Storm Drainage

Chapter 11 regulates the safe and effective removal of rainwater and stormwater from building roofs, paved areas, and courtyards. It establishes the rules for sizing pipe and gutter systems based on local rainfall data, selecting approved materials, preventing stormwater from entering sanitary sewers, and installing specialized systems like emergency overflow drains, subsoil drains, and sump pumps.

  • Storm and Sanitary Do Not Mix: You cannot drain stormwater into a sewer meant only for sanitary sewage.
  • Flow Direction Matters: Just like sanitary systems, you can never reduce the size of a drainage pipe in the direction of flow.
  • Secondary Systems Must Be Separate: Emergency/secondary roof drains must have a completely independent discharge path from the primary drainage system and must discharge above grade where people can see it.
  • Sizing is Local: Storm drain sizing is completely dependent on your specific geographic area's 100-year, 1-hour rainfall rate (measured in inches per hour).
  • Combined Sewers Require Traps: If you are forced to connect a storm drain to a combined public sewer (handling both storm and sanitary), the storm system must be trapped.
  • Conductor: An inside pipe that carries stormwater from the roof down to the building storm drain or sewer.
  • Leader: An exterior vertical drainage pipe for conveying stormwater from roof or gutter drains.
  • Scupper: An opening cut through a parapet wall or raised roof edge that allows water to drain off the roof.
  • Subsoil Drain: An underground, perforated, or open-jointed pipe installed to collect and drain away groundwater or subsurface water from around a building's foundation.
  • Sump: A pit or tank below the normal drainage level that collects liquids so they can be pumped up and out of the building.
  • Secondary (Emergency) Drain: A backup drainage system designed to take over if the primary roof drains become clogged, preventing the roof from collapsing under the weight of ponded water.

Exam Prep & Tips

  • Rainfall Rate is the Key: Whenever you see a question about sizing storm drains, remember the magic phrase: "100-year, 1-hour rainfall rate."
  • Sump Pit Dimensions: Commit the minimum sump pit dimensions (18" diameter, 24" deep) to memory; this is a very common exam question.
  • Scuppers vs. Primary Drains: Remember that when sizing an emergency (secondary) system or scupper, you do not factor in the primary system's flow. You assume the primary system is 100% blocked.
  • Pump Valves: Pay close attention to what valves are required on a sump pump discharge. Commercial needs both a gate valve and a check valve; residential (1- & 2-family) only needs a check valve.

Prohibited Practices

  • Stormwater into sanitary sewer: Stormwater shall not be drained into sewers intended for sewage only. (1101.3)
  • Pipe reduction: The size of a drainage pipe shall not be reduced in the direction of flow. (1101.5)
  • Mixing pipe uses: Conductor pipes shall not be used as soil, waste, or vent pipes, and vice-versa. (1104.1)
  • Floor drains: Floor drains shall not be connected to a storm drain. (1104.2)
  • Combining discharges: Secondary roof drain systems shall not share a discharge endpoint with the primary system (they must be separate). (1108.2)

Most Tested Numbers

  • 100-year, 1-hour: The design rainfall rate event used for sizing storm drains.
  • 4 inches: Minimum opening height for a parapet wall scupper.
  • 4 inches: Minimum pipe diameter for a subsoil drain.
  • 2 roof drains: The minimum number of controlled flow roof drains required for roof areas of 10,000 square feet or less.
  • 4 roof drains: The minimum number of controlled flow roof drains required for roof areas over 10,000 square feet.
  • 18 inches: Minimum required diameter for a sump pit.
  • 24 inches: Minimum required depth for a sump pit.
  • 50% (One-half): The amount of a vertical wall's area that must be added to the projected roof area when sizing drains, if that wall diverts rainwater onto the roof.

Section 1101: General

  • 1101.1 & 1101.2 Scope & Disposal: Rainwater from roofs and paved areas must drain to an approved location. For 1- and 2-family homes, you can discharge rainwater onto lawns or streets as long as the water flows away from the building foundation.
  • 1101.3 Prohibited drainage: Never run storm water into a sewer built only for sanitary sewage.
  • 1101.4 Tests: Storm drains and conductors must be tested just like sanitary systems (as covered in Section 312).
  • 1101.5 Change in size: Pipe sizes cannot shrink as they head downstream (in the direction of flow).
  • 1101.6 Fittings: You must use approved drainage-type fittings that don't block or slow down the water flow.
  • 1101.7 Roof design: Roofs must be structurally designed to handle the max weight/depth of water if all primary drains get blocked. The calculation includes the depth of water needed to trigger the emergency (secondary) drains.
  • 1101.8 Cleanouts: Storm drains need cleanouts following the same rules as sanitary sewers, except you don't need cleanouts for subsurface (subsoil) drainage.
  • 1101.9 Backwater valves: If the system is subject to backing up, it needs a backwater valve (just like a sanitary system).

Section 1102: Materials

  • 1102.1 - 1102.4 General Pipe Materials: This covers approved materials for different parts of the system. Inside conductors, underground drains, and building storm sewers can use common plastics (ABS, PVC, PE, PP), cast iron, copper, or stainless steel, as long as they meet specific ASTM/CSA standards.
  • 1102.5 Subsoil drain pipe: These must be open-jointed, horizontally split, or perforated pipes (like corrugated PE, PVC, cast iron, or porous clay) so water from the soil can seep into them.
  • 1102.6 Roof drains: Must meet ASME testing standards.
  • 1102.7 Fittings: Must match the pipe material and have a smooth interior (no ledges or shoulders to catch debris). Threaded fittings must be the recessed drainage type.

Section 1103: Traps

  • 1103.1 Main trap: If you are connecting storm drains to a combined sewer (handles both sewage and rain), you must install a trap to keep sewer gases out. You can trap individual branches or put one main trap before the sewer connection. If you are connecting to a dedicated storm sewer, traps are not required.
  • 1103.2 - 1103.4 Trap Rules: The trap must be the same material and size as the horizontal pipe it connects to. You must install an accessible cleanout on the building side of the trap.

Section 1104: Conductors and Connections

  • 1104.1 Prohibited use: Do not mix systems. A storm conductor cannot act as a sanitary waste/vent pipe, and a sanitary waste/vent pipe cannot act as a storm conductor.
  • 1104.2 Floor drains: Do not connect floor drains (which handle sanitary waste/spills) into the storm drain system.

Section 1105: Roof Drains

  • 1105.1 & 1105.2 Installation: Follow the manufacturer's instructions. Do not let roofing membranes block the drain opening. When sizing pipes, use the roof drain's published flow rate based on the maximum expected water ponding depth.

Section 1106: Size of Conductors, Leaders, and Storm Drains

  • 1106.1 Sizing Basis: All sizing is based on the "100-year, 1-hour rainfall rate" (provided in regional maps or local weather data).
  • 1106.2 Pipe Sizing & Conversion (1106.2.1): Pipes are sized based on GPM flow. To convert rainfall to GPM, use Equation 11-1: GPM = Rainfall Rate (inches/hr) x Roof Area (sq ft) x 0.0104.
  • 1106.3 Vertical Leaders: Sized using Table 1106.3 based on GPM capacity.
  • 1106.4 Vertical Walls: If a vertical wall sits above a roof and deflects driving rain down onto that roof, you must add 50% (one-half) of that wall's square footage to the roof's total square footage for sizing calculations.
  • 1106.5 Parapet wall scuppers: Scuppers must be sized to prevent water from rising higher than the roof's structural limit. A scupper opening must be at least 4 inches high, and its width must at least equal the circumference of a standard roof drain sized for that same roof area.
  • 1106.6 Horizontal Gutters: Sized using Table 1106.6 based on flow rate and slope.

Section 1107: Siphonic Roof Drainage Systems

  • 1107.1 General: These are engineered systems that utilize a vacuum effect to pull water off the roof at high speeds. They must be designed strictly to ASME A112.6.9 and ASPE 45 standards.

Section 1108: Secondary (Emergency) Roof Drains

  • 1108.1 When Required: If the roof has parapet walls that would trap water if the primary drains clogs, you must install secondary (emergency) drains or scuppers.
  • 1108.2 Separate systems: The emergency drains must pipe to a completely separate endpoint than the primary drains. They must discharge above grade in a spot where building occupants or maintenance will clearly see the water pouring out (so they know the main drains are clogged).
  • 1108.3 Sizing: Size the emergency system identically to the primary system. When calculating the emergency system, assume the primary system is 100% blocked (do not subtract the primary's flow capacity). Emergency scuppers must be at least 4 inches high.

Section 1109: Combined Sanitary and Storm Public Sewer

  • 1109.1 General: Even if the city public sewer combines both storm and sanitary sewage into one pipe, you must run your building's storm sewer completely separate until it connects independently to the public sewer.

Section 1110: Controlled Flow Roof Drain Systems

  • 1110.1 - 1110.3 Engineered Storage: Sometimes roofs are intentionally designed as temporary "bathtubs" to hold water during heavy storms and release it slowly (so city sewers don't flood). This is highly engineered. Control devices regulate the slow drain and must be protected by strainers.
  • 1110.4 Minimum Drain Count: Controlled flow roofs must have at least 2 roof drains if the roof is 10,000 square feet or smaller. If the roof is over 10,000 square feet, you need at least 4 roof drains.

Section 1111: Subsoil Drains

  • 1111.1 Installation: Subsoil drains collect ground water around foundations. They must be at least 4 inches in diameter and perforated/open-jointed. If there's a risk of water backing up into them, they need an accessible backwater valve. They can drain to a trapped area drain, dry well, or sump. A subsoil sump pit does not need a gastight cover or a vent.

Section 1112: Building Subdrains

  • 1112.1 Lift Systems: If building storm subdrains are lower than the public sewer elevation, gravity won't work. The water must drain into a sump or receiving tank and be automatically pumped up and out.

Section 1113: Sumps and Pumping Systems

  • 1113.1.1 Pump capacity: The pump must be strong enough to handle the anticipated water volume and lift (head).
  • 1113.1.2 Sump pit dimensions: Sump pits must be at least 18 inches in diameter and 24 inches deep. They need a solid floor to support the pump and a removable cover tough enough to handle foot/vehicle traffic above.
  • 1113.1.3 Electrical: Must follow the National Electrical Code (NFPA 70).
  • 1113.1.4 Piping & Valves: The discharge pipe must be the same size as (or larger than) the pump's outlet. Commercial pumps require both a full-flow check valve AND a gate valve. Exception: 1- and 2-family residential homes only require a check valve on the pump discharge.

TABLE 1102.4 - BUILDING STORM SEWER PIPE

MATERIALSTANDARD
Acrylonitrile butadiene styrene (ABS) plastic pipe in IPS diameters, including Schedule 40, DR 22 (PS 200) and DR 24 (PS 140); with a solid, cellular core or composite wallASTM D2661;ASTM F628; ASTM F1488; CSA B181.1; CSA B182.1
Cast-iron pipeASTM A74;ASTM A888; CISPI 301
Concrete pipeASTM C14; ASTM C76; CSA A257.1; CSA A257.2
Copper or copper-alloy tubing (Type K, L, M or DWV)ASTM B75; ASTM B88; ASTM B251; ASTM B306
Polyethylene (PE) plastic pipeASTM F667; ASTM F2306/F2306M; ASTM F2648/F2648M; ASTM F2763; ASTM F2947/F2947M; CSA B182.8
Polypropylene (PP) pipeASTM F2764; ASTM F2881; CSA B182.13
Polyvinyl chloride (PVC) plastic pipe (Type DWV, SDR26, SDR35, SDR41, PS50 or PS100) in IPS diameters, including Schedule 40, DR 22 (PS 200) and DR 24 (PS 140); with a solid, cellular core or composite wallASTM D2665; ASTM D3034; ASTM F891; ASTM F1488; CSA B181.2; CSA B182.2; CSA B182.4
Stainless steel drainage systems, Type 316LASME A112.3.1
Vitrified clay pipeASTM C4; ASTM C700

TABLE 1102.5 - SUBSOIL DRAIN PIPE

MATERIALSTANDARD
Cast-iron pipeASTM A74; ASTM A888; CISPI 301
Polyethylene (PE) plastic pipeASTM F667; CSA B182.1; CSA B182.6; CSA B182.8
Polyvinyl chloride (PVC) plastic pipe (type sewer pipe, SDR35, PS25, PS50 or PS100)ASTM D2729; ASTM D3034; ASTM F891; CSA B182.2; CSA B182.4
Stainless steel drainage systems, Type 316LASME A112.3.1
Vitrified clay pipeASTM C4; ASTM C700

TABLE 1102.7 - PIPE FITTINGS

MATERIALSTANDARD
Acrylonitrile butadiene styrene (ABS) plasticASTM D2661; ASTM D3311; CSA B181.1
Cast ironASME B16.4; ASME B16.12; ASTM A74; ASTM A888; CISPI 301
Coextruded composite ABS and drain DR-PS in PS35, PS50, PS100, PS140, PS200ASTM D2751
Coextruded composite ABS DWV Schedule 40 IPS pipe (solid or cellular core)ASTM D2661; ASTM D3311; ASTM F628
Coextruded composite PVC DWV Schedule 40 IPS-DR, PS140, PS200 (solid or cellular core)ASTM D2665; ASTM D3311; ASTM F891
Coextruded composite PVC sewer and drain DR-PS in PS35, PS50, PS100, PS140, PS200ASTM D3034
Copper or copper alloyASME B16.15; ASME B16.18; ASME B16.22; ASME B16.23; ASME B16.26; ASME B16.29
Gray iron and ductile ironAWWA C110/A21.10
Malleable ironASME B16.3
Plastic, generalASTM F409
Polyethylene (PE) plastic pipeASTM F667/F667M; ASTM F2306/F2306M; ASTM F2763; ASTM F2947/F2947M
Polypropylene (PP) plastic pipeASTM F2764; ASTM F2881/F2881M
Polyvinyl chloride (PVC) plasticASTM D2665; ASTM D3311; ASTM F1866; ASTM F3202
Stainless steel drainage systems, Type 316LASME A112.3.1
SteelASME B16.9; ASME B16.11; ASME B16.28

TABLE 1106.2 - STORM DRAIN PIPE SIZING

CAPACITY (gpm) SLOPE OF HORIZONTAL DRAIN

PIPE SIZE(inches)VERTICAL DRAIN1/16 inch per foot1/8 inch per foot1/4 inch per foot1/2 inch per foot
23415223144
387395579111
418081115163231
5311117165234331
6538243334487689
81,1175057141,0101,429
102,0509271,3111,8552,623
123,2721,4802,0932,9604,187
155,5432,5083,5465,0167,093

For SI: 1 inch = 25.4 mm, 1 foot = 304.8 mm, 1 gallon per minute = 3.785 L/m.

TABLE 1106.3 - VERTICAL LEADER SIZING

SIZE OF LEADER (inches)CAPACITY (gpm)
230
2x230
1 1/2 x 2 1/230
2 1/254
2 1/2 x 2 1/254
392
2x492
2 1/2 x 392
4192
3 x 4 1/2192
3 1/2 x 4192
5360
4x5360
4 1/2 x 4 1/2360
6563
5x6563
5 1/2 x 5 1/2563
81208
6x81208

For SI: 1 inch = 25.4 mm, 1 gallon per minute = 3.785 L/m.

TABLE 1106.6 - HORIZONTAL GUTTER SIZING

GUTTER DIMENSIONS(a) (a) (inches)SLOPE (inch per foot)CAPACITY (gpm)
1 1/2 x 2 1/21/426
1 1/2 x 2 1/21/240
41/839
2 1/4 x 31/455
2 1/4 x 31/287
51/874
4 x 2 1/21/4106
3 x 3 1/21/2156
61/8110
3x51/4157
3x51/2225
81/16172
81/8247
4 1/2 x 61/4348
4 1/2 x 61/2494
101/16331
101/8472
5x81/4651
4 x 101/21055

For SI: 1 inch = 25.4 mm, 1 foot = 304.8 mm, 1 gallon per minute = 3.785 L/m, 1 inch per foot = 83.3 mm/m.

a. Dimensions are width by depth for rectangular shapes. Single dimensions are diameters of a semicircle.