Topic 05 · Water Supply & Distribution
Water Supply & Distribution
Chapter 6 covers the critical requirements for the design, installation, and maintenance of potable water supply and distribution systems within buildings. Its primary focus is ensuring that the drinking water supply provides adequate pressure and flow while remaining strictly protected against contamination through proper material selection, approved joint connections, and stringent backflow prevention measures.
- Potable Water is Mandatory: Drinking, bathing, culinary, and medical fixtures must be supplied exclusively with potable (safe to drink) water.
- Separation from Contamination: Water service lines must maintain strict distance from sewer lines, septic tanks, and contaminated soil.
- Pressure Regulation: If incoming static water pressure exceeds 80 psi, a pressure-reducing valve (PRV) must be installed.
- Thermal Expansion: A thermal expansion tank is required if the system has a check valve, backflow preventer, or PRV on the cold water supply to a water heater.
- Cross-Connection Control: The potable water system must be protected from backflow using approved devices (e.g., air gaps, RPZs, vacuum breakers) matched to the hazard level.
- Material & Joint Restrictions: Only approved materials may be used. Prohibited practices include solvent-cementing different types of plastic, using saddle fittings, or using cement/concrete joints.
- Nonpotable System Identification: Systems carrying reclaimed, rain, or graywater must be clearly marked with purple colors, continuous labels, and warning signs.
- Potable Water: Water that is safe for drinking, bathing, cooking, and processing food or medical products.
- Air Gap: The unobstructed vertical distance between the lowest opening of a water supply pipe and the flood level rim of the fixture it dumps into (the ultimate backflow prevention).
- Backflow: The dangerous reversal of normal water flow, which can suck or push contaminated water into the potable drinking supply.
- Cross-Connection: Any physical link where nonpotable (unsafe) water or chemicals could potentially enter the potable water system.
- Water Hammer Arrestor: A device designed to absorb the destructive hydraulic shock created when a quick-closing valve shuts off water flow instantly.
- Tempered Water: Water mixed to a safe, controlled temperature limit (usually max 110ºF) to prevent scalding during bathing or washing.
- Barometric Loop: A vertical loop of pipe rising at least 35 feet, used naturally to prevent backsiphonage due to atmospheric pressure limits.
Exam Prep & Tips
- Memorize Backflow Hazards: Test-makers love asking which backflow preventer goes with which hazard. Know Table 608.1 (e.g., RPZs for high hazard/backpressure, Vacuum breakers for backsiphonage only).
- Air Gap Sizing: The rule of thumb for air gaps is two times the effective opening of the pipe, but never less than 1 inch (or 1.5 inches if close to a wall).
- Valve Locations: Know the difference between where a "full-open valve" (gate/ball valve) is required versus a "shutoff valve" (stop valve).
- Purple Pipe: Always associate the color purple with nonpotable water distribution.
- Well Clearances: Memorize the distance from private wells to contamination sources (e.g., 50 ft to a septic tank seepage pit).
Prohibited Practices
- DO NOT replace existing metallic water service piping used for grounding with non-metallic pipe until another approved grounding method is in place.
- DO NOT install well pits.
- DO NOT run water service pipes in, under, or above cesspools, septic tanks, drainage fields, or seepage pits.
- DO NOT use cement or concrete joints on water pipes.
- DO NOT use solvent-cement joints to connect different types of plastic pipe together.
- DO NOT use saddle-type fittings.
- DO NOT place potable water gravity tanks directly beneath soil/waste piping or contamination sources.
- DO NOT install potable water outlets or combination stop-and-waste valves underground or below grade (except approved freeze-proof yard hydrants).
- DO NOT return water used for heating/cooling processes back into the potable water system.
- DO NOT reuse pipes that once carried nonpotable fluids to carry potable water.
- DO NOT install vacuum breakers under exhaust hoods or anywhere they could suck in toxic fumes.
- DO NOT make bends in PE plastic pipe within 10 pipe diameters of any fitting or valve.
Most Tested Numbers
- Pipe Sizes:
- Minimum water service pipe diameter: 3/4 inch.
- Minimum fixture supply size for a water closet (flush tank) or lavatory: 3/8 inch.
- Minimum fixture supply size for a bathtub, sink, or shower: 1/2 inch.
- Pressures:
- Max allowable static pressure before needing a PRV: 80 psi.
- Min working pressure rating for underground water service at 73.4ºF: 160 psi.
- Min pressure rating for hot water distribution pipe at 180ºF: 100 psi.
- Max pressure for vacuum relief on a pressure tank: 200 psi.
- Booster pump low-pressure cutoff: 10 psi.
- Flow Rates & Consumption:
- Max water closet flush volume: 1.6 gallons.
- Max urinal flush volume: 1.0 gallon.
- Max flow rate for a private lavatory or sink: 2.2 gpm at 60 psi.
- Max flow rate for a shower head: 2.0 gpm at 80 psi.
- Distances & Clearances:
- Water service and building sewer separation: 5 feet horizontal OR water pipe must be 12 inches above the sewer top.
- Max distance from fixture connection point to the supply pipe termination: 30 inches.
- Max developed length of hot water piping from source to fixture: 50 feet.
- Basement well pump mounting height: 18 inches above the floor.
- Nonpotable warning labels interval: Every 25 feet.
- Air gap required above gravity tank overflow: 4 inches.
- Barometric loop minimum height: 35 feet.
- Vacuum breaker critical level above flood rim: 6 inches minimum (12 inches for pressure/spill-resistant assemblies, 1 inch for deck-mounted).
- Medical vacuum breakers height: Bedpan washers = 5 feet above floor; Lab/Health care hose connections = 6 feet above floor.
- Temperatures & Lead Content:
- Max limit for tempered water: 110ºF.
- Recirculation system cold water inlet max temp limit: 104ºF.
- Max lead content for pipes/fittings generally: 8%.
- Max weighted average lead content for drinking water pipes/fittings: 0.25%.
- Disinfection:
- Chlorine flush: 50 ppm for 24 hours, OR 200 ppm for 3 hours.
Section 601: General
- 601.1 Scope: This chapter outlines the rules for materials, design, and installation of both hot and cold water supply systems.
- 601.2 Solar energy utilization: Solar heating systems must comply with the code and cannot compromise backflow or cross-connection protections.
- 601.3 Existing piping used for grounding: If a metal water service pipe is currently acting as the electrical ground for a building, you cannot replace it with plastic (nonmetallic) until a licensed electrician establishes a new, approved ground.
- 601.4 Tests: The water distribution system must be tested to ensure there are no leaks.
- 601.5 Rehabilitation of piping: If old pressure pipes are fixed by blowing an epoxy lining inside them, the system must meet ASTM F2831.
Section 602: Water Required
- 602.1 - 602.2 Potable water required: Any structure meant for human occupancy must have enough potable (drinking-quality) water at proper pressures. Potable water is strictly required for drinking, bathing, cooking, or medical processing.
- 602.3 Individual water supply: If city water isn't available, you must use an individual source like a well. Surface water or cisterns require approved treatment.
- 602.3.2 Minimum quantity: The well/storage must keep up with the fixture demands of the building.
- 602.3.3 Water quality: The authority having jurisdiction must approve the water as potable before you hook it to the plumbing system.
- 602.3.4 Disinfection: Newly constructed individual water systems must be flushed and disinfected.
- 602.3.5 Pumps: Pumps must be rated for potable water (NSF 61). They must be sealed to the well casing.
- 602.3.5.1 Pump enclosure: Pump rooms must be drained and protected from freezing. If a pump is in a basement, it must sit on a block at least 18 inches above the floor. Well pits are strictly prohibited.
Section 603: Water Service
- 603.1 Size of water service pipe: The main water pipe coming into the building must be properly sized for the demand but can never be smaller than 3/4 inch in diameter.
- 603.2 Separation of water service and building sewer: Water and sewer lines should ideally be kept apart. If they are in the same trench, the sewer must be made of approved heavy-duty materials. If not, they must be separated by at least 5 feet of solid earth horizontally. If they cross, the water pipe must be sleeved for 5 feet on either side of the sewer. You can ignore the 5-foot horizontal rule if the bottom of the water pipe is at least 12 inches higher than the top of the sewer line.
- 603.2.1 Sources of pollution: Do not run water service pipes through or near cesspools, septic tanks, or drain fields.
Section 604: Design of Building Water Distribution System
- 604.1 - 604.3 Design criteria: Water systems must be designed to handle peak demand, maintaining minimum flow rates and pressures at the fixture outlets.
- 604.4 Maximum flow: To conserve water, fixtures have maximum allowed flow rates. For example, standard water closets use max 1.6 gallons per flush; private lavatory faucets flow at max 2.2 gpm.
- 604.5 Size of fixture supply: The pipe connecting the wall distribution line to the actual fixture cannot be smaller than the sizes listed in Table 604.5 (e.g., 3/8" for toilets and lavatories, 1/2" for showers and sinks). The supply pipe can only stick out up to 30 inches before connecting to the fixture.
- 604.6 Variable street pressures: Design the system based on the minimum pressure available from the city.
- 604.7 Inadequate water pressure: If street pressure is too low, you must install a booster pump system.
- 604.8 Water pressure-reducing valve (PRV): If street static pressure exceeds 80 psi, you must install a PRV with a strainer to knock the pressure down to 80 psi or lower.
- Note: You don't need a PRV on lines serving only outside hose bibbs.
- The PRV must fail "open" so you don't lose water flow, and it must be installed in a way that allows removal/repair without cutting the pipe.
- 604.9 Water hammer: Systems with quick-closing valves (like dishwashers or washing machines) must have water-hammer arrestors to absorb the shock and prevent pipe banging.
- 604.10 Manifolds: Manifold systems (like PEX home-run setups) must be sized correctly based on velocity, and every shutoff valve on the manifold must be clearly labeled to show which fixture it controls. Access to the manifold is required.
- 604.11 Pressure balancing valves: Individual in-line pressure balancing valves must be accessible but cannot replace the main anti-scald valve required in a shower.
Section 605: Materials, Joints, and Connections
- 605.1 Soil and ground water: Never bury water pipes in soil contaminated with fuels or solvents. If suspected, a chemical analysis is required.
- 605.2 Lead content: General water pipes/fittings can have a max of 8% lead. Pipes/fittings used specifically for drinking/cooking water must have a weighted average of 0.25% lead or less (NSF 372).
- 605.3 Water service pipe: Underground water service pipes must be rated for at least 160 psi at 73.4ºF. Dual check valves installed on the supply must meet ASSE 1024.
- 605.4 Water distribution pipe: Hot water pipes inside the building must be rated for at least 100 psi at 180ºF.
- 605.5 Fittings: Fittings must match the pipe material and be NSF 61 approved. Mechanically formed tees (pulled tees) must have a height at least 3x the branch wall thickness and require two inspection dimples.
- 605.6 Flexible connectors: Supply lines must be accessible.
- 605.9 Prohibited joints: You cannot use cement/concrete joints, unapproved fittings, solvent cement between different types of plastic (e.g., gluing PVC to ABS directly), or saddle-type fittings.
- 605.10 - 605.22 Material-specific joints:
- ABS/PVC/CPVC: Clean surfaces, apply appropriate primers/cements. Threaded plastic needs Schedule 80 pipe thickness.
- Copper: Soldered joints must be "lead-free" (0.2% lead max). Ream cut ends.
- PEX/PE: Use approved mechanical, crimp, or push-fit joints. Keep PE pipe bends at least 10 pipe diameters away from fittings.
- Stainless Steel: Welded or mechanical joints.
- 605.23 Joints between different materials: Transitioning between materials (e.g., copper to galvanized steel) requires a dielectric fitting or union to prevent galvanic corrosion. Transitioning plastics requires approved adapters.
Section 606: Installation of the Building Water Distribution System
- 606.1 Location of full-open valves: "Full-open" valves (valves that don't restrict flow, like ball valves) must be placed at the water service entrance, meter discharge, base of risers, top of down-feeds, entrance to dwelling units, and on water heater supplies.
- 606.2 Location of shutoff valves: Shutoff valves (stops) must be installed at every plumbing fixture (except tubs/showers in residential), hose bibbs, and appliances.
- 606.3 - 606.4 Access and ID: You must be able to get to all valves, and they must be tagged/identified if it's not totally obvious what they control.
- 606.5 Water pressure booster systems: Used when city pressure is too low.
- Gravity tanks must be covered and vented (vent needs a bug screen).
- Overflows must discharge safely with an air gap.
- Pumps need a low-pressure cutoff at 10 psi so they don't suck the city main dry.
- Tanks need a drain pipe at the lowest point.
- Pressure relief: Hydropneumatic tanks need a pressure relief valve set to the tank's rating.
Section 607: Hot Water Supply System
- 607.1 Where required: Hot water is required in homes for bathing, washing, and cooking. Commercial buildings require hot water for cleaning/laundry, and hot/tempered water for bathing/washing.
- Tempered water: Must be controlled to a max of 110ºF by an approved mixing valve. (Shower anti-scald valves are a separate, additional requirement).
- 607.2 Maximum distance: The pipe length from the hot water source to the fixture cannot exceed 50 feet. Recirculating lines or heat-trace cables count as the "source".
- 607.2.2 Recirculation systems: Pumps must be controlled by demand (a button, sensor, or flow switch) to save energy, and the cold water return pipe can't exceed 104ºF.
- 607.3 Thermal expansion control: If you have a closed system (e.g., a check valve or PRV on the main line), water expanding as it heats up in the water heater has nowhere to go. You must install a thermal expansion tank downstream of those check valves to absorb the pressure.
- 607.4 Hot water location: Hot water always goes on the left side of the faucet.
Section 608: Protection of Potable Water Supply
- 608.1 - 608.8 General rules: You must protect the drinking water from contamination. Do not pipe cooling/heating process water back into the drinking lines. Do not put potable outlets or stop-and-waste valves underground.
- 608.9 Identification of nonpotable water: Reclaimed/graywater pipes must be clearly marked. The pipes must be purple or wrapped in purple tape. Warning signs must say "CAUTION: NONPOTABLE WATER - DO NOT DRINK" every 25 feet.
- 608.10 - 608.11 Reutilization and Reuse: Never reuse process water for drinking. Never use old nonpotable pipes for a new potable water system.
- 608.14 - 608.16 Backflow protection methods:
- Air gap: The best protection. Measured from the pipe opening to the flood rim. Usually 2x the pipe diameter, minimum 1 inch.
- Vacuum breakers (Atmospheric & Pressure): Must be installed at least 6 inches above the flood level rim. Cannot be installed in toxic areas (like exhaust hoods).
- RPZ (Reduced Pressure Principle): Highest mechanical protection. Used for high-hazard situations. The relief port spits water if it fails, so it must discharge to an indirect waste via air gap where it won't cause damage.
- Barometric loop: Must rise 35 feet high.
- 608.17 Specific connections:
- Carbonated beverage dispensers: Need an ASSE 1022 backflow preventer.
- Boilers: Need a vented backflow preventer (ASSE 1012). If chemicals are added, needs an RPZ or Air Gap.
- Sprinkler/Irrigation systems: Must be protected by backflow devices based on the hazard level (chemicals = RPZ).
- 608.18 Individual water supplies (Wells): Private wells must be kept safe distances from contamination (e.g., 50 ft from septic fields). Casings must extend at least 10 feet into the ground and sit at least 6 inches above the platform. They must have watertight covers.
Section 609: Health Care Plumbing
- 609.1 - 609.2 Redundancy: Group I-2 Condition 2 facilities (hospitals) must have at least two separate water service pipes. If one breaks, the other must handle the entire building's demand. Underground plastic pipes need a tracer wire.
- 609.3 - 609.8 Special rules:
- Bedpan washer vacuum breakers must be 5 feet off the floor.
- Lab/health care hose vacuum breakers must be 6 feet off the floor.
- You cannot supply clinical sinks or toilets with jet orifices from the normal water supply unless protected.
- Sterilizers need leakage diverters so unsterile water doesn't sneak into the sterile zone.
Section 610: Disinfection of Potable Water System
- 610.1 Purge and disinfect: New water systems must be flushed clean, then disinfected with chlorine.
- Method 1: 50 parts per million (ppm) chlorine left to sit for 24 hours.
- Method 2: 200 ppm chlorine left to sit for 3 hours.
- Afterward, flush the system clean and pass a bacteriological test.
Section 611: Drinking Water Treatment Units
- 611.1 - 611.3 Reverse Osmosis (RO): RO units must comply with NSF standards. The waste discharge line from an RO system must connect to the drainage system via an air gap to prevent sewage from backing up into the filter.
Section 612: Solar Systems
- 612.1 Code overlap: Solar heating systems for water must comply with the International Mechanical Code (IMC).
Section 613: Temperature Control Devices and Valves
- 613.1 Master mixing valves: Temperature-actuated mixing valves used to limit the overall water temperature in a system must comply with ASSE 1017 and be installed right at the hot water source.
TABLE 604.3 - WATER DISTRIBUTION SYSTEM DESIGN CRITERIA REQUIRED CAPACITY AT FIXTURE SUPPLY PIPE OUTLETS
| FIXTURE SUPPLY OUTLET SERVING | FLOW RATE (gpm) | FLOW PRESSURE (psi) |
|---|---|---|
| Bathtub, balanced-pressure, thermostatic or combination balanced-pressure/thermostatic mixing valve | 4 | 20 |
| Bidet, thermostatic mixing valve | 2 | 20 |
| Combination fixture | 4 | 8 |
| Dishwasher, residential | 2.75 | 8 |
| Drinking fountain | 0.75 | 8 |
| Laundry tray | 4 | 8 |
| Lavatory, private | 0.88 | 8 |
| Lavatory, private, mixing valve | 0.88 | 8 |
| Lavatory, public | 0.48 | 8 |
| Shower | 2.5 | 8 |
| Shower, balanced-pressure, thermostatic or combination balanced-pressure/thermostatic mixing valve | 2.5 | 20 |
| Sill cock, hose bibb | 5 | 8 |
| Sink, residential | 1.75 | 8 |
| Sink, service | 3 | 8 |
| Urinal, valve | 12 | 25 |
| Water closet, blow out, flushometer valve | 25 | 45 |
| Water closet, flushometer tank | 1.6 | 20 |
| Water closet, siphonic, flushometer valve | 25 | 35 |
| Water closet, tank, close coupled | 3 | 20 |
| Water closet, tank, one piece | 6 | 20 |
For SI:1 pound per square inch = 6.895 kPa, 1 gallon per minute = 3.785 L/m.\n a. For additional requirements for flow rates and quantities, see Section 604.4.\n b. Where the shower mixing valve manufacturer indicates a lower flow rating for the mixing valve, the lower value shall be applied.\n
TABLE 604.4 - MAXIMUM FLOW RATES AND CONSUMPTION FOR PLUMBING FIXTURES AND FIXTURE FITTINGS
| PLUMBING FIXTURE OR FIXTURE FITTING | MAXIMUM FLOW RATE OR QUANTITY |
|---|---|
| Lavatory, private | 2.2 gpm at 60 psi |
| Lavatory, public (metering) | 0.25 gallon per metering cycle |
| Lavatory, public (other than metering) | 0.5 gpm at 60 psi |
| Shower head (a,c) | 2.0 gpm at 80 psi |
| Sink faucet | 2.2 gpm at 60 psi |
| Urinal | 1.0 gallon per flushing cycle |
| Water closet | 1.6 gallons per flushing cycle |
For SI: 1 gallon = 3.785 L, 1 gallon per minute = 3.785 L/m, 1 pound per square inch = 6.895 kPa.\n a. A hand-held shower spray is a shower head.\n b. Consumption tolerances shall be determined from referenced standards.\n c. Shower heads shall comply with all requirements for high-efficiency showerheads in ASME A112.18.1-2020/CSA B125.1.\n
TABLE 604.5 - MINIMUM SIZES OF FIXTURE WATER SUPPLY PIPES
| FIXTURE | MINIMUM PIPE SIZE (inch) |
|---|---|
| Bathtubs (60″ x 32″ and smaller) | 1/2 |
| Bathtubs (larger than 60″ x 32″) | 1/2 |
| Bidet | 3/8 |
| Combination sink and tray | 1/2 |
| Dishwasher, domestic | 1/2 |
| Drinking fountain | 3/8 |
| Hose bibbs | 1/2 |
| Kitchen sink | 1/2 |
| Laundry, 1, 2 or 3 compartments | 1/2 |
| Lavatory | 3/8 |
| Shower, single head | 1/2 |
| Sinks, flushing rim | 3/4 |
| Sinks, service | 1/2 |
| Urinal, flush tank | 1/2 |
| Urinal, flushometer valve | 3/4 |
| Wall hydrant | 1/2 |
| Water closet, flush tank | 3/8 |
| Water closet, flushometer tank | 3/8 |
| Water closet, flushometer valve | 1 |
| Water closet, one piece | 1/2 |
For SI: 1 inch = 25.4 mm, 1 foot = 304.8 mm, 1 pound per square inch = 6.895 kPa.\n a. Where the developed length of the distribution line is 50 feet or less, and the available pressure at the meter is 35 psi or greater, the minimum size of an individual distribution line supplied from a manifold and installed as part of a parallel water distribution system shall be one nominal tube size smaller than the sizes indicated.
TABLE 604.10.1 - MANIFOLD SIZING
| NOMINAL SIZE INTERNAL DIAMETER (inches) | MAXIMUM DEMAND (gpm) Velocity at 4 feet per second | MAXIMUM DEMAND (gpm) Velocity at 8 feet per second |
|---|---|---|
| 1/2 | 2 | 5 |
| 3/4 | 6 | 11 |
| 1 | 10 | 20 |
| 1 1/4 | 15 | 31 |
| 1 1/2 | 22 | 44 |
For SI: 1 inch = 25.4 mm, 1 gallon per minute = 3.785 L/m, 1 foot per second = 0.305 m/s.
TABLE 605.3 - WATER SERVICE PIPE
| MATERIAL | STANDARD |
|---|---|
| Acrylonitrile butadiene styrene (ABS) plastic pipe | ASTM D1527; ASTM D2282 |
| Chlorinated polyvinyl chloride (CPVC) plastic pipe | ASTM D2846; ASTM F441; ASTM F442; CSA B137.6 |
| Chlorinated polyvinyl chloride/aluminum/chlorinated polyvinyl chloride (CPVC/AL/CPVC) | ASTM F2855 |
| Copper or copper-alloy pipe | ASTM B42; ASTM B43; ASTM B302 |
| Copper or copper-alloy tubing (Type K, WK, L, WL, M or WM) | ASTM B75; ASTM B88; ASTM B251; ASTM B447 |
| Cross-linked polyethylene (PEX) plastic pipe and tubing | ASTM F876; AWWA C904; CSA B137.5 |
| Cross-linked polyethylene/aluminum/cross-linked polyethylene (PEX-AL-PEX) pipe | ASTM F1281; ASTM F2262; CSA B137.10 |
| Cross-linked polyethylene/aluminum/high-density polyethylene (PEX-AL-HDPE) | ASTM F1986 |
| Ductile iron water pipe | AWWA C115/A21.15; AWWA C151/A21.51 |
| Galvanized steel pipe | ASTM A53 |
| Polyethylene (PE) plastic pipe | ASTM D2239; ASTM D3035; AWWA C901; CSA B137.1 |
| Polyethylene (PE) plastic tubing | ASTM D2737; AWWA C901; CSA B137.1 |
| Polyethylene/aluminum/polyethylene (PE-AL-PE) pipe | ASTM F1282; CSA B137.9 |
| Polyethylene of raised temperature (PE-RT) plastic tubing | ASTM F2769; CSA B137.18 |
| Polypropylene (PP) plastic pipe or tubing | ASTM F2389; CSA B137.11 |
| Polyvinyl chloride (PVC) plastic pipe | ASTM D1785; ASTM D2241; ASTM D2672; CSA B137.3 |
| Stainless steel pipe (Type 304/304L) | ASTM A269/A269M; ASTM A312; ASTM A778 |
| Stainless steel pipe (Type 316/316L) | ASTM A269/A269M; ASTM A312; ASTM A778 |
| Stainless steel tubing (Type 304/304L) | ASTM A269/A269M; ASTM A312; ASTM A778 |
| Stainless steel tubing (Type 316/316L) | ASTM A269/A269M; ASTM A312; ASTM A778 |
TABLE 605.4 - WATER DISTRIBUTION PIPE
| MATERIAL | STANDARD |
|---|---|
| Chlorinated polyvinyl chloride (CPVC) plastic pipe and tubing | ASTM D2846; ASTM F441; ASTM F442; CSA B137.6 |
| Chlorinated polyvinyl chloride/aluminum/chlorinated polyvinyl chloride (CPVC/AL/CPVC) | ASTM F2855 |
| Copper or copper-alloy pipe | ASTM B42; ASTM B43; ASTM B302 |
| Copper or copper-alloy tubing (Type K, WK, L, WL, M or WM) | ASTM B75; ASTM B88; ASTM B251; ASTM B447 |
| Cross-linked polyethylene (PEX) plastic tubing | ASTM F876; CSA B137.5 |
| Cross-linked polyethylene/aluminum/cross-linked polyethylene (PEX-AL-PEX) pipe | ASTM F1281; ASTM F2262; CSA B137.10 |
| Cross-linked polyethylene/aluminum/high-density polyethylene (PEX-AL-HDPE) | ASTM F1986 |
| Ductile iron pipe | AWWA C115/A21.15; AWWA C151/A21.51 |
| Galvanized steel pipe | ASTM A53 |
| Polyethylene/aluminum/polyethylene (PE-AL-PE) composite pipe | ASTM F1282 |
| Polyethylene of raised temperature (PE-RT) plastic tubing | ASTM F2769; CSA B137.18 |
| Polypropylene (PP) plastic pipe or tubing | ASTM F2389; CSA B137.11 |
| Stainless steel pipe (Type 304/304L) | ASTM A312; ASTM A778 |
| Stainless steel pipe (Type 316/316L) | ASTM A312; ASTM A778 |
| Stainless steel tubing (Type 304/304L) | ASTM A269/A269M; ASTM A312; ASTM A778 |
| Stainless steel tubing (Type 316/316L) | ASTM A269/A269M; ASTM A312; ASTM A778 |
TABLE 605.5 - PIPE FITTINGS
| MATERIAL | STANDARD |
|---|---|
| Acrylonitrile butadiene styrene (ABS) plastic | ASTM D2468 |
| Cast iron | ASME B16.4 |
| Chlorinated polyvinyl chloride (CPVC) plastic | ASSE 1061; ASTM D2846; ASTM F437; ASTM F438; ASTM F439; CSA B137.6 |
| Copper or copper alloy | ASME B16.15; ASME B16.18; ASME B16.22; ASME B16.26; ASME B16.51; ASSE 1061; ASTM F1476; ASTM F1548; ASTM F3226 |
| Cross-linked polyethylene/aluminum/high-density polyethylene (PEX-AL-HDPE) | ASTM F1986 |
| Fittings for cross-linked polyethylene (PEX) plastic tubing | ASSE 1061; ASTM F877; ASTM F1807; ASTM F1960; ASTM F2080; ASTM F2098; ASTM F2159; ASTM F2434; ASTM F2735; ASTM F3347; ASTM F3348; CSA B137.5 |
| Fittings for polyethylene of raised temperature (PE-RT) plastic tubing | ASSE 1061; ASTM D3261; ASTM F1807; ASTM F2098; ASTM F2159; ASTM F2735; ASTM F2769; ASTM F3347; ASTM F3348; CSA B137.18 |
| Gray iron and ductile iron | ASTM F1476; ASTM F1548; AWWA C110/A21.10; AWWA C153/A21.53; |
| Insert fittings for polyethylene/aluminum/polyethylene (PE-AL-PE) and cross-linked polyethylene/aluminum/cross-linked polyethylene (PEX-AL-PEX) | ASTM F1281; ASTM F1282; ASTM F1974; CSA B137.9; CSA B137.10 |
| Malleable iron | ASME B16.3 |
| Metal (copper alloy) insert fittings for polyethylene/alumi-num/polyethylene (PE-AL-PE) and cross-linked polyethylene/aluminum/cross-linked polyethylene (PEX-AL-PEX) | ASTM F1974 |
| Polyethylene (PE) plastic pipe | ASTM D2609; ASTM D2683; ASTM D3261; ASTM F1055; CSA B137.1 |
| Polypropylene (PP) plastic pipe or tubing | ASTM F2389; CSA B137.11 |
| Polyvinyl chloride (PVC) plastic | ASTM D2464; ASTM D2466; ASTM D2467; CSA B137.2; CSA B137.3 |
| Stainless steel (Type 304/304L) | ASTM A269; ASTM A312; ASTM A778; ASTM F1476; ASTM F1548; ASTM F3226 |
| Stainless steel (Type 316/316L) | ASTM A269; ASTM A312; ASTM A778; ASTM F1476; ASTM F1548; ASTM F3226 |
| Steel | ASME B16.9; ASME B16.11; ASME B16.28; ASTM F1476; ASTM F1548; ASTM F3226 |
TABLE 605.7 - VALVES
| MATERIAL | STANDARD |
|---|---|
| Chlorinated polyvinyl chloride (CPVC) plastic | ASME A112.4.14; ASME A112.18.1/CSA B125.1; ASTM F1970; CSA B125.3; IAPMO Z1157; MSS SP-122 |
| Copper or copper alloy | ASME A112.4.14; ASME A112.18.1/CSA B125.1; ASME B16.34; CSA B125.3; IAPMO Z1157; MSS SP-67; MSS SP-80; MSS SP-110; MSS SP-139 |
| Cross-linked polyethylene (PEX) plastic | ASME A112.4.14; ASME A112.18.1/CSA B125.1; CSA B125.3; IAPMO Z1157; NSF 359 |
| Gray iron and ductile iron | AWWA C500; AWWA C504; AWWA C507; IAPMO Z1157; MSS SP-67; MSS SP-70; MSS SP-71; MSS SP-72; MSS SP-78 |
| Polypropylene (PP) plastic | ASME A112.4.14; ASTM F2389; IAPMO Z1157 |
| Polyvinyl chloride (PVC) plastic | ASME A112.4.14; ASTM F1970; IAPMO Z1157; MSS SP-122 |
| Stainless steel (Type 304/304L) | ASME A112.4.14; IAPMO Z1157 |
| Stainless steel (Type 316/316L) | ASME A112.4.14; IAPMO Z1157 |
TABLE 605.8 - MANUFACTURED PIPE NIPPLES
| MATERIAL | STANDARD |
|---|---|
| Copper, copper alloy, and chromium-plated | ASTM B687 |
| Steel | ASTM A733 |
TABLE 606.5.4 SIZES FOR OVERFLOW PIPES FOR WATER SUPPLY TANKS
| MAXIMUM CAPACITY OF WATER SUPPLY LINE TO TANK (gpm) | DIAMETER OF OVERFLOW PIPE (inches) |
|---|---|
| 0 - 50 | 2 |
| 50 - 150 | 2 1/ 2 |
| 150 - 200 | 3 |
| 200 - 400 | 4 |
| 400 - 700 | 5 |
| 700 - 1,000 | 6 |
| Over 1,000 | 8 |
For SI: 1 inch = 25.4 mm, 1 gallon per minute = 3.785 L/m.
TABLE 606.5.7 - SIZE OF DRAIN PIPES FOR WATER TANKS
| TANK CAPACITY (gallons) | DRAIN PIPE (inches) |
|---|---|
| Up to 750 | 1 |
| 751 to 1,500 | 1 1/2 |
| 1,501 to 3,000 | 2 |
| 3,001 to 5,000 | 2 1/2 |
| 5,000 to 7,500 | 3 |
| Over 7,500 | 4 |
For SI: 1 inch = 25.4 mm, 1 gallon = 3.785 L.
TABLE 608.1 - APPLICATION OF BACKFLOW PREVENTERS
| DEVICE | DEGREE OF HAZARD | APPLICATION | APPLICABLE STANDARDS |
|---|---|---|---|
| Backflow prevention assemblies: | |||
| Double check backflow prevention assembly | Low hazard | Backpressure or backsiphonage Sizes 1/4″-16″ | ASSE 1015; AWWA C510; CSA B64.5; CSA B64.5.1 |
| Double check detector fire protection backflow prevention assemblies | Low hazard | Backpressure or backsi-phonage Sizes 1″-16″ | ASSE 1048 |
| Pressure vacuum breaker assembly | High or low hazard | Backsiphonage only Sizes 1/2″-2″ | ASSE 1020; CSA B64.1.2 |
| Reduced pressure principle backflow prevention assembly | High or low hazard | Backpressure or backsiphonage Sizes 1/4″-16″ | ASSE 1013; AWWA C511; CSA B64.4; CSA B64.4.1 |
| Reduced pressure detector fire protection backflow prevention assemblies | High or low hazard | Backsiphonage or backpressure (automatic sprinkler systems) | ASSE 1047 |
| Spill-resistant vacuum breaker assembly | High or low hazard | Backsiphonage only Sizes 1/4″-2″ | ASSE 1056; CSA B64.1.3 |
| Backflow preventer plumbing devices: | |||
| Antisiphon-type fill valves for gravity water closet flush tanks | High hazard | Backsiphonage only | ASSE 1002/ASME A112.1002/CSA B125.12; CSA B125.3 |
| Backflow preventer for carbonated beverage machines | Low hazard | Backpressure or backsiphonage Sizes 1/4″-1/2″ | ASSE 1022 |
| Backflow preventer with intermediate atmospheric vents | Low hazard | Backpressure or backsiphonage Sizes 1/4″-3/4″ | ASSE 1012; CSA B64.3 |
| Backflow preventer with intermediate atmospheric vent and pressure-reducing valve. | Low hazard | Backpressure or backsiphonage Sizes 1/2″-3/4″ | ASSE 1081 |
| Dual-check-valve-type backflow preventer | Low hazard | Backpressure or backsiphonage Sizes 1/4″-2″ | ASSE 1024; CSA B64.6 |
| Hose connection backflow preventer | High or low hazard | Low head backpressure, rated working pressure, backpressure or backsiphonage Sizes 1/2″-1″ | ASME A112.21.3; ASSE 1052; CSA B64.2.1.1 |
| Hose connection vacuum breaker | High or low hazard | Low head backpressure or backsiphonage Sizes 1/2″, 3/4″, 1″ | ASME A112.21.3; ASSE 1011; CSA B64.2; CSA B64.2.1 |
| Laboratory faucet backflow preventer | High or low hazard | Low head backpressure and backsiphonage | ASSE 1035; CSA B64.7 |
| Pipe-applied atmospheric-type vacuum breaker | High or low hazard | Backsiphonage only Sizes 1/8″-8″ | ASSE 1001; CSA B64.1.1 |
| Vacuum breaker wall hydrants, frost-resistant, automatic-draining-type | High or low hazard | Low head backpressure or backsiphonage Sizes 3/4˝, 1˝ | ASME A112.21.3; ASSE 1019; CSA B64.2.2 |
| Other means or methods: | |||
| Air gap | High or low hazard | Backsiphonage or backpressure | ASME A112.1.2 |
| Air gap fittings for use with plumbing fixtures, appliances and appurtenances | High or low hazard | Backsiphonage or backpressure | ASME A112.1.3 |
| Barometric loop | High or low hazard | Backsiphonage only | (See Section 608.14.4) |
For SI: 1 inch = 25.4 mm.\n a. Low hazard - See Pollution (Section 202).\n High hazard - See Contamination (Section 202).\n b. See Backpressure, low head (Section 202, Backflow).\n See Backsiphonage (Section 202, Backflow).
TABLE 608.9.2.2 - SIZE OF PIPE IDENTIFICATION
| PIPE DIAMETER (inches) | LENGTH BACKGROUND COLOR FIELD (inches) | SIZE OF LETTERS (inches) |
|---|---|---|
| 3/4 to 1 1/4 | 8 | 0.5 |
| 1 1/2 to 2 | 8 | 0.75 |
| 2 1/2 to 6 | 12 | 1.25 |
| 8 to 10 | 24 | 2.5 |
| over 10 | 32 | 3.5 |
For SI: 1 inch = 25.4 mm.
TABLE 608.16.1 - MINIMUM REQUIRED AIR GAPS
| FIXTURE | MINIMUM AIR GAP Away from a wall (inches) | MINIMUM AIR GAP Close to a wall (inches) |
|---|---|---|
| Lavatories and other fixtures with effective openings not greater than 1/2 inch in diameter | 1 | 1 1/2 |
| Sinks, laundry trays, gooseneck back faucets and other fixtures with effective openings not greater than 3/4 inch in diameter | 1 1/2 | 2 1/2 |
| Over-rim bath fillers and other fixtures with effective openings not greater than 1 inch in diameter | 2 | 3 |
| Drinking water fountains, single orifice not greater than 7/16 inch in diameter or multiple orifices with a total area of 0.150 square inch (area of circle 7/16 inch in diameter) | 1 | 1 1/2 |
| Effective openings greater than 1 inch | Two times the diameter of the effective opening | Three times the diameter of the effective opening |
For SI:1 inch = 25.4 mm, 1 square inch = 645 mm2.\n a. Applicable where walls or obstructions are spaced from the nearest inside-edge of the spout opening a distance greater than three times the diameter of the effective opening for a single wall, or a distance greater than four times the diameter of the effective opening for two intersecting walls.
TABLE 608.18.1 - DISTANCE FROM CONTAMINATION TO PRIVATE WATER SUPPLIES AND PUMP SUCTION LINES
| SOURCE OF CONTAMINATION | DISTANCE (feet) |
|---|---|
| Barnyard | 100 |
| Farm silo | 25 |
| Pasture | 100 |
| Pumphouse floor drain of cast iron draining to ground surface | 2 |
| Seepage pits | 50 |
| Septic tank | 25 |
| Sewer | 10 |
| Subsurface disposal fields | 50 |
| Subsurface pits | 50 |
For SI: 1 foot = 304.8 mm.