Topic 12 · Nonpotable Water Systems
Nonpotable Water Systems
Chapter 13 regulates the materials, design, construction, and installation of nonpotable water systems, which include on-site water reuse, rainwater collection, and reclaimed water from treatment facilities. Its primary goal is to safely reduce potable water demand by providing strict guidelines for the storage, treatment, distribution, and cross-connection prevention of nonpotable water to protect public health and the main drinking water supply.
- Protect the Potable Supply: Anytime a potable water system connects to a nonpotable system (like for makeup water), it must be protected against backflow.
- Mandatory Signage: All nonpotable outlets and storage tanks must be clearly labeled with specific "CAUTION: NONPOTABLE WATER - DO NOT DRINK" signage.
- Strict Filtration for Flushing: Nonpotable water used for flushing toilets and urinals must be filtered to at least 100 microns (except reclaimed water).
- Trenching Rules: Underground nonpotable pipes generally need a 5-foot horizontal separation from building sewers and potable pipes, with specific exceptions for sleeving or vertical elevation.
- Max Pressure: Nonpotable distribution systems exceeding 80 psi static pressure must have a pressure-reducing valve installed.
- No Blackwater Reuse: Wastewater containing urine, feces, or heavy food/chemical waste (kitchen sinks, dishwashers) cannot be used in on-site nonpotable reuse systems.
- Nonpotable Water: Water that is not safe for drinking, personal, or culinary use, but can be used for things like flushing toilets or irrigation.
- Reclaimed Water: Wastewater that has been treated by an off-site wastewater treatment facility to a standard suitable for specific beneficial uses.
- On-site Nonpotable Water Reuse System: A system that collects waste discharge from specific clean-ish sources (like bathtubs, showers, lavatories, and clothes washers) for treatment and reuse.
- First-flush Diverter: An automatic device on a rainwater system that diverts the initial, dirtiest wash of rain runoff away from the storage tank.
- Debris Excluder: A device (like a screen or filter) connected to downspouts to keep large debris like leaves and sticks out of the rainwater storage tank.
- Ballast: Weight or anchors used to hold down an empty underground storage tank so groundwater doesn't float it out of the ground.
Exam Prep & Tips
- Memorize the 5-foot underground trenching separation rule and its specific exceptions (vertical separation of 12 inches, or sleeving the pipe 5 feet on both sides of a crossing).
- Know the exact wording for the required signage: "CAUTION: NONPOTABLE WATER - DO NOT DRINK."
- Pay close attention to what can and cannot go into an On-site Nonpotable Water Reuse System. Showers and clothes washers are OK; kitchen sinks and dishwashers are strictly forbidden.
- Remember the difference between graywater retention (max 24 hours untreated) and tank testing (must hold water for 24 hours).
Prohibited Practices
- Wastewater containing urine or fecal matter shall not be diverted to on-site nonpotable reuse systems.
- Reject water from reverse osmosis, water softeners, kitchen sinks, dishwashers, and wet-hood scrubbers shall not be collected for on-site reuse.
- Collected untreated graywater shall not be retained in collection reservoirs for more than 24 hours.
- Reservoir vents shall not be connected to sanitary drainage system vents.
- Overflow drains shall not be equipped with shutoff valves.
- Two separate shutoff valves shall not be used to serve as a bypass valve.
- Water drained from roof washers/debris excluders shall not drain to the sanitary sewer or onto roof surfaces.
- Tank outlets shall not skim water from the surface (must pull from at least 4 inches above the bottom).
Most Tested Numbers
- Disinfection Limits: Not more than 4 ppm (4 mg/L) of chloramines or free chlorine.
- Filtration: Must use a 100-micron (0.1 mm) or finer filter for water closet/urinal flushing.
- Signage Letters: Not less than 0.5 inch (12.7 mm) in height.
- Tank Manholes: Min 24 inches square or 24 inches inside diameter; must extend at least 4 inches above ground.
- Tank Service Ports: Min 8 inches in diameter; at least 4 inches above grade.
- Exception for small tanks: Treated-water below-grade tanks under 800 gallons don't need a full manhole, just an 8-inch service port.
- Tank Vent Outlets: Min 4 inches above grade.
- Tank Testing: Leave exposed and watertight for 24 hours, then add supplemental water for 15 minutes to test overflow.
- Trenching Separation: 5 feet horizontally.
- Trenching Vertical Exceptions: 12 inches above the highest point of the lower pipe.
- Trenching Crossing Sleeves: Sleeved for 5 feet horizontally on both sides of a crossing.
- Untreated Graywater Retention: Max 24 hours.
- Tank Outlets: Located at least 4 inches above the tank bottom.
- Max Pressure: 80 psi static (requires PRV if higher).
- Rainwater Gutter Slope: Min 1/8 inch per foot.
- Gutter Test: Pour not less than 1 gallon of water.
Section 1301 - General Nonpotable Requirements
1301.1 General This chapter covers how to build and install systems that collect, store, treat, and distribute nonpotable water. You can also use the CSA B805/ICC 805 standard as an alternative for rainwater systems. You must always follow local laws regarding how this water is used.
1301.2 Water Quality The water must meet the quality standards set by local laws for its specific use. If you mix water from different nonpotable sources, the entire system must meet the strictest code requirements that apply to any of those sources.
- 1301.2.1 Residual disinfectants: If using chlorine, the water can't have more than 4 ppm of chloramines or free chlorine. If using ozone, there shouldn't be gas bubbles of ozone at the fixture. (Reclaimed water is exempt from this).
- 1301.2.2 Filtration required: If using this water to flush toilets or urinals, it must be filtered to at least 100 microns (0.1 mm). (Reclaimed water is exempt).
1301.3 Signage required Every place the nonpotable water comes out (hose bibbs, faucets, etc.) must have a sign saying: "Nonpotable water is utilized for [application name]. CAUTION: NONPOTABLE WATER - DO NOT DRINK." It must be on a waterproof, corrosion-resistant tag or printed on the fixture. Letters must be at least 0.5 inches tall in a contrasting color. A standard "Do Not Drink" pictograph is also required.
1301.4 Permits You need permits and approved construction documents to build, alter, or repair nonpotable systems.
1301.5 Potable water connections If you hook up city drinking water (potable water) to the nonpotable system (like for a backup supply), you must protect the potable side with approved backflow prevention.
1301.6 Components and materials Use only manufacturer-approved piping and plumbing parts for these systems.
1301.7 Insect and vermin control Protect the system (especially tanks and pipes) from bugs and rodents using compatible screen materials that won't rust.
1301.8 Freeze protection If it gets freezing cold, you must protect the storage tanks and pipes from freezing.
1301.9 Nonpotable water storage tanks Tanks have a lot of specific rules:
- 1301.9.1 Location: Above-ground tanks must be protected from sunlight to stop algae. Use opaque materials, tinting, paint, sun barriers, or put them in a shed/garage.
- 1301.9.2 Materials: Must be durable, nonabsorbent, corrosion-resistant, and handle disinfection chemicals. Wooden tanks need a flexible liner unless they have a makeup water source.
- 1301.9.3 Foundation and supports: Tanks must be on a firm base that can handle the full weight.
- 1301.9.3.1 Ballast: Underground tanks in wet soil must be anchored down so they don't pop out of the ground like a bobber when empty.
- 1301.9.3.2 Structural support: Underground tanks must withstand earth loads without crushing.
- 1301.9.4 Makeup water: If the system needs continuous water, you must provide potable or reclaimed makeup water, protected by backflow. It needs a full-open valve, an automatic fill valve to prevent overflow, and the water level can't drop below the pump intake.
- 1301.9.5 Overflow: The tank needs an overflow pipe sized correctly. It must discharge safely away from the foundation, be bug-proofed, not freeze on walkways, and cannot have a shutoff valve. Needs a cleanout.
- 1301.9.6 Access: Tanks need an access opening to clean and inspect, and it must lock. Below-grade outdoor tanks need a 24-inch manhole extending 4 inches above ground, sloped to shed water. Manholes need an 8-inch service port. Exception: Below-grade treated tanks under 800 gallons just need the 8-inch service port, not a full manhole.
- 1301.9.7 Venting: Tanks must be vented. Do not tie this into the sanitary plumbing vent. Vent outlets must point downward (U-bend or cap), extend 4 inches above grade, and have bug screens.
- 1301.9.8 Draining of tanks: You must be able to drain the tank using a pump or a drain at the lowest point. Drain pipe needs a cleanout.
- 1301.9.9 Marking and signage: Label the tank's capacity and put the "CAUTION" wording on it. If a person can fit inside, label it "DANGER - CONFINED SPACE" with 0.5-inch letters.
- 1301.9.10 Storage tank tests: Fill the tank to the overflow and let it sit for 24 hours with exposed joints. No leaks allowed. Then run supplemental water for 15 minutes to check the overflow system. Check drains and auto-shutoff valves.
1301.10 System abandonment If an owner stops using a system: remove utility connections, replace distribution pipes with approved potable pipes (or hook fixtures back to the existing potable system), and secure the tank (lock it or fill it with sand).
1301.11 Trenching requirements Nonpotable/reclaimed pipes must be 5 feet away horizontally from sanitary sewers and potable water pipes. No running them in/over septic fields. Exceptions (when you don't need the 5ft):
- Nonpotable pipe is at least 12 inches above the sewer.
- Potable pipe is at least 12 inches above the nonpotable pipe.
- Nonpotable pipe is in the same trench as a sewer if the sewer is made of approved materials.
- Nonpotable crosses a sewer but is sleeved 5 feet horizontally on both sides of the crossing.
- Potable crosses nonpotable but is sleeved 5 feet horizontally on both sides of the crossing.
- Outdoor irrigation piping downstream of a backflow preventer.
1301.12 Outdoor outlet access Outdoor hose bibbs/hydrants supplied by nonpotable water must either be in a locked box or require a removable key to operate.
Section 1302 - On-Site Nonpotable Water Reuse Systems
(This section covers recycling your own building's wastewater.)
1302.1 General Governs on-site reuse systems per ASTM E2635.
1302.2 Sources You can only collect wastewater from: bathtubs, showers, lavatories (bathroom sinks), clothes washers, and laundry trays.
- 1302.2.1 Prohibited sources: You cannot use water containing urine or feces (blackwater). You also cannot use reject water from reverse osmosis or water softeners, kitchen sinks, dishwashers, or wet-hood scrubbers. These must go to the regular sanitary sewer.
1302.3 Traps Fixtures draining to the reuse system still need standard plumbing traps.
1302.4 Collection pipe Use standard approved drainage pipe and vent pipe. Install and size it like normal sanitary drainage. No extra special marking is required beyond normal sanitary pipe markings.
1302.5 Filtration Water must be filtered. Filters must be accessible, have a pressure gauge (or indicator) so you know when they are clogged, and have shutoff valves right before and after them so you can change the filter without draining the system.
1302.6 Disinfection and treatment Treat the water as needed for its end use. Crucial Rule: Untreated graywater can only sit in a collection tank for a maximum of 24 hours.
- 1302.6.1 Graywater used for fixture flushing: Must be treated by an NSF 350 system.
1302.7 Storage tanks Follow general tank rules (1301.9), plus:
- 1302.7.1 Location: Must follow clearance distances (e.g., 5 ft from property lines/septic/water service, 10 ft from public water mains, 50 ft from streams/wells).
- 1302.7.2 Outlets: Water coming out of the tank must be drawn from at least 4 inches above the bottom, and cannot skim off the very top surface.
1302.8 Valves
- 1302.8.1 Bypass valve: You need a 3-way diverter valve upstream of the tank to send the graywater directly to the sanitary sewer for maintenance. It must be clearly marked. You cannot just use two separate shutoff valves for this.
- 1302.8.2 Backwater valve: Install backwater valves on overflow and tank drain pipes.
1302.9 Pumping and control system Pumps and controls must be accessible for maintenance and deliver the right flow/pressure.
1302.10 Water pressure-reducing valve or regulator If the pump pushes more than 80 psi static pressure, you must install a PRV to drop it to 80 psi or less.
1302.11 Distribution piping Follow standard nonpotable pipe material, sizing, and labeling rules (except for outdoor irrigation downstream of backflow).
1302.12 Tests and inspections
- Collection/Vent: Standard DWV tests.
- Tanks: 24-hour water test.
- Supply/Distribution: Standard water pipe tests.
- Backflow/Backwater: Standard assembly testing.
- Vermin protection: Visual inspection of bug screens.
- Water quality: Tested at the point of use to verify it meets local requirements.
1302.13 Operation and maintenance manuals A hardcopy manual must be provided. It must include schematics, parts lists, maintenance schedules (noting filter part numbers), and startup/shutdown/operating procedures.
Section 1303 - Nonpotable Rainwater Collection and Distribution Systems
1303.1 General Rules for collecting and using rainwater for nonpotable applications. (Fire protection rainwater systems fall under the Fire Code).
1303.2 Collection surface You can only collect rainwater from above-ground impervious roofs, or approved parking/walking surfaces.
1303.3 Debris excluders Downspouts must have a device (like a leaf screen) to keep leaves, pine needles, and sticks out of the tank.
1303.4 First-flush diverter You must install an automatic diverter to throw away the first (dirtiest) wash of rain. It can't drain back onto the roof and must go to a safe runoff location.
1303.5 Roof gutters and downspouts Materials must be compatible and watertight.
- 1303.5.1 Slope: Gutters and downspouts must slope at least 1/8 inch per foot so water doesn't pool. (Siphonic roof drains are the exception).
- 1303.5.2 Size: Size them based on local rainfall rates.
- 1303.5.3 Cleanouts: Put cleanouts in the system so you can reach and clean all filters and downspouts.
1303.6 Drainage Water flushed away by the debris excluder or roof washer cannot go into the sanitary sewer. It must drain to property runoff without causing erosion. It must auto-drain between storms.
1303.7 Collection pipe Use approved DWV pipes and vents. Install and size them normally. No special extra markings needed.
1303.8 Filtration Same as graywater: filters need access, a gauge to show clogging, and isolation valves.
1303.9 Disinfection If chlorinated, max residual chlorine must comply with local limits (test via ASTM D1253).
1303.10 Storage tanks Follow general tank rules, plus:
- 1303.10.1 Location: Must be at least 5 feet from lot lines, seepage pits, and septic tanks.
- 1303.10.2 Inlets: Water must enter the tank calmly without stirring up the muck at the bottom.
- 1303.10.3 Outlets: Must pull water from at least 4 inches above the bottom, and not skim the top.
1303.11 Valves Must have backwater valves on overflow and drain pipes.
1303.12 Pumping and control system Mechanicals must be accessible and provide proper flow.
1303.13 Water pressure-reducing valve or regulator If pressure is over 80 psi static, install a PRV.
1303.14 Distribution piping Follow standard nonpotable pipe rules, design, and labeling (purple pipes/marking).
1303.15 Tests and inspections
- 1303.15.1 Roof gutter test: Inspect slope, then pour at least 1 gallon of water at the far end. It must not leak or leave standing water.
- 1303.15.2 First-flush test: Run water to prove the automatic diverter works.
- 1303.15.3 to .8: Standard tests for pipes, tanks, backflow, vermin screens, and water quality.
- 1303.15.9 Collected raw rainwater quality: Use ASTM E2727 to see if site conditions require extra treatment.
1303.16 Operation and maintenance manuals Provide a hardcopy manual with schematics, parts, maintenance schedules, and operating procedures.
Section 1304 - Reclaimed Water Systems
(This section covers treated wastewater sent back to buildings by city utility plants, usually in "purple pipes".)
1304.1 General Governs the use of nonpotable reclaimed water systems.
1304.2 Water pressure-reducing valve or regulator Just like the other systems, if the reclaimed water enters the building at more than 80 psi static, you must install a PRV.
1304.3 Reclaimed water systems Must be designed using accepted engineering practices.
- 1304.3.1 Distribution piping: Must use nonpotable approved materials, be sized correctly, and be labeled/marked correctly (except for outdoor irrigation downstream of backflow).
1304.4 Tests and inspections
- 1304.4.1 Water supply test: Test the reclaimed distribution pipe like regular water pipe.
- 1304.4.2 Backflow assemblies: Test backflow preventers according to standard rules.
TABLE 1302.7.1 - LOCATION OF NONPOTABLE WATER REUSE STORAGE TANKS
| ELEMENT | MINIMUM HORIZONTAL DISTANCE FROM STORAGE TANK (feet) |
|---|---|
| Critical root zone (CRZ) of protected trees | 2 |
| Lot line adjoining private lots | 5 |
| Public water main | 10 |
| Seepage pits | 5 |
| Septic tanks | 5 |
| Streams and lakes | 50 |
| Water service | 5 |
| Water wells | 50 |
For SI: 1 foot = 304.8 mm.
TABLE 1303.10.1 - LOCATION OF RAINWATER STORAGE TANKS
| ELEMENT | MINIMUM HORIZONTAL DISTANCE FROM STORAGE TANK (feet) |
|---|---|
| Critical root zone (CRZ) of protected trees | 2 |
| Lot line adjoining private lots | 5 |
| Seepage pits | 5 |
| Septic tanks | 5 |
For SI: 1 foot = 304.8 mm.