PVB & SVB Field Test

The PVB and SVB field tests, and the one difference between them that examiners like to ask about.

The canopy comes off first on both, because watching the poppet move is half the test.

On a PVB the air inlet is tested first, from test cock two, with the kit held level with the air inlet. On an SVB the check valve is tested first, using the vent valve to bring the body to atmosphere without spilling.

On both, the pressure is dropped slowly, no more than a quarter turn of the high bleed. Dropping it fast reads low, exactly as it does on an RP relief valve.

Bleed-off valve assembly: an accessory used to trim the flow when a number one shut-off is passing water.

Vent valve: the SVB feature that makes it spill resistant.

Full travel: the air inlet opening completely once the body drains, which is an observation rather than a reading.

If the air inlet never opens, suspect the number one shut-off before the air inlet. A leaking shut-off keeps feeding the body so the pressure never falls far enough, and calling that an air inlet fault means replacing the wrong part.

Count the test cocks to identify the assembly. Four means an RP or a double check, two means a PVB, one plus a vent valve means an SVB.