Topic 13 · Subsurface Irrigation
Subsurface Irrigation
Chapter 14 governs the materials, design, and installation of subsurface graywater soil absorption systems. It focuses on safely reusing nonpotable graywater for underground landscape irrigation, providing specific rules for soil percolation testing, system sizing, trench/bed excavation, and critical safety clearances to prevent the contamination of potable water sources.
- No Dye or Disinfection Needed: Unlike some other nonpotable water systems, subsurface graywater absorption systems do not require the water to be dyed or disinfected.
- Sizing is Occupant-Based: Residential graywater output is calculated strictly by the number of bedrooms (min. 2 for the first bedroom, 1 for each additional) and specific fixture discharge rates (gallons per day).
- Percolation Testing is Mandatory: You must perform precise timing tests on dug holes to determine how fast the soil absorbs water before designing the system.
- Strict Clearances: Maintaining exact distances from wells, streams, water mains, and buildings is vital to protect the environment and potable water supplies.
- Installation Layers: There are specific depth requirements for gravel (below and above the pipe), barrier materials (hay, straw, or synthetic - never building paper), and topsoil backfill.
- Subsurface Graywater Soil Absorption System: An underground network of trenches or beds that distributes nonpotable graywater into the soil for landscape irrigation.
- Percolation Test: A standardized procedure of digging a hole, filling it with water, and timing the drainage rate to determine how well the soil absorbs liquid.
- Seepage Trench: A narrow absorption excavation (1 to 5 feet wide) containing a single distribution pipe.
- Seepage Bed: A wider absorption excavation (5 feet or wider) that contains multiple distribution pipes.
- Soil Wire: A field test condition where wet soil rolled between the hands forms a string or wire shape, indicating the soil is too wet to safely excavate without smearing.
Exam Prep & Tips
- Sizing Calculations: Be ready to calculate graywater output (). Remember that a 3-bedroom house has 4 occupants (2 for the 1st BR, plus 1 for each of the other two).
- Sandy vs. Other Soils: Understand the difference in percolation testing. Sandy soil tests run for 1 hour, while "other soils" require a 4-hour soak and a 16-30 hour swelling period.
- Trench vs. Bed: Know the difference by width and pipe count. A trench is max 5 feet wide (one pipe). A bed is 5+ feet wide (multiple pipes).
- Material Traps: Exam questions love testing prohibited materials. Remember that building paper is strictly forbidden as an aggregate cover!
Prohibited Practices
- Private sewage disposal systems are strictly PROHIBITED in compacted areas like parking lots and driveways.
- Building paper SHALL NOT be used to cover the aggregate in a trench or bed.
- You SHALL NOT excavate seepage trenches or beds if the soil is so wet it forms a "soil wire" when rolled between your hands.
- During "other soils" percolation tests, you SHALL NOT remove water remaining in the hole after the initial 4-hour period.
- Disinfection and coloring (dye) are NOT REQUIRED for subsurface graywater systems.
Most Tested Numbers
Clearances & Distances (Table 1402.3)
- Water Wells: 100 feet from absorption field / 50 feet from storage tank
- Streams and Lakes: 50 feet from field / 50 feet from tank
- Public Water Main: 10 feet from field / 10 feet from tank
- Water Service: 5 feet from field / 5 feet from tank
- Buildings: 2 feet from field / 5 feet from tank
- Property Lines: 5 feet from field / 5 feet from tank
Sizing Variables
- Residential Occupants: Minimum 2 for the first bedroom; 1 for each additional bedroom.
- Showers/Tubs/Lavatories: 25 gallons per day (gpd) per occupant.
- Clothes Washers/Laundry: 15 gpd per occupant.
Percolation Test Hole Specs
- Hole Diameter: 4 to 8 inches.
- Gravel/Sand in bottom: 2 inches.
Trenches & Beds
- Seepage Trench Width: 1 foot to 5 feet.
- Seepage Trench Max Length: 100 feet.
- Trench Spacing: Minimum 2 feet apart.
- Seepage Bed Width: Minimum 5 feet.
- Bed Pipe Spacing: 3 to 5 feet apart; 1 to 3 feet from the sidewall/headwall.
Aggregate & Backfill
- Aggregate Size: 1/2 inch to 2-1/2 inches.
- Aggregate Below Pipe: Minimum 6 inches.
- Aggregate Above Pipe: Minimum 2 inches.
- Hay/Straw Cover Depth: 9 inches (uncompacted).
- Soil Backfill Depth: Minimum 9 inches above the cover.
Distribution Piping
- Minimum Pipe Diameter: 3 inches.
- Depth to Top of Pipe: Minimum 8 inches below the original surface.
- Pipe Slope: 2 to 4 inches per 100 feet.
Section 1401 General Requirements
1401.1 Scope This chapter covers the materials, design, and installation of subsurface graywater soil absorption systems that use nonpotable water from on-site reuse systems.
1401.2 Materials Above-ground piping must meet standard drain, waste, and vent (DWV) material codes (Table 702.1). Underground piping for the absorption system must meet underground building drainage standards (Table 702.2).
1401.3 & 1401.4 Tests and Inspections Piping must be tested just like standard DWV systems (Section 312), and the whole system must be inspected per general code requirements (Section 111).
1401.5 & 1401.6 Disinfection and Coloring Good news for system designers: graywater used for these subsurface systems does NOT need to be disinfected, nor does it need to be dyed a specific color (unlike some other reclaimed water systems).
Section 1402 System Design and Sizing
1402.1 Sizing The system must be sized based on the total output of all connected fixtures. The formula is simple: C = A x B
- A = Number of Occupants:
- Residential: Actual number, or a minimum of 2 people for a 1-bedroom home, plus 1 extra person for each additional bedroom.
- Commercial: Determined by the International Building Code (IBC).
- B = Estimated Flow Demand per Occupant:
- Residential: 25 gallons per day (gpd) for showers/tubs/lavatories, and 15 gpd for washing machines/laundry trays.
- Commercial: Based on fixture types or water usage records.
- C = Total estimated graywater discharge (in gallons per day).
1402.2 Percolation Tests You must test how fast the soil absorbs water (permeability) using percolation ("perc") tests or professional soil evaluations.
1402.2.1 Perc Tests & Procedures You must perform at least three perc tests in each planned system area, spaced evenly.
1402.2.1.1 The Test Hole Dig or bore a hole with straight vertical sides, measuring 4 to 8 inches across. Scratch the sides and bottom to expose natural, uncompacted soil. Clean out loose dirt and put 2 inches of gravel or coarse sand at the bottom.
1402.2.1.2 Test Procedure for Sandy Soils Fill the hole with at least 12 inches of clear water. See how fast it drains. If a second fill drains in 10 minutes or less, it's a "sandy soil" test.
- Procedure: Add water up to 6 inches above the gravel. Measure the water level drop every 10 minutes for 1 hour.
- If 6 inches drains in under 10 minutes, measure more frequently, but never fill it higher than 6 inches.
- If 6 inches drains in under 2 minutes, stop the test and record the rate as "less than 3 minutes per inch."
- Use the very last drop measurement to calculate the final perc rate. (If the soil fails this, use the "Other Soils" procedure).
1402.2.1.3 Test Procedure for Other Soils For slower soils, fill the hole with 12 inches of water and keep it filled for 4 hours (to pre-soak).
- After 4 hours, do NOT remove the remaining water. Let the soil swell for 16 to 30 hours.
- After swelling, clean out any caved-in dirt. Fill water to 6 inches above the gravel.
- Measure the drop every 30 minutes for 4 hours (unless two consecutive drops vary by no more than 1/16 inch). Record at least three drops. Refill to 6 inches when it gets low.
- Fast draining exception: If the first 6 inches drops in under 30 minutes, switch to 10-minute intervals and run the test for just 1 hour (max water depth 5 inches).
- Use the drop from the final measurement period for the official rate.
1402.2.2 Permeability Evaluation Alternatively, soil can be evaluated by a professional based on texture and structure, using the same boring holes mentioned above.
1402.3 Site Location & Clearances The absorption system must be physically lower than any water well or reservoir. If that's impossible, surface water must drain away from the well. Surface water from neighboring lots must also be diverted away from the system.
- Crucial Rule: Never install these systems under compacted areas like driveways or parking lots!
- Table 1402.3 Clearances: Know your distances. For example, an absorption field must be 100 feet from a water well, 50 feet from a stream, 10 feet from a public water main, and 5 feet from property lines.
Section 1403 Installation
1403.1.1 Absorption Area Calculation Divide your total graywater discharge (C) by the Design Loading Rate (found in Table 1403.1.1, based on your perc test).
- Table Example: If soil takes 10 to 30 minutes to absorb an inch of water, the loading rate is 0.8 gallons per square foot per day.
1403.1.2 Seepage Trench Excavations A trench is narrow: 1 foot to 5 feet wide. Trenches must be spaced at least 2 feet apart. The absorption area is simply the trench bottom width multiplied by the pipe length. A single trench cannot exceed 100 feet in length.
1403.1.3 Seepage Bed Excavations A bed is wide: 5 feet or wider and contains multiple distribution pipes. Calculate area using the bottom of the bed.
- Pipes in a bed must be spaced 3 to 5 feet apart from each other, and 1 to 3 feet away from the bed's walls.
1403.1.4 Excavation and Construction Rules The bottom of the trench or bed must be perfectly level.
- The "Soil Wire" Test: If the soil is wet enough that you can roll it between your hands into a wire shape, it's too wet to dig! Stop digging until it dries, otherwise you'll smear and seal the soil, ruining absorption. If smearing happens, you must scratch (scarify) the walls/bottom to open the pores back up.
1403.1.5 Aggregate and Backfill Layers This is exactly how you must build the trench/bed from bottom to top:
- Bottom Aggregate: At least 6 inches of gravel (size 1/2" to 2-1/2") below the pipe.
- The Pipe: Lay the distribution pipe.
- Top Aggregate: At least 2 inches of gravel over the pipe.
- The Cover: Cover the gravel with an approved synthetic material or 9 inches of uncompacted marsh hay or straw. Never use building paper!
- Backfill: At least 9 inches of soil backfill goes on top.
1403.2 Distribution Piping Requirements
- Size: Pipes must be at least 3 inches in diameter.
- Materials: Must be PE (ASTM F405), PVC (ASTM D2729), or solid core PVC (ASTM F1488).
- Depth: The very top of the pipe must sit at least 8 inches below the surface grade.
- Slope: The pipe must slope gently between 2 inches and 4 inches for every 100 feet of run.
1403.2.1 Joints All joints in the distribution pipe must be made according to standard sanitary drainage joint rules (Section 705).
TABLE 1402.3 - LOCATION OF SUBSURFACE GRAYWATER SOIL ABSORPTION SYSTEM
MINIMUM HORIZONTAL DISTANCE
| ELEMENT | Storage tank (feet) | Absorption field (feet) |
|---|---|---|
| Buildings | 5 | 2 |
| Lot line adjoining private property | 5 | 5 |
| Public water main | 10 | 10 |
| Seepage pits | 5 | 5 |
| Septic tanks | 0 | 5 |
| Streams and lakes | 50 | 50 |
| Water service | 5 | 5 |
| Water wells | 50 | 100 |
For SI: 1 foot = 304.8 mm.
TABLE 1403.1.1 - DESIGN LOADING RATE
| PERCOLATION RATE (minutes per inch) | DESIGN LOADING FACTOR (gallons per square foot per day) |
|---|---|
| 0 to less than 10 | 1.2 |
| 10 to less than 30 | 0.8 |
| 30 to less than 45 | 0.72 |
| 45 to 60 | 0.4 |
For SI: 1 minute per inch = min/25.4 mm, 1 gallon per square foot = 40.7 L/m2.
TABLE 1403.2 - DISTRIBUTION PIPE
| MATERIAL | STANDARD |
|---|---|
| Polyethylene (PE) plastic pipe | ASTM F405 |
| Polyvinyl chloride (PVC) plastic pipe | ASTM D2729 |
| Polyvinyl chloride (PVC) plastic pipe with a 3.5-inch O.D. and solid cellular core or composite wall | ASTM F1488 |
For SI: 1 inch = 25.4 mm.