restroom. (Factories and warehouses can stretch this if the code official approves).
  • 403.3.4 Location in malls: Malls are stricter. The travel distance is max 300 feet, and no more than one story up or down. Distance is measured from the main entrance of a tenant space.
  • 403.3.5 Pay facilities: If you install pay toilets, they don't count toward your minimum required fixtures. The required ones must be free.
  • 403.3.6 Door locking: Multi-occupant restrooms cannot have a lock on the main exit door. Exception: It's allowed only if authorized personnel can lock/unlock it with a key from both the inside and outside, and it meets building code egress rules.
  • 403.4 Signage: Restrooms must have highly visible signs indicating if they are for men, women, or all sexes. Accessible restrooms need ADA-compliant signs.
  • 403.4.1 Directional signage: If the restroom isn't obvious, you must put up directional signs in lobbies or corridors.
  • 403.5 Drinking fountain location: Individual stores don't need their own drinking fountain if there is a public one within 500 feet (or 300 feet in a mall) and within one story.
  • 403.6 Service sink location: Same as drinking fountains. Individual mall stores don't need a mop sink if there's an accessible central one within 300 feet and within one story.

Section 404 - Accessible Plumbing Facilities

  • 404.1 Where required: You must install accessible (ADA-compliant) fixtures according to the Building Code (Chapter 11).
  • 404.2 Accessible fixture requirements: Install them strictly according to ICC A117.1 standards.
  • 404.3 Exposed pipes and surfaces: Any hot/cold water pipes or drain pipes under accessible sinks must be wrapped or shielded so wheelchair users don't burn or scrape their legs.

Section 405 - Installation of Fixtures

  • 405.1 Water supply protection: Every single fixture must be installed to prevent dirty water from flowing backward into the clean water supply.
  • 405.2 Access for cleaning: Install fixtures so plumbers and janitors can easily clean around them.
  • 405.3 Setting: Fixtures must be installed level and square to the walls.
  • 405.3.1 Water closets, urinals, lavatories and bidets: The "Clearance Rule." A toilet, urinal, or bidet must be at least 15 inches from its center to any wall or partition. If they are side-by-side, they must be 30 inches center-to-center. You need 21 inches of clear walking space in front of them. Toilet stalls must be at least 30" wide x 60" deep for floor toilets, or 30" x 56" deep for wall-hung toilets. Exception: Children's accessible toilets can be 12 inches from center to wall.
  • 405.3.2 Public lavatories: Hand sinks must be in the exact same room as the toilets.
  • 405.3.3 Location of fixtures and piping: Don't install pipes or fixtures where they block windows, doors, or emergency exits.
  • 405.3.4 Water closet compartment: Every public toilet must be in its own private stall with a door. Exceptions: Single-user lockable rooms, child daycares (can have one unenclosed toilet), and prison housing areas.
  • 405.3.5 Urinal partitions: Public urinals need privacy partitions. They must be 30 inches apart center-to-center. The partition must start no higher than 12 inches off the floor and go up to at least 60 inches. It must stick out from the wall at least 18 inches, or 6 inches past the front lip of the urinal.
  • 405.4 Floor and wall drainage connections: Floor toilets connect to the drain via a closet flange and a sealing gasket (like a wax ring). Wall-hung toilets connect with special nipples and gaskets, bolted to a hidden wall carrier.
  • 405.4.1 Floor flanges: Brass/copper flanges must be 1/8" thick. Plastic or cast iron must be 1/4" thick. Lead flanges must weigh 1 lb 9 oz. Use corrosion-resistant bolts.
  • 405.4.2 Securing floor outlet fixtures: Floor fixtures must be bolted securely to the flange using corrosion-resistant bolts (brass/stainless).
  • 405.4.3 Securing wall-hung bowls: Wall-hung toilets must be supported by a heavy-duty metal carrier bolted inside the wall framing. The toilet hangs on the carrier, not the pipe, so no strain is put on the plumbing system.
  • 405.5 Pumped waste: Fixtures with built-in waste pumps (like macerating toilets) must meet ASME standards and be installed per manufacturer instructions.
  • 405.6 Watertight joints: Any place a fixture meets a wall or floor must be caulked and sealed watertight.
  • 405.7 Plumbing in mental health centers: Strict safety rule: No exposed pipes or traps. Everything must be hidden, and fixtures bolted directly through the walls to prevent self-harm or vandalism.
  • 405.8 Design of overflows: If a fixture has an overflow hole (like a bathroom sink), it must be designed so water drains out properly and doesn't get stuck rotting inside the overflow channel.
  • 405.8.1 Connection of overflows: Overflows must dump into the drain before the P-trap (so sewer gas doesn't come out the overflow). Exception: Toilet/urinal flush tank overflows dump straight into the bowl.
  • 405.9 Slip-joint connections: Slip joints are only allowed on the trap inlet, trap outlet, and within the trap seal itself. If you hide a slip joint behind a wall or under a tub, you must install an access panel at least 12 inches by 12 inches so plumbers can reach it later.
  • 405.10 Design and installation: Manufactured and custom-built fixtures must meet strict structural design standards.

Section 406 - Automatic Clothes Washers

  • 406.1 Water connection: The water hoses hooking up to a washing machine must have built-in air gaps or backflow preventers.
  • 406.2 Waste connection: Washer drains must discharge through an air break into a standpipe or a laundry sink. The standpipe trap and drain pipe must be at least 2 inches in diameter, and that 2-inch drain must dump into a larger branch or stack that is at least 3 inches in diameter.

Section 407 - Bathtubs

  • 407.1 Approval: Tubs must meet specific manufacturing standards.
  • 407.2 Bathtub waste outlets and overflows: Tubs need a drain hole at least 1-1/2 inches wide with a stopper. The overflow pipe connects above the P-trap.
  • 407.3 Glazing: Any glass (windows/doors) near or in a bathtub enclosure must be safety glass (tempered) per the Building Code.
  • 407.4 Bathtub enclosure: Shower/tub doors must meet safety standards.

Section 408 - Bidets

  • 408.1 Approval: Bidets must meet specific manufacturing standards.
  • 408.2 Water connection: Bidets need serious backflow protection (air gap or vacuum breakers) because the water sprayer sits below the flood rim.
  • 408.3 Bidet water temperature: The water shooting out of a bidet cannot be hotter than 110°F (43°C), controlled by a specialized limiting valve.

Section 409 - Dishwashing Machines

  • 409.1 Approval: Commercial and residential dishwashers must meet NSF sanitation standards.
  • 409.2 Water connection: Supply lines must have air gaps or backflow preventers.
  • 409.3 Waste connection (Commercial): Commercial units have strict indirect waste requirements covered in Chapter 8.
  • 409.4 Residential dishwasher waste connection: A home dishwasher drain hose must loop up and fasten securely under the countertop, then connect to a wye-fitting on the sink drain, hook into a garbage disposal, or dump into a standpipe via an air break.

Section 410 - Drinking Fountains

  • 410.1 Approval: Fountains must meet NSF standards for drinking water and UL standards if refrigerated.
  • 410.2 Small occupancies: You don't need a drinking fountain if the building has 15 or fewer people.
  • 410.3 High and low fountains: When fountains are required, you must install at least two: one low (for wheelchairs) and one high (for standing folks). You can use a combo unit to satisfy this.
  • 410.3.2 More than the minimum: If you install extra fountains, split them 50/50 between high and low.
  • 410.4 Substitution: If a restaurant gives out free water, they don't need a drinking fountain. In other buildings, you can swap out up to 50% of the required drinking fountains for regular water dispensers.
  • 410.5 Prohibited location: Never install a drinking fountain inside a public restroom.

Section 411 - Emergency Showers and Eyewash Stations

  • 411.1 Approval: Must meet ISEA safety standards.
  • 411.2 Waste connection: You are actually not required to hook up a drain for emergency showers/eyewashes. Let it flood the floor; safety comes first.
  • 411.3 Water supply: The water must be controlled by a specific thermostatic mixing valve so you don't freeze or boil the person using it during an emergency.

Section 412 - Faucets and Fixture Fittings

  • 412.1 Approval: Faucets must meet standards, and drinking water faucets must be lead-free (NSF 61). Waste fittings must be proper drainage materials.
  • 412.2 Hand showers: Handheld shower wands must have backflow protection (so sitting bathwater doesn't get sucked into the wand).
  • 412.3 Individual shower valves: Every shower must have a balanced-pressure, thermostatic, or combination mixing valve right at the shower. It must have a mechanical limit stop set to a maximum of 120°F (49°C) to prevent scalding.
  • 412.4 Multiple (gang) showers: Group showers can share one massive mixing valve, or have individual valves. Either way, water cannot exceed 120°F (49°C).
  • 412.5 Bathtub valves: Bathtub fillers also need a temperature-limiting device locked at 120°F (49°C) max. Plumbers must be able to access this device for future repairs.
  • 412.6 Hose-connected outlets: Any faucet with a threaded hose connection needs a vacuum breaker.
  • 412.7 Flow-reduction devices: You can use a temperature-actuated flow reduction device to stop scalding (it shuts off water if it gets too hot), but you can't use it as a replacement for the primary shower mixing valve.
  • 412.8 Transfer valves: Bath/shower diverter valves must meet standards.
  • 412.9 Personal hygiene devices: Bidet-style toilet seats must meet plumbing standards.
  • 412.10 Head shampoo sink faucets: Salon shampoo bowls must be limited to 120°F (49°C) max and must have check valves so hot and cold water don't cross over in the pipes.
  • 412.11 Prerinse spray valves: Restaurant dish-sprayers must meet standards.
  • 412.12 Electrically heated/cooled dispensers: Hot/cold water dispensers must meet ASSE standards.

Section 413 - Floor and Trench Drains

  • 413.1 Approval: Must meet ASME standards.
  • 413.2 Floor drains: Drains must have removable strainers, be capable of being cleaned, and have ready access.
  • 413.3 Size of floor drains: The absolute minimum drain pipe size for a floor drain is 2 inches.
  • 413.4 Public laundries: Laundromats and apartment washrooms must have a floor drain positioned to drain the whole room. This specific drain must be at least 3 inches in diameter.

Section 414 - Floor Sinks

  • 414.1 Approval: Sanitary floor sinks (used mostly in commercial kitchens for indirect waste) must meet standards.

Section 415 - Flushing Devices for Water Closets and Urinals

  • 415.1 Flushing devices required: Everything that flushes needs a flushometer valve, a flushometer tank, or a standard gravity tank that delivers enough water to clean the bowl and refill the trap.
  • 415.1.1 Separate for each fixture: One flush valve = one toilet. No sharing.
  • 415.2 Flushometer valves: These commercial-style flush valves need vacuum breakers to prevent backflow. You must leave access to the vacuum breaker. They only work if the building has high enough water pressure.
  • 415.3 Flush tanks: Standard toilet tanks must automatically refill and shut off.
  • 415.3.1 Fill valves: The fill valve (ballcock) inside the tank must be anti-siphon. The critical level mark on the fill valve must sit at least 1 inch above the top of the overflow pipe.
  • 415.3.2 Overflows in flush tanks: Tanks must have an overflow tube that dumps down into the toilet bowl, big enough to handle the water if the fill valve breaks and stays open.
  • 415.3.3 Sheet copper: Copper linings for flush tanks must be 10 oz per sq ft.
  • 415.3.4 Access required: All moving parts inside a toilet tank must be accessible for repair.
  • 415.4 Flush pipes and fittings: Must be made of non-rusting (nonferrous) metal or plastic.

Section 416 - Food Waste Disposer Units

  • 416.1 Approval: Garbage disposals must meet UL standards. Note: Adding a disposal doesn't increase your drainage fixture unit (DFU) load calculations.
  • 416.2 Domestic disposers: Home disposals need a drain at least 1-1/2 inches wide.
  • 416.3 Commercial disposers: Restaurant disposals also need a 1-1/2 inch drain, but they must have their own separate P-trap; they cannot share a trap with a neighboring sink.
  • 416.4 Water supply: Disposals must be piped with cold water (to solidify grease so it grinds up) and have backflow protection.

Section 417 - Garbage Can Washers

  • 417.1 Water connection: Must have heavy-duty backflow prevention.
  • 417.2 Waste connection: They need their own trap and a removable basket strainer to catch massive chunks of trash before it hits the sewer.

Section 418 - Laundry Trays

  • 418.1 Approval: Utility sinks must meet standards.
  • 418.2 Waste outlet: Must have a drain at least 1-1/2 inches wide and a crossbar/strainer so you don't drop socks down the pipe.

Section 419 - Lavatories

  • 419.1 Approval: Hand sinks must meet standards. If using a massive group wash sink (like in stadiums), every 20 inches of rim space counts as "one" lavatory for your fixture count.
  • 419.2 Cultured marble: Synthetic marble sinks must meet standards.
  • 419.3 Lavatory waste outlets: Bathroom sink drains can be slightly smaller: minimum 1-1/4 inches wide, and must have a pop-up stopper or strainer.
  • 419.4 Movable lavatory systems: Must comply with specific standards.
  • 419.5 Tempered water for public facilities: Public restrooms must supply "tempered" water (warm water, controlled by a mixing valve) to the hand sinks. It cannot just be purely cold or dangerously hot.
  • 419.6 Soap dispenser: Public sinks must have soap dispensers.

Section 420 - Manual Food and Beverage Dispensing Equipment

  • 420.1 Approval: Soda fountains and similar equipment must meet NSF standards.

Section 421 - Showers

  • 421.1 Approval: Prefab showers and valves must meet standards.
  • 421.2 Water supply riser: The pipe running up the wall to the showerhead must be strapped and anchored securely to the wall framing.
  • 421.3 Shower waste outlet: Shower drains must be at least 1-1/2 inches wide and have a removable strainer that is at least 3 inches across. The floor must slope to the drain.
  • 421.4 Shower compartments: A shower stall must have at least 900 square inches of floor space, and you must be able to fit a 30-inch circle inside it (measured to the finished wall). Exception: It can be 25 inches narrow only if the total area is massive (over 1,300 sq inches).
  • 421.4.1 Floor and wall area: Shower walls must be smooth, waterproof, and non-corrosive. The waterproofing must go up to at least 70 inches above the drain, and 6 feet above the bathroom floor level.
  • 421.4.2 Access: The opening to step into the shower must be at least 22 inches wide.
  • 421.5 Shower floors or receptors: Shower floors must be totally waterproof.
  • 421.5.1 Support: Shower pans need a smooth, solid structural base underneath them.
  • 421.5.2 Shower lining: If building a custom tile shower, you must install a waterproof liner (pan). The liner must turn up the walls at least 2 inches above the curb (threshold). You cannot nail or puncture this liner anywhere lower than 1 inch above the finished threshold. The floor mud over the liner must be pitched toward the drain at exactly 2% (1/4 inch per foot). The liner must be water-tested before tiling.
  • 421.5.2.1 to 421.5.2.6: Details on acceptable shower liner materials: PVC, CPE (chlorinated polyethylene), 4 lb sheet lead, 12 oz sheet copper, and specific liquid-applied or sheet-applied bonded membranes.
  • 421.6 Glazing: Glass in shower doors/walls must be safety glass.

Section 422 - Sinks

  • 422.1 Approval: Kitchen and utility sinks must meet standards.
  • 422.2 Sink waste outlets: Minimum drain size is 1-1/2 inches, and needs a strainer.
  • 422.3 Movable sink systems: Must comply with specific standards.

Section 423 - Specialty Plumbing Fixtures

  • 423.1 Water connections: Weird things like baptisteries, aquariums, and lily pools need backflow preventers on their water supply.
  • 423.2 Approval: Custom specialty fixtures must be approved by the local code official.
  • 423.3 Footbaths and pedicure baths: Salon footbaths must have a thermostatic valve limiting the water to 120°F (49°C) to prevent burning feet.

Section 424 - Urinals

  • 424.1 Approval: Urinals must meet water consumption and flush performance standards.
  • 424.2 Substitution for water closets: You can swap out men's toilets for urinals, but there are limits. In assembly spaces (theaters, stadiums) and schools, up to 67% of the required male toilets can be replaced with urinals. Everywhere else, you can only substitute up to 50%.

Section 425 - Water Closets

  • 425.1 Approval: Toilets must meet flush standards and water conservation rules.
  • 425.2 Water closets for public facilities: Public restrooms must use elongated toilet bowls (the long oval shape, not the round ones).
  • 425.3 Water closet seats: Public toilet seats must be made of smooth, nonabsorbent material and must have an open-front (the horseshoe shape).
  • 425.4 Water closet connections: You are allowed to use a 4x3 closet bend (a pipe fitting that transitions a 3-inch pipe up to a 4-inch toilet flange).

Section 426 - Whirlpool Bathtubs

  • 426.1 Approval: Jacuzzi-style tubs must meet safety and plumbing standards.
  • 426.2 Installation: Follow the manufacturer's directions. The circulation pump must be installed higher than the weir (water seal level) of the tub's P-trap.
  • 426.3 Drain: The pump casing (volute) and all the jet piping must be sloped so that when you empty the tub, every drop of water drains out of the pipes so bacteria doesn't grow.
  • 426.4 Suction fittings: The intake grates for the jets must meet anti-entrapment safety standards.
  • 426.5 Access to pump: You must leave an access door to reach the whirlpool pump. It has to be at least 12x12 inches. If the pump is shoved way back (more than 2 feet away), the access door has to be at least 18x18 inches.
  • 426.6 Whirlpool enclosure: Any glass around the whirlpool must meet safety glazing standards.

TABLE 403.1 - MINIMUM NUMBER OF REQUIRED PLUMBING FIXTURES(a) (a) (See Sections 403.1.1 and 403.2)

NO.CLASSIFICATIONDESCRIPTIONWATER CLOSETS (MALE)WATER CLOSETS (FEMALE)LAVATORIES (MALE)LAVATORIES (FEMALE)BATHTUBS/SHOWERSDRINKING FOUNTAIN (SEE SECTION 410)OTHER
1AssemblyTheaters and other buildings for the performing arts and motion pictures(d) (d)1 per 1251 per 651 per 2001 per 200-1 per 5001 service sink
1AssemblyNightclubs, bars, taverns, dance halls and buildings for similar purposes(d) (d)1 per 401 per 401 per 751 per 75-1 per 5001 service sink
1AssemblyRestaurants, banquet halls and food courts(d) (d)1 per 751 per 751 per 2001 per 200-1 per 5001 service sink
1AssemblyCasino gaming areas1 per 100 for the first 400 and 1 per 250 for the remainder exceeding 4001 per 50 for the first 400 and 1 per 150 for the remainder exceeding 4001 per 250 for the first 750 and 1 per 500 for the remainder exceeding 7501 per 250 for the first 750 and 1 per 500 for the remainder exceeding 750-1 per 1,0001 service sink
1AssemblyAuditoriums without permanent seating, art galleries, exhibition halls, museums, lecture halls, libraries, arcades and gymnasiums(d) (d)1 per 1251 per 651 per 2001 per 200-1 per 5001 service sink
1AssemblyPassenger terminals and transportation facilities(d) (d)1 per 5001 per 5001 per 7501 per 750-1 per 1,0001 service sink
1AssemblyPlaces of worship and other religious services(d) (d)1 per 1501 per 751 per 2001 per 200-1 per 1,0001 service sink
1AssemblyColiseums, arenas, skating rinks, pools and tennis courts for indoor sporting events and activities(f) (f)1 per 75 for the first 1,500 and 1 per 120 for the remainder exceeding 1,5001 per 40 for the first 1,520 and 1 per 60 for the remainder exceeding 1,5201 per 2001 per 150-1 per 1,0001 service sink
1AssemblyStadiums, amusement parks, bleachers and grandstands for outdoor sporting events and activities(f) (f)1 per 75 for the first 1,500 and 1 per 120 for the remainder exceeding 1,5001 per 40 for the first 1,520 and 1 per 60 for the remainder exceeding 1,5201 per 2001 per 150-1 per 1,0001 service sink
2BusinessBuildings for the transaction of business, nonmedical professional services, other services involving merchandise, office buildings, banks, light industrial and similar uses1 per 25 for the first 50 and 1 per 50 for the remainder exceeding 501 per 25 for the first 50 and 1 per 50 for the remainder exceeding 501 per 40 for the first 80 and 1 per 80 for the remainder exceeding 801 per 40 for the first 80 and 1 per 80 for the remainder exceeding 80-1 per 1001 service sink(e) (e)
2BusinessAmbulatory care facilities and outpatient clinics1 per 25 for the first 50 and 1 per 50 for the remainder exceeding 501 per 25 for the first 50 and 1 per 50 for the remainder exceeding 501 per 501 per 50-1 per 1001 service sink per floor
3EducationalEducational facilities1 per 501 per 501 per 501 per 50-1 per 1001 service sink
4Factory and industrialStructures in which occupants are engaged in work fabricating, assembly or processing of products or materials1 per 1001 per 1001 per 1001 per 100-1 per 4001 service sink
5InstitutionalAlcohol and drug centers(b) (b)\nCongregate care facilities(b) (b)\nGroup homes(b) (b)\nHalfway houses(b) (b)\nSocial rehabilitation facilities(b) (b)\nFoster care facilities(b) (b)1 per 10 care recipients1 per 10 care recipients1 per 10 care recipients1 per 10 care recipients1 per 8 care recipients--
5InstitutionalAssisted living and residential board and care facilities with care recipients who receive custodial care - Sleeping units for care recipient(c) (c)1 per 2 sleeping units1 per 2 sleeping units1 per 2 sleeping units1 per 2 sleeping units1 per 8 sleeping units--
5InstitutionalAssisted living and residential board and care facilities with care recipients who receive custodial care - Dwelling units for care recipients1 per dwelling unit1 per dwelling unit1 per dwelling unit1 per dwelling unit1 per dwelling unit-1 kitchen sink per dwelling unit
5InstitutionalAssisted living and residential board and care facilities with care recipients who receive custodial care - Employee facilities1 per 60 care recipient units1 per 60 care recipient units1 per 60 care recipient units1 per 60 care recipient units-1 per 1001 service sink per floor
5InstitutionalAssisted living and residential board and care facilities with care recipients who receive custodial care - Visitor facilities1 per 75 care recipient units.1 per 75 care recipient units.1 per 75 care recipient units1 per 75 care recipient units---
5InstitutionalNursing homes(b) (b) - Sleeping units for care recipients(c) (c)1 per 2 care recipient sleeping units1 per 2 care recipient sleeping units1 per 2 care recipient sleeping units1 per 2 care recipient sleeping units1 per 8 care recipient sleeping units--
5InstitutionalNursing homes(b) (b) - Employee facilities1 per 60 care recipient units1 per 60 care recipient units1 per 60 care recipient units1 per 60 care recipient units-1 per 1001 service sink per floor
5InstitutionalNursing homes(b) (b) - Visitor facilities1 per 75 care recipient units1 per 75 care recipient units1 per 75 care recipient sleeping rooms1 per 75 care recipient sleeping rooms---
5InstitutionalHospitals - Sleeping units for care recipients1 per care recipient sleeping unit1 per care recipient sleeping unit1 per care recipient sleeping unit1 per care recipient sleeping unit1 per 100 care recipient sleeping units--
5InstitutionalHospitals - Care recipient treatment areas1 per 25 care recipient treatment rooms1 per 25 care recipient treatment rooms1 per 50 care recipient treatment rooms1 per 50 care recipient treatment rooms1 per 100 care recipient sleeping units1 per 100-
5InstitutionalHospitals - Employee facilities1 per 25 care recipient treatment rooms1 per 25 care recipient sleeping units or treatment room1 per 50 care recipient treatment rooms1 per 50 care recipient treatment rooms-1 per 1001 service sink per floor
5InstitutionalHospitals - Visitor facilities1 per 75 care recipient sleeping units or treatment room1 per 75 care recipient sleeping units or treatment room1 per 50 care recipient sleeping room or treatment room1 per 50 care recipient sleeping room or treatment room-1 per 500-
5InstitutionalPrisons(b) (b)1 per cell1 per cell1 per cell1 per cell1 per 151 per 1001 service sink
5InstitutionalReformatories, detention centers and correctional centers(b) (b) - Cells1 per 151 per 151 per 151 per 151 per 151 per 1001 service sink
5InstitutionalReformatories, detention centers and correctional centers(b) (b) - Congregate Living Facilities1 per 151 per 151 per 151 per 151 per 151 per 1001 service sink
5InstitutionalReformatories, detention centers and correctional centers(b) (b) - Employees1 per 251 per 251 per 351 per 35-1 per 100-
5InstitutionalAdult day care and child day care1 per 151 per 151 per 151 per 1511 per 1001 service sink
6MercantileRetail stores, service stations, shops, salesrooms, markets and shopping centers1 per 5001 per 5001 per 7501 per 750-1 per 1,0001 service sink(e) (e)
7ResidentialHotels, motels, boarding houses (transient)1 per dwelling or sleeping unit1 per dwelling or sleeping unit1 per dwelling or sleeping unit1 per dwelling or sleeping unit1 per dwelling or sleeping unit-1 service sink
7ResidentialDormitories, fraternities, sororities and boarding houses (not transient)1 per 101 per 101 per 101 per 101 per 81 per 1001 service sink
7ResidentialApartment house1 per dwelling unit or sleeping unit1 per dwelling unit or sleeping unit1 per dwelling unit or sleeping unit1 per dwelling unit or sleeping unit1 per dwelling unit or sleeping unit-1 kitchen sink per dwelling unit; 1 automatic clothes washer connection per 20 dwelling units
7ResidentialCongregate living facilities with 16 or fewer care recipients receiving custodial care1 per 101 per 101 per 101 per 101 per 8-1 kitchen sink
7ResidentialOne- and two-family dwellings and lodging houses with five or fewer guestrooms1 per dwelling unit1 per dwelling unit1 per dwelling unit1 per dwelling unit1 per dwelling unit-1 kitchen sink per dwelling unit; 1 automatic clothes washer connection per dwelling unit
8StorageStructures for the storage of goods, warehouses, storehouse and freight depots. Low and Moderate Hazard.1 per 1001 per 1001 per 1001 per 100-1 per 1,0001 service sink

a. The fixtures shown are based on one fixture being the minimum required for the number of persons indicated or any fraction of the number of persons indicated. The number of occupants shall be determined by the International Building Code.\n b. Toilet facilities for employees shall be separate from facilities for inmates or care recipients.\n c. A single-user toilet facility with one water closet and one lavatory serving not more than two adjacent care recipient sleeping units shall be permitted provided that each patient sleeping unit has direct access to the toilet room and provision for privacy for the toilet room user is provided.\n d. The occupant load for seasonal outdoor seating and entertainment areas shall be included when determining the minimum number of facilities required.\n e. For business and mercantile classifications with an occupant load of 15 or fewer, service sinks shall not be required.\n f. The required number and type of plumbing fixtures for indoor and outdoor public swimming pools shall be in accordance with Section 609 of the International Swimming Pool and Spa Code.\n