The service topic is where the calculators in this app earn their place. Almost every question here maps onto a tool: static pressure, airflow, delta-T, target superheat, capacitance, voltage imbalance, circuit ampacity and the fan laws.
Where it lives. Manufacturer service literature and standard engineering practice, with the electrical method following NEC 440.
What it covers. Total external static pressure, airflow per ton, the target delta-T, wet bulb measurement, target superheat, capacitor testing, voltage imbalance, MCA and MOCP, gas furnace input and temperature rise, the fan laws and duct sizing.
On the exam. Airflow is the answer far more often than charge. A wide temperature split, a high temperature rise and a high static pressure are all the same fault seen from three directions.
Total external static pressure is the sum of the magnitudes of the supply and return readings. Friction rate is the available static multiplied by 100 and divided by the total effective length.
- Check airflow before charge. Airflow problems mimic charge problems, and adding refrigerant to a system with a blocked filter makes it worse.
- A wide split is a symptom. It means too little air, not good cooling.
- Power follows the cube of speed. Twenty percent more airflow is seventy-three percent more motor load.