Sanitary Drainage
Chapter 7 governs the design, installation, and materials required for sanitary drainage systems. It establishes the rules for moving wastewater safely from plumbing fixtures to a public sewer or private disposal system, covering proper pipe sizing based on drainage fixture units (DFUs), slope requirements, joint connections, and specialized systems like sumps and vacuum drainage.
- Gravity is King: Horizontal drainage piping must be installed with uniform slopes to ensure wastewater flows out reliably without clogging.
- No Shrinking Pipes: You can never reduce the size of a drainage pipe in the direction of flow.
- Cleanouts are Mandatory: Systems must provide accessible cleanouts at specific intervals (usually every 100 feet) and at major directional changes so blockages can be cleared.
- System Sizing: Plumbers size drainage pipes using "Drainage Fixture Units" (DFUs), a weighted system that calculates the estimated load a specific fixture puts on the plumbing system.
- Proper Directional Changes: Changes in piping direction must be made using specific approved fittings that guide flow smoothly (e.g., sanitary tees only for vertical-to-horizontal transitions, never horizontal-to-horizontal).
- Sanitary Drainage System: The network of pipes that removes wastewater (from toilets, sinks, showers, etc.) and carries it to the sewer or septic system.
- Building Drain: The lowest horizontal piping of a drainage system inside the building that receives discharge from other pipes.
- Building Sewer: The part of the drainage system that extends from outside the building's foundation out to the public sewer or private disposal system.
- Drainage Fixture Unit (DFU): A numerical weight given to a plumbing fixture to estimate its discharge load on the drainage system.
- Macerating Toilet System: A specialized pump that grinds up solid waste into a slurry before pumping it up into the main gravity drainage system.
- Pipe-Bursting: A trenchless method of replacing buried pipes by breaking the old pipe outward while pulling a new pipe into its place.
- Invert: The bottom inside floor of a horizontal pipe.
Exam Prep & Tips
- Memorize the Slope Table: You will undoubtedly be tested on Table 704.1 (1/4" slope for small pipes, 1/8" for medium, 1/16" for large).
- Master Cleanouts: Knowing the 100-foot rule, the 45-degree angle rule, and the specific clearance distances (18 inches vs. 36 inches) is guaranteed points on the exam.
- DFU Conversions: Remember the formula
1 GPM = 2 DFUsfor when a fixture's load is only given in gallons per minute. - Fittings and Flow: Be ready for questions asking which fitting is allowed for a specific change in direction (e.g., horizontal to horizontal requires a sweep or wye, never a sanitary tee).
Prohibited Practices
- Discharging toxic or harmful waste into the ground or waterways without approved treatment first.
- Reducing the size of drainage piping in the direction of flow.
- Connecting back-to-back water closets to a double sanitary tee (unless the connection points are at least 18 inches apart horizontally).
- Using a heel-inlet quarter bend to serve a water closet.
- Using a low-heel inlet as a wet-vented connection.
- Prohibited Joints:
- Cement or concrete joints.
- Mastic or hot-pour bituminous joints.
- Elastomeric rolling O-rings to join different diameter pipes.
- Solvent-cementing different types of plastic together (like PVC to ABS), except for one specific transition joint at the building drain/sewer line.
- Saddle-type fittings.
- Concealing required cleanouts inside walls, plenums, or tight crawl spaces without proper access.
- Using a threaded cleanout opening to add a new plumbing fixture without providing an equivalent cleanout elsewhere.
Most Tested Numbers
- Pipe Slopes:
- 1/4 inch per foot: For pipes 2-1/2 inches or smaller.
- 1/8 inch per foot: For pipes 3 to 6 inches.
- 1/16 inch per foot: For pipes 8 inches or larger.
- 1/4 inch per foot (2% slope): Minimum slope for piping draining to a grease interceptor, regardless of pipe size.
- Temperatures: Wastewater greater than 140°F (60°C) requires specially rated pipe.
- Cleanout Spacing:
- 100 feet: Maximum distance between cleanouts for horizontal drains inside and building sewers under 8 inches.
- 400 feet: Maximum distance between manholes for building sewers 8 inches and larger.
- 40 feet: If you have multiple >45-degree turns within 40 feet, one cleanout handles all of them.
- 10 feet: Distance upstream you are allowed to place the required building drain/sewer junction cleanout.
- Cleanout Clearances:
- 18 inches: Minimum clearance in front of cleanouts 6 inches and smaller.
- 36 inches: Minimum clearance in front of cleanouts 8 inches and larger.
- Sumps & Ejectors:
- 18 inches / 24 inches: Minimum diameter and depth for a sump pit.
- 2 inches: The sump cover can be no more than 2 inches below grade.
- 2 inches (Effluent level): Must be kept 2 inches below the invert of the incoming gravity drain.
- 10 pipe diameters: Minimum distance a pump discharge connection must be away from the base of a soil/waste stack.
- 2 inches: Diameter of spherical solids a standard water closet sewage pump must handle. (Other pumps handle 1/2 inch; grinder pumps can be 1-1/4 inch; macerators can be 3/4 inch).
- Stack Offsets: Horizontal branches must connect at least 10 pipe diameters downstream from the base of a stack.
- Lead Pipes/Traps: Wall thickness must be at least 1/8 inch.
- Vacuum Testing: Vacuum drainage systems must hold 19 inches of mercury.
- Conversions: 1 gpm = 2 DFUs. Clear-water waste receptors = 1/2 DFU.
Section 701: General
- 701.1 & 701.2 Scope & Sewer Connections: All sanitary drainage from a building must go to a public sewer. If there isn't one, it must connect to an approved private sewage system (like a septic tank). Exception: Certain greywater systems (showers, sinks, laundry) can be routed to separate approved greywater systems.
- 701.3 Separate Connections: Each building needs its own separate connection to the street sewer. However, multiple buildings on the same lot can connect to a shared building sewer.
- 701.4 & 701.5 Harmful Waste: You cannot dump raw, harmful waste into the ground or waterways. Anything that damages the public sewer must be treated (via interceptors/separators) before discharge.
- 701.6 & 701.7 Tests & Engineering: Systems must be tested per Chapter 3. Engineered systems must follow specific guidelines.
Section 702: Materials
- 702.1 - 702.4 Material Standards: Plumbers must use approved piping for above-ground (Table 702.1), underground (Table 702.2), building sewers (Table 702.3), and fittings (Table 702.4). Common materials include ABS, PVC, Cast Iron, and Copper.
- 702.5 Temperature Rating: If wastewater will exceed 140°F, you must use piping rated for high temperatures.
- 702.6 Chemical Waste: Chemical drainage systems must be completely separate from regular sanitary systems and use highly resistant materials (like CPVC or glass).
- 702.7 Lead Bends: Lead bends and traps must have a wall thickness of at least 1/8 inch.
Section 703: Building Sewer
- 703.1 & 703.2 Placement: Building sewers installed in unstable or filled ground must be made of strong, durable materials like cast iron, copper, ABS, or PVC.
- 703.3 Sanitary & Storm: Sanitary and storm sewers can be laid side-by-side in the same trench.
- 703.4 Existing Sewers: If you replace an entire plumbing system, you must run a camera down the existing underground pipes to ensure they are sloping correctly, intact, and sized properly before reusing them.
- 703.6 Combined Public Sewers: Even if the city uses a combined sanitary/storm sewer, your building's sanitary pipe must connect to it independently.
Section 704: Drainage Piping Installation
- 704.1 Slope: Gravity pipes must slope downwards uniformly to flow properly:
- 2-1/2" or smaller pipe: 1/4 inch drop per foot.
- 3" to 6" pipe: 1/8 inch drop per foot.
- 8" or larger pipe: 1/16 inch drop per foot.
- Grease interceptor lines: Always at least 1/4 inch per foot (2%).
- 704.2 No Pipe Reductions: You can never shrink a pipe size downstream. (Exceptions: A 4x3 closet flange, an offset flange, or an upright 4x3 closet bend).
- 704.3 Base of Stacks: Where a vertical stack hits horizontal, turbulent flow occurs. You cannot connect a horizontal branch line into this drain until it is at least 10 times the pipe's diameter downstream.
- 704.4 Future Fixtures: Pipes left for future use must be properly capped or plugged.
Section 705: Joints
This section details how to connect different materials:
- 705.2 ABS & 705.10 PVC Plastic: Joint surfaces must be clean. PVC requires purple primer (unless specific exceptions for non-pressure DWV up to 4" using third-party certified cement). Above-ground mechanical joints (like Ferncos) must be shielded.
- 705.3 Cast Iron: Hub/spigot joints are packed with oakum and molten lead (poured at least 1 inch deep) or compression gaskets. Hubless cast iron uses shielded mechanical couplings.
- 705.5 & 705.6 Copper: Joints can be brazed, soldered, threaded, or mechanical. You must ream the pipe, clean it, use flux, and use proper filler metals.
- 705.8 Steel: Galvanized steel joints are threaded or mechanical. Threads must be coated with pipe-joint compound or tape on the male threads only.
- 705.9 Lead: Must be burned (welded) or wiped (at least 3/4" wide and 3/8" thick).
- 705.16 Mixed Materials: When transitioning between different materials (like cast iron to plastic), you must use approved mechanical adapters or transition couplings. You cannot just glue ABS to PVC, except for one specific transition outside the building.
Section 706: Connections Between Drainage Piping and Fittings
- 706.1 & 706.2 Fitting Types: You must use approved drainage fittings. They cannot have internal ledges or shoulders that catch waste. Threads must be recessed.
- 706.3 Direction Changes: Table 706.3 dictates which fittings to use based on the direction of flow.
- Vertical to Horizontal requires sweeps or wyes.
- Horizontal to Horizontal requires sweeps or wyes. You cannot use a sanitary tee for horizontal to horizontal changes.
- Double sanitary tees cannot be used for back-to-back toilets or pumped fixtures unless the toilets are 18+ inches apart.
- 706.4 Quarter Bends: Heel-inlet quarter bends are okay unless they serve a toilet.
Section 707: Prohibited Joints and Connections
- 707.1 Banned Connections: You cannot use cement/concrete joints, mastic/hot-pour tar, saddle-type fittings, or roll O-rings to step down pipe sizes.
Section 708: Cleanouts
- 708.1.1 & 708.1.2 Spacing: Horizontal pipes need cleanouts every 100 feet. Large building sewers (8"+) use manholes every 400 feet.
- 708.1.3 Building Sewer Junction: You need a cleanout right where the building drain meets the building sewer (or within 10 feet upstream).
- 708.1.4 Changes of Direction: Any horizontal turn over 45 degrees needs a cleanout. If there are multiple turns within 40 feet, one cleanout can cover them.
- 708.1.5 Size: Cleanouts must be the same size as the pipe, up to 4 inches. (You don't need a 6-inch cleanout for a 6-inch pipe; a 4-inch cleanout is the max required).
- 708.1.10 Clearances: You must leave working room in front of cleanouts. 18 inches for pipes 6" and smaller. 36 inches for pipes 8" and larger.
- 708.1.11 Access: Cleanouts cannot be hidden in walls or tight crawl spaces (less than 24" high) without proper access panels. Floor cleanouts must sit flush with the floor.
- 708.1.12 Prohibited Use: You cannot unscrew a cleanout plug, hook up a sink drain to it, and leave the pipe without a cleanout.
Section 709: Fixture Units
- 709.1 & 709.2 DFUs: Sizing is based on Drainage Fixture Units (DFUs). Table 709.1 assigns values (e.g., a bathtub is 2 DFUs, a residential toilet is 3 or 4 DFUs). If a fixture isn't listed, size it by its trap size (Table 709.2).
- 709.3 GPM to DFU: If you only know a machine pumps out gallons per minute, convert it: 1 GPM = 2 DFUs.
- 709.4 Clear-Water Receptors: Floor sinks just catching ice bin or display case clear water count as 1/2 DFU.
Section 710: Drainage System Sizing
- 710.1 Load Sizing: Use Table 710.1(1) for sizing building drains/sewers based on slope and total DFUs. Use Table 710.1(2) for sizing vertical stacks and horizontal branches. You cannot reduce a vertical stack to less than half the size of the largest stack size required.
- 710.2 Future Fixtures: If you run pipes for a future bathroom, you must size the system as if those fixtures are already installed.
Section 711: Offsets in Drainage Piping (Five Stories or More)
- 711.1 - 711.3 Tall Building Rules: In buildings 5 stories or higher, vertical stacks handle massive amounts of falling water. If the stack offsets horizontally or vertically, severe pressure zones occur. You must install relief vents for these offsets if they are more than four stories (branch intervals) below the top, unless you oversize the stack/offset drastically to act like a building drain.
Section 712: Sumps and Ejectors
- 712.1 Building Subdrains: Plumbing located below the public sewer level cannot drain by gravity. It must drain into a sealed sump pit and be pumped up.
- 712.2 Valves: The pump discharge pipe needs two valves: a check valve (stops water from falling back down) and a full-open valve (for maintenance).
- 712.3 Pit Design: Sump pits must be at least 18" wide and 24" deep. The cover must be gastight and no more than 2" below the floor. The pump must turn on/off so the water level never gets closer than 2 inches to the incoming gravity drain pipe.
- 712.3.5 Pump Connection: Pump discharge pipes must wye into the top of gravity drains, at least 10 pipe diameters away from the bottom of any vertical stack.
- 712.4 Sewage Ejectors: Toilets require pumps that can pass a 2-inch solid ball (unless it is a specific grinder pump (1-1/4" discharge) or macerating toilet (3/4" discharge)).
Section 713: Computerized Drainage Design
- Plumbers and engineers can use approved computer software to size and layout drainage systems based on sequential discharge and pipe roughness factors. Pipes must be sized to prevent "full-bore" (100% full) flow.
Section 714: Backwater Valves
- 714.1 & 714.2 Protection from Backups: If a plumbing fixture sits lower than the nearest upstream street manhole cover, it is at risk of raw sewage backing up into it if the city sewer clogs. These low fixtures must be protected by a backwater valve. Fixtures sitting above the manhole elevation should not discharge through the backwater valve.
- 714.3 Location: Backwater valves must be accessible for cleaning and maintenance.
Section 715: Vacuum Drainage Systems
- Instead of gravity, these systems use vacuum pumps to suck waste through pipes. They must be engineered and installed strictly per the manufacturer's instructions.
- They are tested under a vacuum of 19 inches of mercury.
- A vacuum toilet counts as exactly 1 Water Supply Fixture Unit.
Section 716: Replacement By Pipe-Bursting Methods
- 716.1 - 716.8 Pipe-Bursting: You can replace old sewer lines without digging up the whole yard using pipe-bursting. It is limited to 6-inch or smaller gravity pipes. You must run a camera before to mark connections, use HDPE SDR 17 pipe, install proper cleanouts, and camera the line again after bursting before final pressure testing.
Section 717: Relining Building Sewers and Drains
- 717.1 - 717.10 Relining: For pipes 4 inches and larger, you can install a structural liner inside the old pipe.
- The pipe must be descaled, flushed, and camera inspected first.
- If the pipe is back-graded (slopes the wrong way) or completely separated, you cannot reline it. The defective section must be dug up and repaired conventionally.
- After installation, it must be flushed, flow-tested, and camera inspected again to prove there are no defects.
Section 718: Rehabilitation of Building Sewers and Drains
- 718.1 Cure-In-Place: Outlines the specific ASTM standards (F2599, F2561, F3240) required when rehabilitating sewer lines and service laterals using cure-in-place pipe (CIPP) and hydrophilic gaskets to stop groundwater from leaking in.
TABLE 702.1 - ABOVE-GROUND DRAINAGE AND VENT PIPE
| MATERIAL | STANDARD |
|---|---|
| Acrylonitrile butadiene styrene (ABS) plastic pipe in IPS diameters, including Schedule 40, DR 22 (PS 200) and DR 24 (PS 140); with a solid, cellular core or composite wall | ASTM D2661; ASTM F628; ASTM F1488; CSA B181.1 |
| Cast-iron pipe | ASTM A74; ASTM A888; CISPI 301 |
| Copper or copper-alloy pipe | ASTM B42; ASTM B43; ASTM B302 |
| Copper or copper-alloy tubing (Type K, L, M or DWV) | ASTM B75; ASTM B88; ASTM B251; ASTM B306 |
| Galvanized steel pipe | ASTM A53 |
| Glass pipe | ASTM C1053 |
| Polyolefin pipe | ASTM F1412; ASTM F3371; CSA B181.3 |
| Polyvinyl chloride (PVC) plastic pipe in IPS diameters, including Schedule 40, DR 22 (PS 200), and DR 24 (PS 140); with a solid, cellular core or composite wall | ASTM D2665; ASTM F891; ASTM F1488; CSA B181.2 |
| Polyvinyl chloride (PVC) plastic pipe with a 3.25-inch O.D. and a solid, cellular core or composite wall | ASTM D2949; ASTM F1488 |
| Polyvinylidene fluoride (PVDF) plastic pipe | ASTM F1673; CSA B181.3 |
| Stainless steel drainage systems, Types 304 and 316L | ASME A112.3.1 |
TABLE 702.2 - UNDERGROUND BUILDING DRAINAGE AND VENT PIPE
| MATERIAL | STANDARD |
|---|---|
| Acrylonitrile butadiene styrene (ABS) plastic pipe in IPS diameters, including Schedule 40, DR 22 (PS 200) and DR 24 (PS 140); with a solid, cellular core or composite wall | ASTM D2661; ASTM F628; ASTM F1488; CSA B181.1 |
| Cast-iron pipe | ASTM A74; ASTM A888; CISPI 301 |
| Copper or copper-alloy tubing (Type K, L, M or DWV) | ASTM B75; ASTM B88; ASTM B251; ASTM B306 |
| Polyethylene (PE) plastic pipe (SDR-PR) | ASTM F714 |
| Polyolefin pipe | ASTM F714; ASTM F1412; ASTM F3371; CSA B181.3 |
| Polyvinyl chloride (PVC) plastic pipe in IPS diameters, including Schedule 40, DR 22 (PS 200) and DR 24 (PS 140); with a solid, cellular core or composite wall | ASTM D2665; ASTM F891; ASTM F1488; CSA B181.2 |
| Polyvinyl chloride (PVC) plastic pipe with a 3.25-inch O.D. and a solid, cellular core or composite wall | ASTM D2949; ASTM F1488 |
| Polyvinylidene fluoride (PVDF) plastic pipe | ASTM F1673; CSA B181.3 |
| Stainless steel drainage systems, Type 316L | ASME A112.3.1 |
For SI: 1 inch = 25.4 mm.
TABLE 702.3 - BUILDING SEWER PIPE
| MATERIAL | STANDARD |
|---|---|
| Acrylonitrile butadiene styrene (ABS) plastic pipe in IPS diameters, including Schedule 40, DR 22 (PS 200) and DR 24 (PS 140); with a solid, cellular core or composite wall | ASTM D2661; ASTM D2680; ASTM F628; ASTM F1488; CSA B181.1 |
| Acrylonitrile butadiene styrene (ABS) plastic pipe in sewer and drain diameters, including SDR 42 (PS 20), PS 35, SDR 35 (PS 45), PS 50, PS 100, PS 140, SDR 23.5 (PS 150) and PS 200; with a solid, cellular core or composite wall | ASTM D2751; ASTM F1488 |
| Cast-iron pipe | ASTM A74; ASTM A888; CISPI 301 |
| Concrete pipe | ASTM C14; ASTM C76; CSA A257.1; CSA A257.2 |
| Copper or copper-alloy tubing (Type K or L) | ASTM B75; ASTM B88; ASTM B251 |
| Polyethylene (PE) plastic pipe (corrugated wall) | ASTM F2947/F2947M |
| Polyethylene (PE) plastic pipe (profile wall) | ASTM F2763 |
| Polyethylene (PE) plastic pipe (SDR-PR) | ASTM F714 |
| Polypropylene (PP) plastic pipe | ASTM F2764; CSA B182.13 |
| Polyvinyl chloride (PVC) plastic pipe in IPS diameters, including Schedule 40, DR 22 (PS 200) and DR 24 (PS 140); with a solid, cellular core or composite wall | ASTM D2665; ASTM F891; ASTM F1488 |
| Polyvinyl chloride (PVC) plastic pipe in sewer and drain diameters, including PS 25, SDR 41 (PS 28), PS 35, SDR 35 (PS 46), PS 50, PS 100, SDR 26 (PS 115), PS 140 and PS 200; with a solid, cellular core or composite wall | ASTM F891; ASTM F1488; ASTM D3034; CSA B182.2; CSA B182.4 |
| Polyvinyl chloride (PVC) plastic pipe with a 3.25-inch O.D. and a solid, cellular core or composite wall | ASTM D2949; ASTM F1488 |
| Polyvinylidene fluoride (PVDF) plastic pipe | ASTM F1673; CSA B181.3 |
| Stainless steel drainage systems, Types 304 and 316L | ASME A112.3.1 |
| Vitrified clay pipe | ASTM C4; ASTM C700 |
For SI: 1 inch = 25.4 mm.
TABLE 702.4 - PIPE FITTINGS
| MATERIAL | STANDARD |
|---|---|
| Acrylonitrile butadiene styrene (ABS) plastic pipe in IPS diameters | ASME A112.4.4; ASTM D2661; ASTM F628; CSA B181.1 |
| Acrylonitrile butadiene styrene (ABS) plastic pipe in sewer and drain diameters | ASTM D2751 |
| Cast iron | ASME B16.4; ASME B16.12; ASTM A74; ASTM A888; CISPI 301 |
| Copper or copper alloy | ASME B16.15; ASME B16.18; ASME B16.22; ASME B16.23; ASME B16.26; ASME B16.29 |
| Glass | ASTM C1053 |
| Gray iron and ductile iron | AWWA C110/A21.10 |
| Polyethylene | ASTM D2683 |
| Polyolefin | ASTM F1412; ASTM F3371; CSA B181.3 |
| Polyvinyl chloride (PVC) plastic in IPS diameters | ASME A112.4.4; ASTM D2665; ASTM F1866 |
| Polyvinyl chloride (PVC) plastic pipe in sewer and drain diameters | ASTM D3034 |
| Polyvinyl chloride (PVC) plastic pipe with a 3.25-inch O.D. | ASTM D2949 |
| Polyvinylidene fluoride (PVDF) plastic pipe | ASTM F1673; CSA B181.3 |
| Stainless steel drainage systems, Types 304 and 316L | ASME A112.3.1 |
| Steel | ASME B16.9; ASME B16.11; ASME B16.28 |
| Vitrified clay | ASTM C700 |
For SI: 1 inch = 25.4 mm.
TABLE 702.6 - CHEMICAL WASTE DRAINAGE SYSTEM PIPE AND FITTINGS
| MATERIAL | STANDARD |
|---|---|
| Chlorinated polyvinyl chloride (CPVC) | ASTM F2618 |
| Borosilicate glass | ASTM C1053 |
| High silicon iron | ASTM A518/A518M |
| Polyolefin | ASTM F1412, CSA B181.3 |
| Polyvinylidene fluoride (PVDF) | ASTM F1673, CSA B181.3 |
TABLE 704.1 - SLOPE OF HORIZONTAL DRAINAGE PIPE
| SIZE (inches) | MINIMUM SLOPE (inch per foot) |
|---|---|
| 2 1/2 or less | 1/4 |
| 3 to 6 | 1/8(a) |
| 8 or larger | 1/16 |
For SI: 1 inch = 25.4 mm, 1 inch per foot = 83.33 mm/m.
a. Slopes for piping draining to a grease interceptor shall comply with Section 704.1.
TABLE 705.18 - CAULKING FERRULE SPECIFICATIONS
| PIPE SIZES (inches) | INSIDE DIAMETER (inches) | LENGTH (inches) | MINIMUM WEIGHT EACH |
|---|---|---|---|
| 2 | 2 1/4 | 4 1/2 | 1 pound |
| 3 | 3 1/4 | 4 1/2 | 1 pound 12 ounces |
| 4 | 4 1/4 | 4 1/2 | 2 pounds 8 ounces |
For SI: 1 inch = 25.4 mm, 1 ounce = 28.35 g, 1 pound = 0.454 kg.
TABLE 705.19 - SOLDERING BUSHING SPECIFICATIONS
| PIPE SIZES (inches) | MINIMUM WEIGHT EACH |
|---|---|
| 1 1/4 | 6 ounces |
| 1 1/2 | 8 ounces |
| 2 | 14 ounces |
| 2 1/2 | 1 pound 6 ounces |
| 3 | 2 pounds |
| 4 | 3 pounds 8 ounces |
For SI: 1 inch = 25.4 mm, 1 ounce = 28.35 g, 1 pound = 0.454 kg.
TABLE 706.3 - FITTINGS FOR CHANGE IN DIRECTION
| TYPE OF FITTING PATTERN | Horizontal to vertical | Vertical to horizontal | Horizontal to horizontal |
|---|---|---|---|
| Sixteenth bend | X | X | X |
| Eighth bend | X | X | X |
| Sixth bend | X | X | X |
| Quarter bend | X | X | X |
| Short sweep | X | X (a,b) | X |
| Long sweep | X | X | X |
| Sanitary tee | X | - | - |
| Wye | X | X | X |
| Combination wye and eighth bend | X | X | X |
For SI: 1 inch = 25.4 mm.
a. The fittings shall only be permitted for a 2-inch or smaller fixture drain.
b. Three inches or larger.
c. For a limitation on double sanitary tees, see Section 706.3.
TABLE 709.1 - DRAINAGE FIXTURE UNITS FOR FIXTURES AND GROUPS
| FIXTURE TYPE | DRAINAGE FIXTURE UNIT VALUE AS LOAD FACTORS | MINIMUM SIZE OF TRAP (inches) |
|---|---|---|
| Automatic clothes washers, commerciala, | 3 | 2 |
| Automatic clothes washers, residential | 2 | 2 |
| Bathroom group as defined in Section 202 (1.6 gpf water closet) | 5 | - |
| Bathroom group as defined in Section 202 (water closet flushing greater than 1.6 gpf) | 6 | - |
| Bathtub (with or without overhead shower or whirlpool attachments) | 2 | 1 1/2 |
| Bidet | 1 | 1 1/4 |
| Combination sink and tray | 2 | 1 1/2 |
| Dental lavatory | 1 | 1 1/4 |
| Dental unit or cuspidor | 1 | 1 1/4 |
| Dishwashing machine, domestic | 2 | 1 1/2 |
| Drinking fountain | 1/2 | 1 1/4 |
| Emergency floor drain | 0 | 2 |
| Floor drains | $2^h$ | 2 |
| Floor sinks | Note h | 2 |
| Kitchen sink, domestic | 2 | 1 1/2 |
| Kitchen sink, domestic with food waste disposer, dishwasher or both | 2 | 1 1/2 |
| Laundry tray (1 or 2 compartments) | 2 | 1 1/2 |
| Lavatory | 1 | 1 1/4 |
| Shower (based on the total flow rate through showerheads and body sprays) flow rate: 5.7 gpm or less | 2 | 1 1/2 |
| Greater than 5.7 gpm to 12.3 gpm | 3 | 2 |
| Greater than 12.3 gpm to 25.8 gpm | 5 | 3 |
| Greater than 25.8 gpm to 55.6 gpm | 6 | 4 |
| Service sink | 2 | 1 1/2 |
| Sink | 2 | 1 1/2 |
| Urinal | 4 | Note d |
| Urinal, 1 gallon per flush or less | 2 | Note d |
| Urinal, nonwater supplied | 1/2 | Note d |
| Wash sink (circular or multiple) each set of faucets | 2 | 1 1/2 |
| Water closet, flushometer tank, public or private | 4 | Note d |
| Water closet, private (1.6 gpf) | 3 | Note d |
| Water closet, private (flushing greater than 1.6 gpf) | 4 | Note d |
| Water closet, public (1.6 gpf) | 4 | Note d |
| Water closet, public (flushing greater than 1.6 gpf) | 6 | Note d |
For SI: 1 inch = 25.4 mm, 1 gallon = 3.785 L, gpf = gallon per flushing cycle, 1 gallon per minute (gpm) = 3.785 L/m.
a. For traps larger than 3 inches, use Table 709.2.
b. A showerhead over a bathtub or whirlpool bathtub attachment does not increase the drainage fixture unit value.
c. See Sections 709.2 through 709.4.1 for methods of computing unit value of fixtures not listed in this table or for rating of devices with intermittent flows.
d. Trap size shall be consistent with the fixture outlet size.
e. For the purpose of computing loads on building drains and sewers, water closets and urinals shall not be rated at a lower drainage fixture unit unless the lower values are confirmed by testing.
f. For fixtures added to a bathroom group, add the dfu value of those additional fixtures to the bathroom group fixture count.
g. See Section 406.2 for sizing requirements for fixture drain, branch drain and drainage stack for an automatic clothes washer standpipe.
h. See Sections 709.4 and 709.4.1.
TABLE 709.2 - DRAINAGE FIXTURE UNITS FOR FIXTURE DRAINS OR TRAPS
| FIXTURE DRAIN OR TRAP SIZE (inches) | DRAINAGE FIXTURE UNIT VALUE |
|---|---|
| 1 1/4 | 1 |
| 1 1/2 | 2 |
| 2 | 3 |
| 2 1/2 | 4 |
| 3 | 5 |
| 4 | 6 |
For SI: 1 inch = 25.4 mm.
TABLE 710.1(1) - BUILDING DRAINS AND SEWERS
MAXIMUM NUMBER OF DRAINAGE FIXTURE UNITS CONNECTED TO ANY PORTION OF THE BUILDING DRAIN OR THE BUILDING SEWER, INCLUDING BRANCHES OF THE BUILDING DRAIN
| DIAMETER OF PIPE (inches) | Slope per foot 1/16 inch | Slope per foot 1/8 inch | Slope per foot 1/4 inch | Slope per foot 1/2 inch |
|---|---|---|---|---|
| 1 1/4 | --- | --- | 1 | 1 |
| 1 1/2 | --- | --- | 3 | 3 |
| 2 | --- | --- | 21 | 26 |
| 2 1/2 | --- | --- | 24 | 31 |
| 3 | --- | 36 | 42 | 50 |
| 4 | --- | 180 | 216 | 250 |
| 5 | --- | 390 | 480 | 575 |
| 6 | --- | 700 | 840 | 1,000 |
| 8 | 1,400 | 1,600 | 1,920 | 2,300 |
| 10 | 2,500 | 2,900 | 3,500 | 4,200 |
| 12 | 3,900 | 4,600 | 5,600 | 6,700 |
| 15 | 7,000 | 8,300 | 10,000 | 12,000 |
For SI: 1 inch = 25.4 mm, 1 inch per foot = 83.3 mm/m.
a. The minimum size of any building drain serving a water closet shall be 3 inches.
TABLE 710.1(2) - HORIZONTAL FIXTURE BRANCHES AND STACKS
MAXIMUM NUMBER OF DRAINAGE FIXTURE UNITS (dfu)
| DIAMETER OF PIPE (inches) | Total for horizontal branch | Total discharge into one branch interval | Total for stack of three branch intervals or less | Total for stack greater than three branch intervals |
|---|---|---|---|---|
| 1 1/2 | 3 | 2 | 4 | 8 |
| 2 | 6 | 6 | 10 | 24 |
| 2 1/2 | 12 | 9 | 20 | 42 |
| 3 | 20 | 20 | 48 | 72 |
| 4 | 160 | 90 | 240 | 500 |
| 5 | 360 | 200 | 540 | 1,100 |
| 6 | 660 | 350 | 960 | 1,900 |
| 8 | 1,400 | 600 | 2,200 | 3,600 |
| 10 | 2,500 | 1,000 | 3,800 | 5,600 |
| 12 | 3,900 | 1,500 | 6,000 | 8,400 |
| 15 | 7,000 | Note c | Note c | Note c |
For SI:1 inch = 25.4 mm.
a. Does not include branches of the building drain. Refer to Table 710.1(1).
b. Stacks shall be sized based on the total accumulated connected load at each story or branch interval.
As the total accumulated connected load decreases, stacks are permitted to be reduced in size.
Stack diameters shall not be reduced to less than one-half of the diameter of the largest stack size required.
c. Sizing load based on design criteria.
TABLE 712.4.2 - MINIMUM CAPACITY OF SEWAGE PUMP OR SEWAGE EJECTOR
| DIAMETER OF THE DISCHARGE PIPE (inches) | CAPACITY OF PUMP OR EJECTOR (gpm) |
|---|---|
| 2 | 21 |
| 2 1/2 | 30 |
| 3 | 46 |
For SI: 1 inch = 25.4 mm, 1 gallon per minute = 3.785 L/m.