Type III: Low Pressure Chillers

Everything distinctive about Type III follows from one fact: a low pressure machine runs in a vacuum. That single point explains the purge unit, the freezing hazard, the deepest evacuation requirement in the tables and the very low test pressure.

Where it lives. 40 CFR 82.156 for the 25 mm Hg absolute requirement, and 82.152 for the low pressure definition.

What it covers. Vacuum operation and air ingress, purge units and their efficiency, the 32 degree freezing hazard during recovery, rupture discs and test pressures, centrifugal compressors and surge, approach temperature, and R-123 exposure limits.

On the exam. Questions often describe a symptom, such as a purge running constantly or an approach temperature that has risen, and ask for the cause. Both point back to air getting in or heat transfer getting worse.

A low pressure appliance uses a refrigerant with a liquid saturation pressure below 45 psia at 104 degrees F, such as R-11, R-113, R-123 and R-245fa.

  • 25 mm Hg absolute. The deepest requirement in the table and the only one quoted in absolute units.
  • Never below 32 degrees F during recovery. Water in the tubes freezes and splits them.
  • Test below 10 psig. The rupture disc opens near 15, and bursting it vents the entire charge.