A2L Refrigerants & the 2025 Transition

A2L refrigerants are the biggest change to this trade in thirty years and the reason a 2019 study guide is now misleading. The thermodynamics are unchanged: superheat, subcooling, evacuation and recovery all work exactly as before. What is new is that the refrigerant is a fuel, so ignition sources, equipment ratings and charge limits all matter.

Where it lives. The AIM Act of 2020 and its Technology Transitions Rule, with equipment requirements in UL and IEC 60335-2-40 and classification in ASHRAE Standard 34.

What it covers. The A2L classification, the 2025 transition, R-454B, R-32 and R-452B, cylinder markings and left-hand threads, rated recovery equipment, leak sensors and mitigation, charge limits, and blend glide.

On the exam. Section 608 itself has not changed for A2L, and questions often test exactly that: existing certification stays valid. Employer and manufacturer training is a separate requirement.

A2L means lower toxicity and mildly flammable, with a burning velocity of 10 cm/s or less. R-454B is roughly 68.9 percent R-32 and 31.1 percent R-1234yf by mass.

  • The restriction is on new equipment. Servicing existing R-410A systems is entirely legal and will be for years.
  • Dew for superheat, bubble for subcooling. Swapping them is the most common blend mistake, and the error equals the whole glide.
  • A1 equipment is not acceptable. Recovery machines, vacuum pumps, hoses and cylinders all need an A2L rating.