Topic 07 · Type II: High Pressure Appliances
Type II: High Pressure Appliances
Type II is the largest section and covers the equipment most technicians actually work on. The evacuation table is the part people try to memorise cell by cell and should instead learn as a pattern: deeper recovery for larger charges, newer equipment and lower pressure refrigerants.
Where it lives. 40 CFR 82.156 Table 1 for evacuation levels and 82.152 for the pressure class definitions.
What it covers. The pressure classes, required evacuation levels, liquid and push-pull recovery, non-condensables, TXV and fixed orifice charging, superheat and subcooling, compression ratio, and system components.
On the exam. Diagnosis questions give superheat and subcooling together and ask what is wrong. Learn the four combinations as a grid rather than as four separate facts.
The pressure classes are defined by liquid saturation pressure at 104 degrees F: above 355 psia is very high, 170 to 355 is high, 45 to 170 is medium, and below 45 is low.
- The four-box diagnosis grid. High superheat with low subcooling is undercharge; with high subcooling it is a restriction. Low superheat with high subcooling is overcharge; both low means the compressor is not pumping.
- TXV by subcooling, piston by superheat. The valve holds its own superheat, so superheat cannot measure the charge.
- Absolute pressures for compression ratio. Add 14.7 to both readings first.