RP Field Test

The full reduced pressure principle field test, phase by phase. This is the procedure candidates fail on.

Five phases. Prepare, observe check one, record the relief valve, observe check two under backpressure, then record the numbers and return to service.

Nobody forgets that a relief valve opens at 2.0 psid. What people forget is which bleed closes first: the high bleed, every time, and the low bleed last.

Two things separate a good tester from a fast one. Opening the low control no more than a quarter turn, so the relief valve reading is honest. And resetting the gauge before the check valve one reading, so disc compression does not inflate it.

Buffer: check valve one minus the relief valve opening point, which must be 3.0 psid or more.

Disc compression: a check held hard against its seat reading higher than it will hold in service.

Vent hose: the third hose, used to apply backpressure from test cock four.

Learn the sequence as five phases rather than thirty steps. Each phase leaves the assembly in the state the next one needs, and once that clicks the order stops being arbitrary.

One drip from the relief vent may be residual water. Two drips after a proper gauge reset is check valve two failing. That distinction is worth a mark on almost every exam.