This chapter establishes the rules for keeping dangerous or foul-smelling sewer gases out of buildings using traps, and for keeping harmful substances (like grease, oil, and sand) out of the municipal sewer system using interceptors and separators. By ensuring proper trap seals and adequate filtration of waste, these systems protect both public health and the structural integrity of the drainage network.

  • Every plumbing fixture must have its own separate liquid-seal trap (with a few specific exceptions for combination sinks and interceptors).
  • Trap seals must be maintained between 2 inches and 4 inches deep to prevent sewer gas from entering the building.
  • Trap seal primers or barrier devices are required where trap seals (like emergency floor drains) are subject to evaporation.
  • Grease interceptors are mandatory in commercial kitchens and food prep areas, but are explicitly NOT required in private dwellings.
  • Certain trap designs are strictly forbidden, including "S" traps, bell traps, and traps with moving parts, because they are highly prone to losing their water seal or failing.
  • Trap Seal: The vertical depth of liquid in a trap (between the crown weir and the top of the dip) that acts as a barrier to sewer gases.
  • Interceptor / Separator: A device designed to intercept and separate harmful or undesirable matter (grease, oil, sand, glass) from wastewater before it enters the public sewer.
  • Hydromechanical Grease Interceptor: A type of grease interceptor that relies on flow control, baffles, and air entrainment to separate fats, oils, and greases.
  • Gravity Grease Interceptor: A large tank-style interceptor that relies on volume and long retention times (usually 30+ minutes) to allow grease to float to the top.
  • Trap Seal Primer: A device or system that introduces a small amount of water into a trap to prevent the water seal from evaporating.

Exam Prep & Tips

  • Distance Rules: You will absolutely see questions about the maximum distances between the fixture outlet and the trap. Memorize 24 inches vertical and 30 inches horizontal.
  • Trap Seals: The minimum and maximum trap seal depths (2 inches to 4 inches) are highly tested standard IPC numbers.
  • Interceptor Math: If asked about Gravity Grease Interceptor sizing, remember the formula: Peak flow (gpm) x 30 minutes. For Hydromechanical Interceptors over 100 gpm, you simply double the gpm to get the required grease retention in pounds.
  • Oil Separator Math: For garages, the baseline is 6 cubic feet for the first 100 sq ft of drained area, plus 1 cubic foot for each additional 100 sq ft.

Prohibited Practices

  • NO Double trapping a fixture.
  • NO Traps that depend on moving parts to maintain the seal.
  • NO Bell traps, Crown-vented traps, "S" traps, or Building (house) traps.
  • NO Drum traps (except when used as solids interceptors or for chemical waste).
  • NO Food waste disposers discharging into a grease interceptor.
  • NO Emulsifiers, chemicals, or enzymes discharged into grease interceptors (only approved microbes for bioremediation are allowed).
  • NO Exposed plumbing pipes or traps in mental health centers.
  • NO Ledges, shoulders, or reductions in fittings that could obstruct flow.

Most Tested Numbers

  • 24 inches: Maximum vertical distance from fixture outlet to trap weir.
  • 30 inches: Maximum horizontal distance from fixture outlet centerline to trap inlet centerline.
  • 6 inches: Maximum depth difference between compartments on a combination plumbing fixture sharing one trap.
  • 30 inches: Maximum distance between waste outlets on a combination fixture sharing one trap.
  • 2 inches: Minimum depth of a trap liquid seal.
  • 4 inches: Maximum depth of a standard trap liquid seal.
  • 6 inches: Depth of concrete embedment required around underground acid-resisting (brittleware) traps.
  • 30 minutes: Retention time used to calculate gravity grease interceptor capacity.
  • 2 feet (24 inches): Minimum depth below the invert of the discharge drain for oil separators.
  • 18 inches: Minimum water seal depth for the outlet opening of an oil separator.
  • 6 cubic feet: Base capacity of an oil separator for the first 100 sq. ft. of drainage area in a garage.
  • 1 cubic foot: Additional capacity required for every extra 100 sq. ft. of garage drainage area.
  • 6 inches: Minimum water seal for commercial sand interceptors.
  • 1/2 inch: Minimum size of solids that a clothes washer interceptor basket must prevent from passing.

Section 1001: General

1001.1 Scope: This chapter covers what materials to use and how to install traps, interceptors, and separators.

Section 1002: Trap Requirements

1002.1 Fixture traps: Every individual plumbing fixture must have its own liquid-seal trap.

  • Distances: The vertical distance from the fixture outlet down to the trap weir cannot exceed 24 inches. The horizontal distance from the center of the outlet to the center of the trap inlet cannot exceed 30 inches.
  • Double Trapping: You can never double-trap a fixture (putting one trap right after another).
  • Exceptions (When you can bend the rules):
    1. Fixtures with built-in (integral) traps (like toilets) don't need a separate one.
    2. A combo sink can share one trap if the compartments aren't deeper than 6 inches from each other, and the drain outlets are no more than 30 inches apart.
    3. Floor drains in parking garages discharging to storm sewers don't need individual traps. If they go to a combined sewer, they can share a main building trap instead.
    4. A food utensil/pot sink connected to a hydromechanical grease interceptor can use the interceptor as its trap, provided the vertical drop is under 30 inches, the total pipe length is under 60 inches (5 feet), and an emergency floor drain is provided on the branch.

1002.2 Design of traps: Traps must be "self-scouring" (they clean themselves every time water flows). They cannot have interior partitions unless the trap is integral to the fixture or made of corrosion-resistant material. Slip joints are strictly limited: you can only use them on the trap inlet, trap outlet, or right within the trap seal.

1002.3 Prohibited traps: You can NEVER use:

  1. Traps with moving parts.
  2. Bell traps.
  3. Crown-vented traps.
  4. Traps with interior partitions (unless approved/integral).
  5. "S" traps.
  6. Drum traps (Exception: Drum traps are allowed if used as a solids interceptor or for chemical waste).

1002.4 Trap seals: A standard fixture trap must have a liquid water seal between 2 inches and 4 inches deep. (Deeper seals are allowed for special ADA/accessible fixture designs).

1002.4.1 Trap seal protection: Traps that dry out easily (like emergency floor drains) must be protected from evaporation using one of these approved methods:

  • 1002.4.1.1 Potable water primer: A valve that drips drinking water into the trap.
  • 1002.4.1.2 Reclaimed/graywater primer: A valve that drips safe reclaimed water into the trap.
  • 1002.4.1.3 Wastewater primer: A device using wastewater from another fixture.
  • 1002.4.1.4 Barrier-type device: A physical barrier (like a rubber flapper) installed in the drain that lets water down but stops evaporation from coming up.
  • 1002.4.1.5 Fixture drain connection: Using the tailpiece waste of a nearby sink or drinking fountain to prime the floor drain. The connection must happen below the flood rim but above the floor drain's trap inlet.

1002.5 Size of fixture traps: The trap must be big enough to drain the fixture quickly (matching Table 709.1) but it can NEVER be larger than the drainage pipe it connects to.

1002.6 Building traps: Whole-building traps (house traps) are strictly prohibited (except for the parking garage exception in 1002.1).

1002.7 & 1002.8 Setting, Protection & Recesses: Traps must be installed perfectly level so the water seal works correctly. If there is a risk of freezing, they must be protected. If a trap is installed underground in a recess (like under a slab bathtub), the box must be corrosion-resistant and bug/mouse-proof.

1002.9 Acid-resisting traps: If you install an underground trap made of vitrified clay or brittleware (for acid waste), it must be encased in a minimum of 6 inches of concrete on the bottom and sides to prevent it from cracking.

1002.10 Mental health centers: For safety reasons, no pipes or traps can be exposed in a mental health center.

Section 1003: Interceptors and Separators

1003.1 & 1003.2 Where required & Approval: You must use interceptors or separators whenever wastewater contains grease, oil, sand, or anything hazardous to the sewer. Only waste that actually needs treatment should go through these devices.

1003.3 Grease interceptors:

  • 1003.3.1 Where required: Mandatory in commercial food prep (restaurants, hotels, schools, wok stations, auto-hood washers).
  • 1003.3.2 Food waste disposers: Garbage disposals are NEVER allowed to discharge into a grease interceptor.
  • 1003.3.3 Additives: You cannot use emulsifiers, chemicals, or enzymes to break down grease (it just pushes the grease further down the sewer line). You can use approved microbes that physically eat the grease (bioremediation).
  • 1003.3.4 Not required: You do not need a grease interceptor for private homes or apartment dwelling units.
  • 1003.3.5 Hydromechanical Sizing: Must follow ASME/CSA standards. Table 1003.3.5.1 dictates capacity based on flow rate (gpm). As a general rule for flows up to 100 gpm, the required grease retention in pounds is roughly double the flow in gpm (e.g., 50 gpm flow = 100 lbs capacity). For flows over 100 gpm, the code explicitly says to double the flow rating to get the pound capacity.
  • 1003.3.5.2 Flow controls: Grease interceptors must have vented flow controls to ensure water doesn't rush through too fast, preventing the grease from separating.
  • 1003.3.6 Automatic devices: Must be sized correctly to handle peak flow and installed with ready access for maintenance.
  • 1003.3.7 Gravity Grease Interceptors: These are the large, underground tanks. Capacity is sized by taking the peak drain flow (gpm) x 30 minutes.
  • 1003.3.8 Direct connection: Discharge pipes must connect directly to the sanitary drainage system.

1003.4 Oil separators:

  • Where Required: Garages with floor drains, car washes, factories with flammable wastes, and hydraulic elevator pits. (Exception: Elevator pits don't need one if they have an approved alarm system that won't shut off emergency firefighter pumps).
  • 1003.4.2 Design: Separators must be at least 2 feet deep below the discharge pipe invert. The outlet must have at least an 18-inch water seal.
  • 1003.4.2.2 Garage Sizing: For service/repair garages, the separator must hold 6 cubic feet for the first 100 square feet of drained floor area. Add 1 cubic foot for every additional 100 square feet. (Note: Simple parking/storage garages without wash/repair stations do not need oil separators).

1003.5 Sand interceptors: Used in commercial setups. Must have easy access for cleaning and a minimum water seal of 6 inches.

1003.6 Clothes washer interceptors: Commercial clothes washers must discharge through a wire basket interceptor that catches solids, string, and buttons 1/2 inch or larger. (This is NOT required for residential washing machines).

1003.7 & 1003.8 Bottling plants & Slaughterhouses: Bottling plants need an interceptor to catch broken glass. Slaughterhouses need separators to catch feathers, entrails, and animal byproducts before they clog the public sewer.

1003.9 Venting: Interceptors and separators must be properly vented so they do not become "air bound" (which would stop the flow of drainage).

1003.10 Access and maintenance: All interceptors and separators must be readily accessible for service. They must be periodically pumped/cleaned out by removing accumulated grease, oil, and solids.

Section 1004: Materials, Joints, and Connections

1004.1 General: The materials used for traps and separators must meet the standard IPC material codes. Crucially, fittings inside these systems cannot have ledges, shoulders, or reductions that could snag debris and cause clogs.

TABLE 1003.3.5.1 - CAPACITY OF GREASE INTERCEPTORS(a) (a)

TOTAL FLOW-THROUGH RATING (gpm)GREASE RETENTION CAPACITY (pounds)
48
612
714
918
1020
1224
1428
1530
1836
2040
2550
3570
50100
75150
100200

For SI: 1 gallon per minute = 3.785 L/m, 1 pound = 0.454 kg.

a. For total flow-through ratings greater than 100 (gpm), double the flow-through rating to determine the grease retention capacity (pounds).